We are experiencing a sulfur smell coming from the hopper and we've troubleshooted what we thought it may be does anyone know why we are getting this smell?
- warminmn
- Member
- Posts: 8185
- Joined: Tue. Feb. 08, 2011 5:59 pm
- Location: Land of 11,842 lakes
- Hand Fed Coal Stove: Chubby Junior, Riteway 37
- Coal Size/Type: nut and stove anthracite, lignite
- Other Heating: Wood and wear a wool shirt
I'll leave most of the answer to stoker experts, but if you don't have a working, tested, CO detector I would open a window. I probably would anyway until you know you don't have a high CO level. Sulfur is what anthracite coal gasses smell like.
- SWPaDon
- Member
- Posts: 9857
- Joined: Sun. Nov. 24, 2013 12:05 pm
- Location: Southwest Pa.
- Hand Fed Coal Furnace: Clayton 1600M
- Coal Size/Type: Bituminous
- Other Heating: Oil furnace
Possibly lost your draft. Do you have a manometer to check it? And most importantly do you have working carbon monoxide detectors.........what you are smelling is deadly.
Shut down til you figure it out.
Need more info on what you've troubleshooted, as well as more info on your setup.
Shut down til you figure it out.
Need more info on what you've troubleshooted, as well as more info on your setup.
- Sunny Boy
- Member
- Posts: 25706
- Joined: Mon. Nov. 11, 2013 1:40 pm
- Location: Central NY
- Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
- Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
- Coal Size/Type: Nuts !
- Other Heating: Oil &electric plenum furnace
Or, if it was fine during the colder weather, it may be back drafting occasionally due to low draft pressure. Especially easy to happen if your weather is warming up. Some stove/chimney setups don't do well at low draft pressures that can be caused by warmer weather.SWPaDon wrote:Possibly lost your draft. Do you have a manometer to check it? And most importantly do you have working carbon monoxide detectors.........what you are smelling is deadly.
Shut down til you figure it out.
Need more info on what you've troubleshooted, as well as more info on your setup.
If so, you need to open the dampers more and run the stove hotter to get the draft hotter/stronger, or shut down the stove for the season.
Paul
CO monitor is a MUST.
As mentioned warmer weather will hurt draft. What worked in cold weather may be marginal to not working at all in warmer temps. Check the exhaust pipes, fly ash build up in exhaust pipes that didn't hurt draft in colder weather can be deadly in warmer weather.
Manometer is very good to have so you can see the difference in draft before it starts putting CO in the house.
As mentioned warmer weather will hurt draft. What worked in cold weather may be marginal to not working at all in warmer temps. Check the exhaust pipes, fly ash build up in exhaust pipes that didn't hurt draft in colder weather can be deadly in warmer weather.
Manometer is very good to have so you can see the difference in draft before it starts putting CO in the house.
-
- Member
- Posts: 3555
- Joined: Tue. Sep. 04, 2007 10:14 pm
- Location: Dalton, MA
- Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
- Coal Size/Type: Buckwheat/anthracite
I agree with Paul that sometimes in the spring the effort to idle down and conserve coal sometimes goes to far, and may undermine the chimney draft. And with titleist1 about fly ash build-up in flue pipes. What feed/air and timer settings are being used?
Other possible contributing factors may be:
- Air vent holes in auger pipe blocked (e.g., if coal contains wet fines)
- Lack of make-up air; exhaust fans, other chimneys in house, etc. drawing air from boiler room
- Boiler passages or thimble area of chimney full of fly ash or other obstructions
- Excessive air leaks into boiler/base
- Excessive combustion air (fire burning too low in pot).
Most/all of these are mentioned in the manual and have been discussed in other threads if more info required.
Mike
Other possible contributing factors may be:
- Air vent holes in auger pipe blocked (e.g., if coal contains wet fines)
- Lack of make-up air; exhaust fans, other chimneys in house, etc. drawing air from boiler room
- Boiler passages or thimble area of chimney full of fly ash or other obstructions
- Excessive air leaks into boiler/base
- Excessive combustion air (fire burning too low in pot).
Most/all of these are mentioned in the manual and have been discussed in other threads if more info required.
Mike
- SWPaDon
- Member
- Posts: 9857
- Joined: Sun. Nov. 24, 2013 12:05 pm
- Location: Southwest Pa.
- Hand Fed Coal Furnace: Clayton 1600M
- Coal Size/Type: Bituminous
- Other Heating: Oil furnace
No response from the OP. We have no idea if it's fixed, shut down, or if he died from CO poisoning. I pray that it wasn't the latter.
- coalkirk
- Member
- Posts: 5185
- Joined: Wed. May. 17, 2006 8:12 pm
- Location: Forest Hill MD
- Stoker Coal Boiler: 1981 EFM DF520 retired
- Hand Fed Coal Stove: Jotul 507 on standby
- Coal Size/Type: Lehigh anthracite/rice coal
Man I HATE it when guys come in here and post something like this and then don't follow up. Hope he is OK!!!!!!
- coaledsweat
- Site Moderator
- Posts: 13766
- Joined: Fri. Oct. 27, 2006 2:05 pm
- Location: Guilford, Connecticut
- Stoker Coal Boiler: Axeman Anderson 260M
- Coal Size/Type: Pea
He visited yesterday after Pacowy's post.
- SWPaDon
- Member
- Posts: 9857
- Joined: Sun. Nov. 24, 2013 12:05 pm
- Location: Southwest Pa.
- Hand Fed Coal Furnace: Clayton 1600M
- Coal Size/Type: Bituminous
- Other Heating: Oil furnace
Pacoway's post was 2 days ago. Going by his name on here, the only Curt's Gun Shop I could find is in Mifflinville, Pa.. The last death I could find in the Mifflinville obituaries was on Feb. 28th. . The last post on Curt's Gun Shop facebook page was 2 hours before the post here.coaledsweat wrote:He visited yesterday after Pacowy's post.
Dunno if it's the same person though.