Keystoker Koker smell

 
Liccs
New Member
Posts: 14
Joined: Sat. Jan. 21, 2023 12:42 am
Location: Bloomsbury NJ Near Easton PA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Buck

Post by Liccs » Mon. Jan. 23, 2023 11:30 am

nepacoal wrote:
Mon. Jan. 23, 2023 5:20 am
Fire actually looks good! You even have some additional capacity if you ever needed more heat. A manometer would be the next logical thing to get so you can check your draft to see what it's doing at the start of a heat call and at idle. On a stoker it's inserted into the stove to check and set over fire air (set after a long run so the chimney is up to temp). I use a magnehelic I found on ebay for $25. The Dwyer mark II 25 is another popular choice here.

Maybe the wet load of coal caused a short term anomaly. Wet coal causes most of the stoker problems we see.

I didn't think to ask, but you do keep your hopper on the full side, right? Letting it get real low could possibly cause it to leak exhaust as the fan first turns on.
yeah, im going to have to look into this manometer...i just wouldnt have the slighest clue how to use it!! lol but i always keep my hopper full tbh, and like sometimes the coal is damp when i pour it in cause its like always raining by me for some reason no idea why its annoying. but ill def look into this manometer cause everyone keeps saying it!!


 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Mon. Jan. 23, 2023 11:39 am

You could bump up your barometric damper to -.05 to give yourself a little more cushion with your draft. Probably a good idea until you get the manometer set up.

 
User avatar
Idlorah
Member
Posts: 520
Joined: Wed. Nov. 18, 2020 6:31 pm
Location: New Ringgold, PA
Stoker Coal Boiler: Allen 700 stoker
Hand Fed Coal Stove: Gibralter MCC
Coal Size/Type: Buck in the Allen and anything goes in the MCC, Anthracite
Other Heating: None, maybe some wood in the MCC in the shoulder season

Post by Idlorah » Mon. Jan. 23, 2023 9:16 pm

Liccs wrote:
Mon. Jan. 23, 2023 12:12 am
So this is the fire when I just turned the thermostat on and it just started calling for heat
In the photo of your barometric damper it does not appear to be level. these dampers need the hinge part to be level to work properly.

 
Liccs
New Member
Posts: 14
Joined: Sat. Jan. 21, 2023 12:42 am
Location: Bloomsbury NJ Near Easton PA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Buck

Post by Liccs » Mon. Jan. 23, 2023 11:44 pm

Idlorah wrote:
Mon. Jan. 23, 2023 9:16 pm
In the photo of your barometric damper it does not appear to be level. these dampers need the hinge part to be level to work properly.
Okay I will level it…I just turn it right??

 
User avatar
Idlorah
Member
Posts: 520
Joined: Wed. Nov. 18, 2020 6:31 pm
Location: New Ringgold, PA
Stoker Coal Boiler: Allen 700 stoker
Hand Fed Coal Stove: Gibralter MCC
Coal Size/Type: Buck in the Allen and anything goes in the MCC, Anthracite
Other Heating: None, maybe some wood in the MCC in the shoulder season

Post by Idlorah » Tue. Jan. 24, 2023 12:47 am

Yes, the bar for the hinge should be level.

 
Liccs
New Member
Posts: 14
Joined: Sat. Jan. 21, 2023 12:42 am
Location: Bloomsbury NJ Near Easton PA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Buck

Post by Liccs » Tue. Jan. 24, 2023 9:56 am

Idlorah wrote:
Tue. Jan. 24, 2023 12:47 am
Yes, the bar for the hinge should be level.
What part is the bar hinge…just the bar the door sits on right???

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Jan. 24, 2023 10:06 am

Screenshot_20230124-100419.png
.PNG | 477.2KB | Screenshot_20230124-100419.png
In this screenshot, they are labeled as pivot points. You want those level with each other.


 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Wed. Jan. 25, 2023 10:47 am

nepacoal wrote:
Mon. Jan. 23, 2023 11:39 am
You could bump up your barometric damper to -.05 to give yourself a little more cushion with your draft. Probably a good idea until you get the manometer set up.
I don't have the Koker, but do have the Kaa-2 boiler. Without looking, and going by memory, it seems the over fire draft is -.02, and chimney pipe was -.o3, or maybe -.o4. If me, I'd consider lowering your over fire to -.02, rather than upping chimney draft. Remember, the fan is forcing air through the coal fire. You are not depending on chimney draw to pull air through the coal bed. Speaking of combustion fan forcing air through the fire, that could also be the culprit. Too much positive pressure from combustion fan. Try cutting off the combustion air a little, which is how you adjust the over fire air flow anyways. Cut off combustion air just enough till smell goes away.

 
Liccs
New Member
Posts: 14
Joined: Sat. Jan. 21, 2023 12:42 am
Location: Bloomsbury NJ Near Easton PA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Buck

Post by Liccs » Thu. Jan. 26, 2023 1:18 pm

How do I cut off the combustion air?? or adjust??

