EFM 520 Sulfur Smell From Hopper

Post Reply
 
curtsgunshop
New Member
Posts: 3
Joined: Fri. Jan. 22, 2016 1:53 pm
Stoker Coal Boiler: 520
Coal Size/Type: rice

Post by curtsgunshop » Thu. Apr. 14, 2016 9:34 am

We are experiencing a sulfur smell coming from the hopper and we've troubleshooted what we thought it may be does anyone know why we are getting this smell?

 
User avatar
warminmn
Member
Posts: 8110
Joined: Tue. Feb. 08, 2011 5:59 pm
Location: Land of 11,842 lakes
Hand Fed Coal Stove: Chubby Junior, Efel Nestor Martin, Riteway 37
Coal Size/Type: nut and stove anthracite, lignite
Other Heating: Wood and wear a wool shirt

Post by warminmn » Thu. Apr. 14, 2016 9:37 am

I'll leave most of the answer to stoker experts, but if you don't have a working, tested, CO detector I would open a window. I probably would anyway until you know you don't have a high CO level. Sulfur is what anthracite coal gasses smell like.

 
User avatar
SWPaDon
Member
Posts: 9857
Joined: Sun. Nov. 24, 2013 12:05 pm
Location: Southwest Pa.
Hand Fed Coal Furnace: Clayton 1600M
Coal Size/Type: Bituminous
Other Heating: Oil furnace

Post by SWPaDon » Thu. Apr. 14, 2016 9:38 am

Possibly lost your draft. Do you have a manometer to check it? And most importantly do you have working carbon monoxide detectors.........what you are smelling is deadly.

Shut down til you figure it out.

Need more info on what you've troubleshooted, as well as more info on your setup.


 
User avatar
Sunny Boy
Member
Posts: 25562
Joined: Mon. Nov. 11, 2013 1:40 pm
Location: Central NY
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace

Post by Sunny Boy » Thu. Apr. 14, 2016 10:46 am

SWPaDon wrote:Possibly lost your draft. Do you have a manometer to check it? And most importantly do you have working carbon monoxide detectors.........what you are smelling is deadly.

Shut down til you figure it out.

Need more info on what you've troubleshooted, as well as more info on your setup.
Or, if it was fine during the colder weather, it may be back drafting occasionally due to low draft pressure. Especially easy to happen if your weather is warming up. Some stove/chimney setups don't do well at low draft pressures that can be caused by warmer weather.

If so, you need to open the dampers more and run the stove hotter to get the draft hotter/stronger, or shut down the stove for the season.

Paul

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Thu. Apr. 14, 2016 11:21 am

CO monitor is a MUST.

As mentioned warmer weather will hurt draft. What worked in cold weather may be marginal to not working at all in warmer temps. Check the exhaust pipes, fly ash build up in exhaust pipes that didn't hurt draft in colder weather can be deadly in warmer weather.

Manometer is very good to have so you can see the difference in draft before it starts putting CO in the house.

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Thu. Apr. 14, 2016 11:28 am

I agree with Paul that sometimes in the spring the effort to idle down and conserve coal sometimes goes to far, and may undermine the chimney draft. And with titleist1 about fly ash build-up in flue pipes. What feed/air and timer settings are being used?

Other possible contributing factors may be:

- Air vent holes in auger pipe blocked (e.g., if coal contains wet fines)
- Lack of make-up air; exhaust fans, other chimneys in house, etc. drawing air from boiler room
- Boiler passages or thimble area of chimney full of fly ash or other obstructions
- Excessive air leaks into boiler/base
- Excessive combustion air (fire burning too low in pot).

Most/all of these are mentioned in the manual and have been discussed in other threads if more info required.

Mike


 
User avatar
SWPaDon
Member
Posts: 9857
Joined: Sun. Nov. 24, 2013 12:05 pm
Location: Southwest Pa.
Hand Fed Coal Furnace: Clayton 1600M
Coal Size/Type: Bituminous
Other Heating: Oil furnace

Post by SWPaDon » Thu. Apr. 14, 2016 10:28 pm

No response from the OP. We have no idea if it's fixed, shut down, or if he died from CO poisoning. I pray that it wasn't the latter.

 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Sat. Apr. 16, 2016 9:35 am

Man I HATE it when guys come in here and post something like this and then don't follow up. Hope he is OK!!!!!!

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sat. Apr. 16, 2016 10:15 am

He visited yesterday after Pacowy's post.

 
User avatar
SWPaDon
Member
Posts: 9857
Joined: Sun. Nov. 24, 2013 12:05 pm
Location: Southwest Pa.
Hand Fed Coal Furnace: Clayton 1600M
Coal Size/Type: Bituminous
Other Heating: Oil furnace

Post by SWPaDon » Sat. Apr. 16, 2016 1:22 pm

coaledsweat wrote:He visited yesterday after Pacowy's post.
Pacoway's post was 2 days ago. Going by his name on here, the only Curt's Gun Shop I could find is in Mifflinville, Pa.. The last death I could find in the Mifflinville obituaries was on Feb. 28th. . The last post on Curt's Gun Shop facebook page was 2 hours before the post here.

Dunno if it's the same person though.

Post Reply