LL AA-220 Relocation

User avatar
nepacoal
Member
Posts: 368
Joined: Wed. Nov. 21, 2012 7:49 am
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly"
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck
Location: NEPA

Post By: nepacoal » Thu. Jan. 10, 2019 8:03 am

-.01 is a little low for over fire draft. Lowering flue draft would lower it even further, right. I'd leave it as is or maybe lower combustion air slightly to get closer to -.015 per the manual. You seem to check on it at least daily so you're probably OK at -.01, but it will drop fast once your PV starts ashing up.

Visit Alternate Heating Sytems

User avatar
lsayre
Member
Posts: 15747
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post By: lsayre » Thu. Jan. 10, 2019 8:22 am

swyman wrote:
Thu. Jan. 10, 2019 7:14 am
Finally had some cold, well colder weather....low 20's with a strong NNW wind. Absolutely no propane fire cycles and boiler is keeping up on it's own!
Good to hear this!

User avatar
swyman
Member
Posts: 1224
Joined: Mon. Apr. 13, 2015 9:50 pm
Stoker Coal Boiler: Leisure Line AA-220
Coal Size/Type: Lehigh Rice/Buck
Location: Blissfield, MI

Post By: swyman » Thu. Jan. 10, 2019 8:40 am

lsayre wrote:
Thu. Jan. 10, 2019 8:22 am
Good to hear this!
Larry, do you think I would benefit to changing the flue draft to .04 from .05?

User avatar
lsayre
Member
Posts: 15747
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post By: lsayre » Thu. Jan. 10, 2019 9:56 am

swyman wrote:
Thu. Jan. 10, 2019 8:40 am
Larry, do you think I would benefit to changing the flue draft to .04 from .05?
I have no knowledge of power vents.

User avatar
swyman
Member
Posts: 1224
Joined: Mon. Apr. 13, 2015 9:50 pm
Stoker Coal Boiler: Leisure Line AA-220
Coal Size/Type: Lehigh Rice/Buck
Location: Blissfield, MI

Post By: swyman » Thu. Jan. 10, 2019 11:47 am

lsayre wrote:
Thu. Jan. 10, 2019 9:56 am
I have no knowledge of power vents.
I don't see where that would make a difference...draft at breech is what it is weather it's being pulled from a chimney or power vent correct? The baro sets the breech draft and my theory is -.04 is a slower draft than -.05 but I don't know how much? Also not sure if it would affect the over fire draft it I went down to -.04. Guess I'll have to experiment.

User avatar
hotblast1357
Member
Posts: 4463
Joined: Mon. Mar. 10, 2014 10:06 pm
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: oil furnace
Location: Peasleeville NY

Post By: hotblast1357 » Thu. Jan. 10, 2019 12:19 pm

Leave it alone, it’s working.

CapeCoaler
Member
Posts: 5109
Joined: Sun. Feb. 10, 2008 3:48 pm
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove
Location: Cape Cod, MA

Post By: CapeCoaler » Thu. Jan. 10, 2019 7:44 pm

It is working well!...
LOL...

User avatar
McGiever
Member
Posts: 7467
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: RICE,PEA,NUT,STOVE /ANTHRACITE and EGG / BIT
Other Heating: Ground Source Heat Pump and some Solar
Location: Junction of PA-OH-WV

Post By: McGiever » Thu. Jan. 10, 2019 11:10 pm

swyman wrote:
Thu. Jan. 10, 2019 7:14 am
Finally had some cold, well colder weather....low 20's with a strong NNW wind. Absolutely no propane fire cycles and boiler is keeping up on it's own! One thing that confuses me is I installed a foam board cover for the refractory cover and it's still 90* in the boiler room? I thought for sure that cover was radiating all that heat but could it be coming from the 1 1/2" pipes? ANyway was good to finally check settings under a heavy load and I have the fire settings as close to perfect as I have ever had them. Full grate of fire and my draft almost to factory spec...... .01 over fire and .05 at breech. If I went to .04 at breech would that slow down the draft just a fuzz to get more heat absorption in the water?
hotblast1357 wrote:
Thu. Jan. 10, 2019 12:19 pm
Leave it alone, it’s working.
CapeCoaler wrote:
Thu. Jan. 10, 2019 7:44 pm
It is working well!...
LOL...
And it will never be the same as a chimney! A good chimney gets cleaned once a year even if it doesn't need cleaned.

