Post by Pacowy » Tue. Sep. 10, 2019 8:44 am

Larry thanks for the reminder about the 75 deg. I'll change my estimate to 2.75 tons to account for that.

Mike


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 8:50 am

I'm initially estimating that for 6,850 HDD's if you had a 'Manual J' heat loss calculation taken for your home it would come out at about 20,000 BTUH, which means an appliance delivering 28,000 BTUH (or 1.4 x 'Manual J') as output (ballpark 40,000 BTUH as input) should heat your home on the extreme coldest of days.

From there (using my "Rule of 2.5") I estimate an average hourly need for 16,000 input BTUH (which is 40,000 BTUH divided by 2.5). That is 1.3 Lbs. of coal per average hour, or 31.2 Lbs. of coal per average day.

For 210 days you would therefore burn 6,552 Lbs. of coal per "average" year, or 3.28 tons.

So having 3.5 tons on hand would seem to be prudent. At least until you have some history to go by.
Last edited by lsayre on Tue. Sep. 10, 2019 8:55 am, edited 3 times in total.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Tue. Sep. 10, 2019 8:51 am

Having 4 ton would cover the whole shootin match!! :)

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 12:11 pm

Will there be any 'cheating' via the use of other heat sources or fuels which might cut into the calculated 3.28 tons per year?

I missed the parts about the home being well insulated with 2 x 6 studs, and not heating the basement. You may get by with as little as 2.75 tons, particularly if you can live with a T-Stat at 70 degrees. But as for everyone, the annual need will be dependent upon the length and severity of the winter, which is tracked by the regions annual HDD's in conjunction with an aggressive "Manual J" heat loss evaluation. And keeping your T-Stat at 75 degrees is not going to help consumption.

Go here to determine past historical HDD's for your locality:
https://www.huduser.gov/portal/resources/UtilityM ... l/hdd.html

An agressive Manual J heat loss assessment should cost about $150 to perhaps $200. Ask for it to be done aggressively and honestly, else they just may have you heating a small home with a gigantic large home heating appliance.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 6:45 pm

Another ballpark way to guess at daily average demand is to presume it will be half of "Manual J".

Sticking with a Manual J heat loss guess of 20,000 BTUH, this calculates as follows:

20,000/2 = 10,000 BTUH output

10,000/0.70 = 14,286 BTUH input

14,286/12,300 = 1.16 Lbs. per hour ~= 27.8 Lbs. per day

27.8 x 210 = 5,838 Lbs. per average season = 2.92 tons

2.92 tons x 1.14 (for 75 degrees vs. 70 degrees on the T-Stat) = 3.33 tons per average season

 
User avatar
Richard S.
Mayor
Posts: 15183
Joined: Fri. Oct. 01, 2004 8:35 pm
Location: NEPA
Stoker Coal Boiler: Van Wert VA1200
Coal Size/Type: Buckwheat/Anthracite

Post by Richard S. » Tue. Sep. 10, 2019 6:56 pm

Pacowy wrote:
Tue. Sep. 10, 2019 8:19 am
The Mayor's Rule of 5 tons for every 2000 sf of living space would say 2.4 tons,
That's an average house in NEPA that does not have 2*6 walls... ;) If the house is well insulated and new(er) windows wouldn't surprise me if he only used 2 but I would get at least three and figure it out from there.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 6:59 pm

It's all just guessing until there is a legitimate and aggressive (as in cutting it to the quick) 'Manual J' heat loss assessment. But for the cost of a Manual J assessment, he could buy roughly an extra 2/3 tons of coal. I'd probably just go for the extra coal.

My guess is that if 6 Manual J assessments were made, none of them would be in agreement.

Ah, yee of little faith. (that's me)
Last edited by lsayre on Tue. Sep. 10, 2019 7:17 pm, edited 1 time in total.


 
User avatar
Richard S.
Mayor
Posts: 15183
Joined: Fri. Oct. 01, 2004 8:35 pm
Location: NEPA
Stoker Coal Boiler: Van Wert VA1200
Coal Size/Type: Buckwheat/Anthracite

Post by Richard S. » Tue. Sep. 10, 2019 7:14 pm

lsayre wrote:
Tue. Sep. 10, 2019 6:59 pm
It's all just guessing until there is a legitimate 'Manual J' heat loss assessment.
They are estimates Larry but I'm basing it on hundreds of customers and what they used. I had one guy went through more than 20 ton a year in an old farmhouse that couldn't have been more that 1500 sq. ft. Another guy in home that was also about 1500 used 2 and he claimed it provided nearly all the heat for the season.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 7:22 pm

Richard S. wrote:
Tue. Sep. 10, 2019 7:14 pm
They are estimates Larry but I'm basing it on hundreds of customers and what they used. I had one guy went through more than 20 ton a year in an old farmhouse that couldn't have been more that 1500 sq. ft. Another guy in home that was also about 1500 used 2 and he claimed it provided nearly all the heat for the season.
I agree! He should be well closer to 2 tons than to 20 tons. But add on some additional coal for being further north, and some additional coal for 75 degrees on the T-Stat....

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 7:28 pm

Richard S. wrote:
Tue. Sep. 10, 2019 7:14 pm
Another guy in home that was also about 1500 used 2 and he claimed it provided nearly all the heat for the season.
That sounds suspiciously like Freetown Fred. :lol:

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Tue. Sep. 10, 2019 7:48 pm

lsayre wrote:
Tue. Sep. 10, 2019 6:59 pm
It's all just guessing until there is a legitimate and aggressive (as in cutting it to the quick) 'Manual J' heat loss assessment. But for the cost of a Manual J assessment, he could buy roughly an extra 2/3 tons of coal. I'd probably just go for the extra coal.

My guess is that if 6 Manual J assessments were made, none of them would be in agreement.
If the Manual J assessments aren't going to agree with each other, how do you pick the one that is "legitimate"? :roll: Isn't it really all just guessing until the OP runs the unit for a season, or some fraction thereof, and we get to take a look at the actual coal use vs degree days?

Mike

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 10, 2019 8:13 pm

Pacowy wrote:
Tue. Sep. 10, 2019 7:48 pm
If the Manual J assessments aren't going to agree with each other, how do you pick the one that is "legitimate"? :roll: Isn't it really all just guessing until the OP runs the unit for a season, or some fraction thereof, and we get to take a look at the actual coal use vs degree days?

Mike
Yes, and this is precisely why I would spend the money on extra coal instead of a Manual J assessment.

 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Tue. Sep. 10, 2019 11:20 pm

He has a better house than mine, heating less space, and we heat the basement, and 13 x 26 foot garage every nite and the house never gets below 70 and I struggle to burn 7000lbs on the coldest of winters. I am still sticking to my 2 tons with 3 tons as a nice buffer.

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Thu. Sep. 12, 2019 8:35 am

Don't forget the minor impact of the windowstat days when its really warm enough to not need any heat but its too easy to just let the stoker idle away rather than shut it down and then relight. :P

When I moved from the hand fed to the stoker I increased my yearly coal usage because of the comparitively easy operation. I started it earlier in the year and ran it later, didn't burn any wood or as much propain in the shoulder months and left it running 99% of the time.

Since it doesn't go 'bad', I'd get 4 ton loose or 3 pallets of bagged and have some left over to start next year.

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Thu. Sep. 12, 2019 9:22 am

Get extra it won't go bad...
Get too little...
And you will feel the pain...
Besides weather in the heating season may prevent a top off in feb or mar...


Post Reply