Been having some problems with unburnt coal (RIE) (its been making a pan of ash/unburnt a day)
Anyway i was playing around with some settings this past week (ashing temp and hysteris), Saturday morning I turned the grate off for about 8 hours and was close to an out fire.
I think I accidentally changed some settings that I shouldn't have 1st the grate wouldn't turn off, then it wouldn't turn on.
Could someone share the settings from an inkbird controller? Specifically the output (oP) settings for ctrl and run.
As well as the alarm settings (ALP) for alarm mode?
I believe that the rest of the settings are irrelevant for this application, but I may be wrong.
Thanks
Inkbird controller help S260 coalgun
- StokerDon
- Site Moderator
- Posts: 7779
- Joined: Mon. Nov. 11, 2013 11:17 am
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
I had Inkbirds on my Axeman Anderson. Here are the IP and OP settings I used.
IP menu.
SN = y (Thermocouple type).
SC = 0.0 (Temp Offset).
DL = 0.
OP menu.
Ctrl = On Off.
H-C = Heat. If you have this wrong it will turn ON when temp rises instead of OFF.
Run = Currently Auto but I don't think it makes a difference.
Here's a video where I did some explaining.
-Don
IP menu.
SN = y (Thermocouple type).
SC = 0.0 (Temp Offset).
DL = 0.
OP menu.
Ctrl = On Off.
H-C = Heat. If you have this wrong it will turn ON when temp rises instead of OFF.
Run = Currently Auto but I don't think it makes a difference.
Here's a video where I did some explaining.
-Don
- swyman
- Member
- Posts: 2367
- Joined: Mon. Apr. 13, 2015 9:50 pm
- Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
- Coal Size/Type: Lehigh Pea
I have copied Stoker Don's Inkbird controls and this year even added one for boiler control in place of the aquastat and is working out very nice. His video's are very informative and explains (in detail) how to setup.
- Retro_Origin
- Member
- Posts: 1478
- Joined: Sun. Feb. 21, 2021 7:46 pm
- Stoker Coal Boiler: 1957 Axeman Anderson 130
- Coal Size/Type: Pea
If the Inkbird is faster to respond why does it run at a lower temperature than the stock anthrastat? If the stock unit has some delay in reading temperature and is set at 140, it kind of implies your MAX allowable temperature is near 130-140 but the inkbirds are known to be in the 105-110 range, this seems backwards to me?
- Lightning
- Site Moderator
- Posts: 14853
- Joined: Wed. Nov. 16, 2011 9:51 am
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
I always thought that 140 on the anthrastat was too high. When I was using one I set it around 115-120, if I recall correctly lol
I run the inkbird at 115
I run the inkbird at 115