motor won't stop running

Post Reply
 
kycoalminer
New Member
Posts: 3
Joined: Sun. Jan. 20, 2019 9:30 am
Hot Air Coal Stoker Stove: model 77-B
Coal Size/Type: stoker
Other Heating: none

Post by kycoalminer » Sun. Jan. 20, 2019 9:37 am

combustioneer model 77-B. replaced wiring and tried 3 different timer boxes but motor and auger runs non stop. possible solutions?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Jan. 20, 2019 5:17 pm

kycoalminer wrote:
Sun. Jan. 20, 2019 9:37 am
combustioneer model 77-B. replaced wiring and tried 3 different timer boxes but motor and auger runs non stop. possible solutions?
Something has to be mis-wired.
Have you tried it with thermostat wires (T.T.) disconnected from the timer box?
77B Wiring Diagram (Pg. 9).pdf
.PDF | 170.8KB | 77B Wiring Diagram (Pg. 9).pdf
Wiring.JPG
.JPG | 119.5KB | Wiring.JPG

 
kycoalminer
New Member
Posts: 3
Joined: Sun. Jan. 20, 2019 9:30 am
Hot Air Coal Stoker Stove: model 77-B
Coal Size/Type: stoker
Other Heating: none

Post by kycoalminer » Sun. Jan. 20, 2019 7:37 pm

yes. we think it could be the limit switch. no matter how hot it gets it wont open stopping the motor.wiring is correct had multiple people check it.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Jan. 21, 2019 12:05 am

kycoalminer wrote:
Sun. Jan. 20, 2019 7:37 pm
yes. we think it could be the limit switch. no matter how hot it gets it wont open stopping the motor.wiring is correct had multiple people check it.
That limit is not a day to day operational switch, but is a Safety Switch in the rare event some other control should fail you, it's sole operation is as a last resort to shut down the burner. Day to day operational control is the wall thermostat and the timer box.

If you haven't yet, disconnect the 2 T.T. wires from the timer box, do that, and that should stop the burner and if it does stop it then that is your indicator to look closer at the thermostat and or thermostat wiring as being the "short" or faulty culprit.
Sometimes the 2 wires get shorted at a box entry connector or at a wire staple pounded in just a wee too tight...

Running a new wire may be a easier task than trying to locate the problem and fixing it...

 
kycoalminer
New Member
Posts: 3
Joined: Sun. Jan. 20, 2019 9:30 am
Hot Air Coal Stoker Stove: model 77-B
Coal Size/Type: stoker
Other Heating: none

Post by kycoalminer » Mon. Jan. 21, 2019 4:37 am

Ok thanks. we put in a new thermostat and wiring. someone told me that i can set the timer and check the momentary switch. do you know how to set or reset the timer?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Jan. 21, 2019 9:59 pm

I don't know what timer you have there, but with multiple people wire checking and all new wiring you may need someone more divine than an electrician to intervene. :P

Post Reply