Combustion motor
Recently replace combustion fan/motor on keystoker 90. Switched to a ball bearing Dayton 1tdn7. I’m only getting an extremely small flame now. The cfm changed from a 60 to a 50. If I didn’t wire up the new one correctly since the were slightly different would that make the fan only run at half power?
- nepacoal
- Member
- Posts: 1729
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
That's a 16% decrease so I can see it being noticeable. What was the model number of your old one? Those motors only have 2 wires, right? And it doesn't matter which wire is hot or neutral so how could it be wired wrong?
- nepacoal
- Member
- Posts: 1729
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
Dayton lists that blower as non reversible. I don't think any of these blowers are reversible no matter if they're Fasco or Dayton.