by Highlander » Sat. Feb. 02, 2008 9:00 pm
Hello fellow Coalburners
I started with a Harman Magnum stove, and was impressed with the quality of the product. My existing propane boiler was failing and given the ever increasing price of propane, decided to go with coal.
As with the Harman Magnum, I decided against using the simple full on or pilot mode control that Harman still ships with these units and designed a micro PLC based control system for the boiler. In many ways its similar to the Coaltrol, in that it provides a proportional control for stoker on/off time vs the idle or full on most manufacturers still cling to.
It is the same PLC, a Crouzet M2, that I used with the first Harman stove, but the program has grown substantially and includes reset control, proportional / integral control mode, a coal useage counter, a reverse anticipator fucntion, and a scrollable display for water temp, outside temp, manual control mode, Summer / Winter mode and a coal useage counter. The PLC can read 0-10V signals with 8 bits of precision, not great by todays standards, but plenty for this level of process control.
The boiler water temp is monitored by a Crouzet temperature transmitter, this unit, the grey box on top of the boiler transmits a 0-10V signal proportional to the water temp to the PLC. The outdoor temperature is monitored by a small temp sensor with a probe in the outdoor combustion air inlet. This sensor provides another 0-10V signal, that the PLC monitors and adds to the temp setpoint when the outdoor air temp starts to drop below 30 deg.
Ive reconfigured the esisting Johnson controls to provide a two tiered overtemp limit control that will initially energize the fan coil to dump excess heat, and then if the temp continues to rise, will cut power to the stoker and combustion air blower to try and bring the temperature down by cutting off the fuel supply.
Ive added an outside air supply to the combustion blower and a speed control to the blower motor. When stoking the blower runs full tilt, but then cuts back to an idle speed that helps keep a larger fire bed in times of low demand.
A small muffin fan was added to the stoker cover and is wired with the stoker motor, provides cooling to the motor during prolonged periods of operation, since thse motors can run very hot.
A Tripplite APS with a size 29 marine deep cycle battery provide 8 to 12 hours of backup time in the event of a power failure, and prove a measure of surge protection on the incoming line power.
So far Im very pleased with the operation of this unit, my coal useage for the month of January has been about 50# per day, and provides both heat and hot water for a 2000 sq ft house. During the summer months I burned about 12# per day for hot water. I estimate using between 4 and 5 tons for the year. With propane at $3 / gallon, it should have payback in 2 years for an investment of about $5000. Not too shabby.