Post by lsayre » Sun. Jun. 17, 2018 12:45 pm

hotblast1357 wrote:
Sun. Jun. 17, 2018 12:26 pm
The best and only way to know, is to measure what you put in the hopper.
Absolutely!


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Jun. 17, 2018 1:20 pm

I will be up creek next year with my auger installed.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jun. 17, 2018 2:47 pm

hotblast1357 wrote:
Sun. Jun. 17, 2018 1:20 pm
I will be up creek next year with my auger installed.
You should have a pretty decent grasp of your systems needs by now.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Jun. 17, 2018 2:59 pm

lsayre wrote:
Sun. Jun. 17, 2018 2:47 pm
You should have a pretty decent grasp of your systems needs by now.
Oh I do, but I just like to know all the time lol

I will do a feed run anyways to see what it moves per minute/hour.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 17, 2018 7:31 pm

Well, so much for being amazed. I was up late last night and as I was turning the lights out to go to bed, I heard the Axeman running. It seemed odd so I went out to have a look.

The fire was out and it had been running for two and a half hours!
IMG_2708.JPG
.JPG | 350KB | IMG_2708.JPG
IMG_2709.JPG
.JPG | 380KB | IMG_2709.JPG
IMG_2710.JPG
.JPG | 374.2KB | IMG_2710.JPG
IMG_2711.JPG
.JPG | 328.5KB | IMG_2711.JPG
I shut it off and went to bed.

This morning I stuck 4 pieces of charcoal in and torched'em up.
IMG_2713.JPG
.JPG | 303.1KB | IMG_2713.JPG
Put the ashing block in.
IMG_2714.JPG
.JPG | 355.1KB | IMG_2714.JPG
30 minutes later....
IMG_2715.JPG
.JPG | 367KB | IMG_2715.JPG
The charcoal was just about burnt up and no coal fire. WHAT!?!?! :o

Maybe I didn't use enough charcoal. So I put about 10 pieces in. 30 minutes later...
IMG_2716.JPG
.JPG | 337.3KB | IMG_2716.JPG
Still no coal fire. :annoyed:

I decided to have a look at the swirl tube, stove pipe and chimney.
IMG_2717.JPG
.JPG | 369.8KB | IMG_2717.JPG
Got a good bit of ash out of the 5" stove pipe section.
IMG_2718.JPG
.JPG | 311.4KB | IMG_2718.JPG
Pope's Hat.
IMG_2719.JPG
.JPG | 306.6KB | IMG_2719.JPG
Noth'in down in there.
IMG_2720.JPG
.JPG | 292.5KB | IMG_2720.JPG
Pulled the clean out off the chimney.
IMG_2723.JPG
.JPG | 229.2KB | IMG_2723.JPG
Noth'in up there.
IMG_2724.JPG
.JPG | 242.2KB | IMG_2724.JPG
.
I decided to pull the belt off of the auger, hand crank all the coal off of the grate and install a new ash bed.
IMG_2725.JPG
.JPG | 323.6KB | IMG_2725.JPG
An hour later...
IMG_2726.JPG
.JPG | 334.7KB | IMG_2726.JPG
All is well now!

My guess is the out-fire was caused by the stove pipe being partly blocked. The trouble getting it lit was probably a combination of the blockage and no ash on the grate.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jun. 17, 2018 8:30 pm

I've had loads of trouble lighting my AHS Coal Gun with charcoal briquettes, and particularly more so with Royal Oak brand. No such trouble when I use natural wood charcoal.

What brand of anthracite gave you the outfire?

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Mon. Jun. 18, 2018 5:33 am

Wow that’s strange indeed!

It was 92 here yesterday, I had 0 draft, and no problem, it only went to 65 last night, and is suppose to be north of 90 again today.


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Mon. Jun. 18, 2018 8:23 am

I just noticed that you only used 4 pieces of charcoal to light the AA. AHS instructed me to jam 10-12 chunks in when starting the Coal Gun.

Edit: Oops, I just noticed where you followed up with 10. Best advice is to try 10 - 12 roughly briquette sized chunks of natural lump charcoal.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Jun. 18, 2018 6:43 pm

lsayre wrote:
Sun. Jun. 17, 2018 8:30 pm
What brand of anthracite gave you the outfire?
The same Blaschak Pea that I have had all along. This is the bottom of the bin variety though.

This morning it was still looking fine. When I got home from work 12 hours later, it was out again. It is struggling to re-lite now. I have not had any trouble re-liting until now.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Mon. Jun. 18, 2018 6:55 pm

StokerDon wrote:
Mon. Jun. 18, 2018 6:43 pm
The same Blaschak Pea that I have had all along. This is the bottom of the bin variety though.

This morning it was still looking fine. When I got home from work 12 hours later, it was out again. It is struggling to re-lite now. I have not had any trouble re-liting until now.

-Don
You are burning my favorite summer coal. Do you have any measurable draft?

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Mon. Jun. 18, 2018 6:56 pm

I don’t think you are establishing a full enough fire now.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Mon. Jun. 18, 2018 6:59 pm

hotblast1357 wrote:
Mon. Jun. 18, 2018 6:56 pm
I don’t think you are establishing a full enough fire now.
Before he can run DHW and establish a full fire, he first needs to establish a fire. He says he's having difficulty doing this. I suggest lump coal for this. Summer fires require extraneous measures.

Don, when you had it apart, did you pull the Popes Hat and brush out the channel that runs from behind the hat down into the swirl chamber?

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Jun. 18, 2018 7:28 pm

lsayre wrote:
Mon. Jun. 18, 2018 6:55 pm
Do you have any measurable draft?
No, The draft stays at zero at idle, when it's lit. On a DHW call it gets to -.01 to -.02.
lsayre wrote:
Mon. Jun. 18, 2018 6:59 pm
Don, when you had it apart, did you pull the Popes Hat and brush out the channel that runs from behind the hat down into the swirl chamber?
No , I didn't pull the Pope's Hat. I didn't see anything down in the chamber so I moved on. I guess if something gets between the Pope's Hat and the chamber inlet, that would cause problems.

The fire is recovering well now. One thing I noticed is opening the ash door sped things up a bit.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Jun. 18, 2018 8:06 pm

It's back up and running now.
IMG_2738.JPG
.JPG | 162.4KB | IMG_2738.JPG
IMG_2735.JPG
.JPG | 350.6KB | IMG_2735.JPG
IMG_2736.JPG
.JPG | 280.5KB | IMG_2736.JPG
IMG_2737.JPG
.JPG | 268.9KB | IMG_2737.JPG
.
I also wired the timer in just to see if that helps. It's set for 1 minute, 15 seconds every hour.
IMG_2734.JPG
.JPG | 369.4KB | IMG_2734.JPG
I dropped the ashing temperature from 120 to 115.

-Don

 
User avatar
Rob R.
Site Moderator
Posts: 18002
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Jun. 18, 2018 8:27 pm

I also wired the timer in just to see if that helps. It's set for 1 minute, 15 seconds every hour.
That seems like a good start. Axeman sends them out with a timer for a reason.