Your supply comes out of the top of the boiler your return goes in the back on the bottom. Your primary circuit should be atleast 1" if not 1.25" depending on Btu demand of radiators, and how many zones you have "T"ing off of that boiler loop.
Before spending a ton of money on copper and fittings you might want to check out some simple primary/secondary piping schematics.
Before spending a ton of money on copper and fittings you might want to check out some simple primary/secondary piping schematics.
-
- Verified Business Rep.
- Posts: 207
- Joined: Wed. Aug. 26, 2015 6:43 pm
- Location: Belleville, New York
- Stoker Coal Boiler: DS Machines. Keystoker
- Hand Fed Coal Boiler: DS Machines Aqua Gem
- Hot Air Coal Stoker Furnace: Koker 160
- Hot Air Coal Stoker Stove: Anthra Glo
- Hand Fed Coal Stove: Anthramax Comfort Max
- Hand Fed Coal Furnace: DS Kozy King
- Coal Size/Type: Nut, Rice and Stove
- Other Heating: Gas and pellet stoves
- Contact:
Can you take a couple of close ups of the top? And what size copper is that? I don’t know the length of your zones but there should be two 2 inch feeds coming off the top and the same for the returns on the back. We come off with 2 inch black iron and then reduce down to either 1 1/2 or 1 inch minimum.
Last edited by jremington on Sat. Feb. 15, 2020 8:31 am, edited 1 time in total.
-
- Verified Business Rep.
- Posts: 207
- Joined: Wed. Aug. 26, 2015 6:43 pm
- Location: Belleville, New York
- Stoker Coal Boiler: DS Machines. Keystoker
- Hand Fed Coal Boiler: DS Machines Aqua Gem
- Hot Air Coal Stoker Furnace: Koker 160
- Hot Air Coal Stoker Stove: Anthra Glo
- Hand Fed Coal Stove: Anthramax Comfort Max
- Hand Fed Coal Furnace: DS Kozy King
- Coal Size/Type: Nut, Rice and Stove
- Other Heating: Gas and pellet stoves
- Contact:
DS taught me how to install their boilers so I might be a little backwoods but I’m a little confused on what I’m seeing. Where the Sampson regulator going?Jlinde37 wrote: ↑Fri. Feb. 14, 2020 8:37 pmYour supply comes out of the top of the boiler your return goes in the back on the bottom. Your primary circuit should be atleast 1" if not 1.25" depending on Btu demand of radiators, and how many zones you have "T"ing off of that boiler loop.
Before spending a ton of money on copper and fittings you might want to check out some simple primary/secondary piping schematics.
When I bought this unit used it came with the blower so we're hooking up the blower instead of a sampson.
The pipes coming out of the ground is what I put in and they are inch and a quarter I think they reduced everything down to an inch though
The pipes coming out of the ground is what I put in and they are inch and a quarter I think they reduced everything down to an inch though
Attachments
-
- Member
- Posts: 89
- Joined: Sat. Jan. 06, 2018 9:40 am
- Location: Ellicottville, Ny
- Hand Fed Coal Boiler: DS Aquagem 3200
- Coal Size/Type: Nut/Pea
I highly reccomend the use of the samson. It does an excellent job metering air in very fine increments. I've tried using the blower on mine it helps getting a fire lit but after that it just blows all the heat out the chimney.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Coal needs Samson Valve
Blower is a wood thing...
Blower is a wood thing...
-
- Verified Business Rep.
- Posts: 207
- Joined: Wed. Aug. 26, 2015 6:43 pm
- Location: Belleville, New York
- Stoker Coal Boiler: DS Machines. Keystoker
- Hand Fed Coal Boiler: DS Machines Aqua Gem
- Hot Air Coal Stoker Furnace: Koker 160
- Hot Air Coal Stoker Stove: Anthra Glo
- Hand Fed Coal Stove: Anthramax Comfort Max
- Hand Fed Coal Furnace: DS Kozy King
- Coal Size/Type: Nut, Rice and Stove
- Other Heating: Gas and pellet stoves
- Contact:
Do not use the blower with coal. Seriously. Are you feeding with both top feeds? I’d have your installers call Ben at DS before going further.
-
- Verified Business Rep.
- Posts: 207
- Joined: Wed. Aug. 26, 2015 6:43 pm
- Location: Belleville, New York
- Stoker Coal Boiler: DS Machines. Keystoker
- Hand Fed Coal Boiler: DS Machines Aqua Gem
- Hot Air Coal Stoker Furnace: Koker 160
- Hot Air Coal Stoker Stove: Anthra Glo
- Hand Fed Coal Stove: Anthramax Comfort Max
- Hand Fed Coal Furnace: DS Kozy King
- Coal Size/Type: Nut, Rice and Stove
- Other Heating: Gas and pellet stoves
- Contact:
That all looks confusing. Let’s start fresh. Do you have 2 feeds off the top and 2 returns on the back bottom of the boiler? Both being 2 inch at the boiler? Something looks like it’s been put into the Sampson regulator fitting. And are there two separate feeds going to the house, both being their own zones? And where is the low pressure regulator feeding the boiler? Those pictures are making my eyes bleed lol. And didn’t you say your running the pumps 24/7?
-
- Verified Business Rep.
- Posts: 207
- Joined: Wed. Aug. 26, 2015 6:43 pm
- Location: Belleville, New York
- Stoker Coal Boiler: DS Machines. Keystoker
- Hand Fed Coal Boiler: DS Machines Aqua Gem
- Hot Air Coal Stoker Furnace: Koker 160
- Hot Air Coal Stoker Stove: Anthra Glo
- Hand Fed Coal Stove: Anthramax Comfort Max
- Hand Fed Coal Furnace: DS Kozy King
- Coal Size/Type: Nut, Rice and Stove
- Other Heating: Gas and pellet stoves
- Contact:
And it’s just my opinion but the pump should be on the return. Can we start over?