LL AA-220 Relocation

 
lzaharis
Member
Posts: 2366
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Mon. Feb. 25, 2019 7:43 am

Hello and good morning Swyman,

Using my case with my old handfed and the stoker I have now as an example the barometric damper opens up and the firebox is bypassed if the air leaks into the home are large enough.
-----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
The barometric damper/draft regulator allows a constant regulated rate of draft to occur in the firebox with the forced air or natural draft combustion with a hand fed boiler. The weight on the draft door keeps the air in the room from entering the chimney and maintains the amount of draft required to maintain the needed water column reading to maintain the proper draft in the

If you have a downdraft in a chimney it does not allow the chimney draft to work properly and makes it too weak. A chimney extension with a rain cap helps to prevent down drafts as well to allow the chimney and barometric damper to work correctly and maintain negative water column reading at the flue breech.

If the draft as sensed by the barometric damper is too strong (maybe the wind over the chimney top is strong and increasing the draft):, in this case the draft inside the flue, at the breech at the draft regulator is more negative-maybe 1.2" water column.
Since the air in the room is at normal pressure it will be stronger than the pressure inside the flue, so the air inside the room will push the draft regulator door "in and make it open, letting room air into the chimney until, balanced by the setting of the weight
on the moving draft regulators door, the incoming room air enters the flue in enough volume to drop the draft pressure back to its desired setting.


 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Feb. 27, 2019 4:50 am

This has been a good year, the company I work for (FCA) just announced to us that they are investing $119 million to bring a new engine to be built at my plant and they will be starting immediately. What that means for me is lots of overtime which equals CHIMNEY! Just what I needed and with the chimney and extra $$$ I should be able to upgrade to a higher capacity boiler! If I start a new thread with one of those boring EFM's or S260's, how many pages do you think I'll hit, 2-3? I am very excited to get going!

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Wed. Feb. 27, 2019 11:24 am

Arrg Capt'n ya want the 260 AA or AHS...
Fer heatin' yar big pool...

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 27, 2019 11:34 am

CapeCoaler wrote:
Wed. Feb. 27, 2019 11:24 am
Arrg Capt'n ya want the 260 AA or AHS...
Fer heatin' yar big pool...
I believe the gross output of the AA or AHS 260 will prove to be a tad greater than the DF520, though in this regard they should be close. The AA or AHS will not likely need to be cleaned quite as often, if that matters. But there may be the occasional puff-back.

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Feb. 27, 2019 12:02 pm

CapeCoaler wrote:
Wed. Feb. 27, 2019 11:24 am
Arrg Capt'n ya want the 260 AA or AHS...
Fer heatin' yar big pool...
Honestly a AA or AHS 260 is my first choice judging by what I have read and nothing against the 520 guys but I think a 520 would be easier to find? What type of coal do either of these take and if multi what works the best? I like how my current boiler runs with buck compared to rice. I seem to have more control and produce a hotter fire with it. I guess I need to go through the archives and read as much as I can about the 2. Only thing I have seen bad about either is the "puff Backs" from the Axeman design but I still really know nothing about. Even newcomer bodyshoppat said he was experiencing them with a brand new unit? Something to be concerned about?

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Feb. 27, 2019 12:06 pm

CapeCoaler wrote:
Wed. Feb. 27, 2019 11:24 am
Arrg Capt'n ya want the 260 AA or AHS...
Fer heatin' yar big pool...
Not happening now, I removed the vault I had buried in the yard that housed the valves just at the beginning of this season. I think I am getting old as I don't want to do anymore digging around the house anymore if I don't have to! In the past I was always looking for an excuse to break out the backhoe and dig trenches!

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 27, 2019 1:51 pm

swyman wrote:
Wed. Feb. 27, 2019 12:02 pm
Only thing I have seen bad about either is the "puff Backs" from the Axeman design but I still really know nothing about. Even newcomer bodyshoppat said he was experiencing them with a brand new unit? Something to be concerned about?
You simply dial them out via changing the ashing settings. I had two or three when I switched from Blaschak to Lehigh, but as soon as I got the Lehigh dialed in, I haven't had a puff-back since.

AA-AHS burn buck and pea. EFM burns buck and rice.


 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Feb. 27, 2019 1:52 pm

You can burn smaller size nut all the way down to rice. The auger might not like the nut, but a hopper fed eshland or AHS that you fill manually would burn nut.

I’ve never had a puff back. It’s very simple to avoid, it’s just setting the fire height correctly. It’s a no brainer.

Whee you are located, I feel your gonna travel for any brand, so might as go with the best deal.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 27, 2019 1:52 pm

hotblast1357 wrote:
Wed. Feb. 27, 2019 1:52 pm
You can burn smaller size nut all the way down to rice. The auger might not like the nut, but a hopper fed eshland or AHS that you fill manually would burn nut.

I’ve never had a puff back. It’s very simple to avoid, it’s just setting the fire height correctly. It’s a no brainer.

Whee you are located, I feel your gonna travel for any brand, so might as go with the best deal.
Change coal suppliers and you may find that you have a couple.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Feb. 27, 2019 1:54 pm

lsayre wrote:
Wed. Feb. 27, 2019 1:52 pm
Change coal suppliers and you may find that you have a couple.
I don’t change coal suppliers.

If you set the fire correctly from the beginning you shouldn’t have any.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 27, 2019 1:56 pm

hotblast1357 wrote:
Wed. Feb. 27, 2019 1:54 pm
I don’t change coal suppliers.

If you set the fire correctly from the beginning you shouldn’t have any.
I wish I lived in your perfect world.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Feb. 27, 2019 5:47 pm

lsayre wrote:
Wed. Feb. 27, 2019 1:56 pm
I wish I lived in your perfect world.
Buy it by the tractor trailer load and you can lol

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 27, 2019 6:01 pm

hotblast1357 wrote:
Wed. Feb. 27, 2019 5:47 pm
Buy it by the tractor trailer load and you can lol
I wasn't referring to the coal. I was referring to setting it up to run perfectly from the very onset. That is always a hunt and peck sort of thing.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Feb. 27, 2019 6:43 pm

I feel like having a background in hand feeding coal stoves gives one a advantage with running these. The fire characteristics are the same. Unlike pot style and flat bed stokers.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Feb. 27, 2019 7:00 pm

swyman wrote:
Wed. Feb. 27, 2019 4:50 am
What that means for me is lots of overtime which equals CHIMNEY!
Amen to that!!!

In my opinion, there is no way to have a serious coal central heating system without a chimney.

As far as what boiler; keep in mind that the AA or AHS 260 has a lot more output than the EFM 520. I think you would be in EFM 700 territory if you want to beat a 260.

Again, I don't think there is any problem with your current boiler. If you put a bigger stoker underneath it, you would have all the heat you need. But, that's a whole conversion thing that you might not want to get involved in.

Chimney first, then you can dream of what coal burner to get.

-Don