 
Liccs
New Member
Posts: 14
Joined: Sat. Jan. 21, 2023 12:42 am
Location: Bloomsbury NJ Near Easton PA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Buck

Post by Liccs » Thu. Jan. 26, 2023 1:19 pm

oliver power wrote:
Wed. Jan. 25, 2023 10:47 am
I don't have the Koker, but do have the Kaa-2 boiler. Without looking, and going by memory, it seems the over fire draft is -.02, and chimney pipe was -.o3, or maybe -.o4. If me, I'd consider lowering your over fire to -.02, rather than upping chimney draft. Remember, the fan is forcing air through the coal fire. You are not depending on chimney draw to pull air through the coal bed. Speaking of combustion fan forcing air through the fire, that could also be the culprit. Too much positive pressure from combustion fan. Try cutting off the combustion air a little, which is how you adjust the over fire air flow anyways. Cut off combustion air just enough till smell goes away.
how do i adjust the combustion air fan?? its not the btu knob coming out of the feed plate correct??

 
Liccs
New Member
Posts: 14
Joined: Sat. Jan. 21, 2023 12:42 am
Location: Bloomsbury NJ Near Easton PA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Buck

Post by Liccs » Thu. Jan. 26, 2023 1:21 pm

nepacoal wrote:
Tue. Jan. 24, 2023 10:06 am
Screenshot_20230124-100419.pngIn this screenshot, they are labeled as pivot points. You want those level with each other.
okay thank you!! its level now!!

 
Eab91276
Member
Posts: 57
Joined: Mon. Jan. 28, 2019 9:23 pm
Location: EasternPA
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: Rice/Anthracite
Other Heating: Propane Insert; Heat Pump

Post by Eab91276 » Thu. Jan. 26, 2023 8:16 pm

The combustion fan has a plate over the intake. You’ll see it under the pusher bar assembly. I’ll put a pic here. My advice, don’t mess with combustion air until you know your draft. Without an accurate draft measurement this is all guessing. Here is my manometer mounted on the wall. I have direct vent not a chimney, but it will measure draft no matter what. Finally, if you go to the Keystoker website they have helpful videos and manuals. Trust me it is a learning curve. We bought our house in 2017 with the koker all ready there. I had no clue how to run it. Haha.

 
waytomany?s
Member
Posts: 3751
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Thu. Jan. 26, 2023 9:05 pm

Eab91276 wrote:
Thu. Jan. 26, 2023 8:16 pm
The combustion fan has a plate over the intake. You’ll see it under the pusher bar assembly. I’ll put a pic here. My advice, don’t mess with combustion air until you know your draft. Without an accurate draft measurement this is all guessing.
EEC04071-C700-400F-AAE3-CD5AC5DDFFF2.jpeg

Here is my manometer mounted on the wall. I have direct vent not a chimney, but it will measure draft no matter what.
05A564E0-4A81-4D3A-83C1-956263157F7A.jpeg

Finally, if you go to the Keystoker website they have helpful videos and manuals. Trust me it is a learning curve. We bought our house in 2017 with the koker all ready there. I had no clue how to run it. Haha.
Switch your hose to the other side of the mano, way easier to read.

 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Fri. Jan. 27, 2023 9:09 pm

Eab91276 wrote:
Thu. Jan. 26, 2023 8:16 pm
The combustion fan has a plate over the intake. You’ll see it under the pusher bar assembly. I’ll put a pic here. My advice, don’t mess with combustion air until you know your draft. Without an accurate draft measurement this is all guessing.
EEC04071-C700-400F-AAE3-CD5AC5DDFFF2.jpeg

Here is my manometer mounted on the wall. I have direct vent not a chimney, but it will measure draft no matter what.
05A564E0-4A81-4D3A-83C1-956263157F7A.jpeg

Finally, if you go to the Keystoker website they have helpful videos and manuals. Trust me it is a learning curve. We bought our house in 2017 with the koker all ready there. I had no clue how to run it. Haha.
He'd be safe to close it a little. Enough till smell goes away. But surely would not want to open it ANY without knowing draft. I see some have a rivit from factory setting the air. The rivit would need drilling out. My Kaa-2 was not rivited from factory.

 
WIburnerPaul
Member
Posts: 28
Joined: Tue. Feb. 28, 2023 4:33 am
Location: West Allis WI
Hand Fed Coal Stove: King Oak 19B
Coal Size/Type: Anthracite Nut
Other Heating: Harman Absolute43 wood pellet. Lamppa Kuuma Vapor-Fire 200 gasification wood furnace.

Post by WIburnerPaul » Mon. Mar. 06, 2023 5:37 am

Liccs wrote:
Mon. Jan. 23, 2023 12:12 am
So this is the fire when I just turned the thermostat on and it just started calling for heat
[/quote} Please tell about your chimney in detail.