Performance of a PV degrades minute by minute, day by day. :)

Visit Alternate Heating Sytems

User avatar
swyman
Member
Posts: 1224
Joined: Mon. Apr. 13, 2015 9:50 pm
Stoker Coal Boiler: Leisure Line AA-220
Coal Size/Type: Lehigh Rice/Buck
Location: Blissfield, MI

Post By: swyman » Fri. Jan. 11, 2019 7:03 am

McGiever wrote:
Thu. Jan. 10, 2019 11:10 pm

Performance of a PV degrades minute by minute, day by day. :)
True statement! I feel it is in my best interest to have a chimney built. I need to get a chimney quote so I will know for sure how much I need to save and set a fund aside... it is an inconvenience cleaning for sure.

User avatar
hotblast1357
Member
Posts: 4463
Joined: Mon. Mar. 10, 2014 10:06 pm
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: oil furnace
Location: Peasleeville NY

Post By: hotblast1357 » Fri. Jan. 11, 2019 7:11 am

It did not cost me much to build mine.. but if your uncomfortable doing it yourself I understand.

User avatar
swyman
Member
Posts: 1224
Joined: Mon. Apr. 13, 2015 9:50 pm
Stoker Coal Boiler: Leisure Line AA-220
Coal Size/Type: Lehigh Rice/Buck
Location: Blissfield, MI

Post By: swyman » Fri. Jan. 11, 2019 9:46 am

Here is a pic of where it would have to go. I have the first overhang from the new addition and then the massive overhang at the peak of the gable end. How would you do it? Remove the siding from that side of the house and block up attaching to house every so many feet and just cut the overhangs and flash around? I would just want to make sure it would last. And how do you come out of the basement to attach, just a triple walled piece above ground to tie into the base of the chimney?
20180809_082738.jpg

User avatar
hotblast1357
Member
Posts: 4463
Joined: Mon. Mar. 10, 2014 10:06 pm
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: oil furnace
Location: Peasleeville NY

Post By: hotblast1357 » Fri. Jan. 11, 2019 9:50 am

Yes to the siding and overhangs.

You need to dig down and put a good size footer in, a lot of weight in a chimney, and then you put the flue through the concrete wall under grade.

User avatar
swyman
Member
Posts: 1224
Joined: Mon. Apr. 13, 2015 9:50 pm
Stoker Coal Boiler: Leisure Line AA-220
Coal Size/Type: Lehigh Rice/Buck
Location: Blissfield, MI

Post By: swyman » Fri. Jan. 11, 2019 9:55 am

hotblast1357 wrote:
Fri. Jan. 11, 2019 9:50 am


You need to dig down and put a good size footer in, a lot of weight in a chimney, and then you put the flue through the concrete wall under grade.
So would you put the flue in the footer or dig really deep and start the block say 3' below grade and put the flue in that? How would you clan that, by taking the flue apart from the inside? Seems like a lot of dust would settle there.

User avatar
hotblast1357
Member
Posts: 4463
Joined: Mon. Mar. 10, 2014 10:06 pm
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: oil furnace
Location: Peasleeville NY

Post By: hotblast1357 » Fri. Jan. 11, 2019 10:23 am

You should go down below frost, put a pad in as a footer, then just start stacking your blocks. The bottom block gets the clean out, this is usually at floor grade inside or a little higher, then just stack your block and flue up as you go, and put the round flue in through the wall where you need it to go, as high as possible I advise.

CapeCoaler
Member
Posts: 5109
Joined: Sun. Feb. 10, 2008 3:48 pm
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove
Location: Cape Cod, MA

Post By: CapeCoaler » Fri. Jan. 11, 2019 10:37 am

And Insulate between block and round tile...

Visit Alternate Heating Sytems