Central Boiler FORGE 3500 Outdoor Coal Boiler

Post Reply
 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Dec. 07, 2018 2:30 pm

That is all correct, yes. Except for the widows. They are closed, unless like you mentioned it's warm outside.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Dec. 07, 2018 4:14 pm

Page 1 post 4:

McGiever wrote:
Wed. Nov. 28, 2018 10:31 am
With that much coal burning o n the grate there should be no shortage of heat available...you are correct to assume a flow or lack of flow issue.
Before condemning the pump be sure the system has all the air pockets purged...power purged, by garden hose...not by circulator.

Air pockets anywhere along/in that single loop can choke any size pump down to a dribble of flow.

Anyways, that would be my first step before any disassembly and/or opening the check-book.


Guess my comment on possible air in loop piping choking down available flow capacity was a dud idea. Remember power purge comment?

Would be ashame to of missed a 30 minute fix, if that could of made a small improvement...undersized rads running at fraction of their potential is a double whammy

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Dec. 07, 2018 4:50 pm

The quick fix? The two zone valves are marked N/C and N/O (normally closed and normally open). Both loops can be set up to circulate continuously so neither one freezes. When the T-Stat calls for heat in the house N/C opens and N/O closes. When the T-Stat heat call is satisfied N/C closes and N/O opens.

Screenshot from 2018-12-07 16-45-49.png
.PNG | 52KB | Screenshot from 2018-12-07 16-45-49.png
Last edited by lsayre on Fri. Dec. 07, 2018 4:54 pm, edited 1 time in total.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Dec. 07, 2018 4:53 pm

Yeah thanks for bringing that back up Mac. We should do that. Just disconnect at the boiler and shove a hose into the pex? Would that suffice?

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Dec. 07, 2018 5:13 pm

Larry, is that pump thermally protected? Will it shut down if it gets too hot, do you know?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Dec. 07, 2018 5:59 pm

Lightning wrote:
Fri. Dec. 07, 2018 5:13 pm
Larry, is that pump thermally protected? Will it shut down if it gets too hot, do you know?
Now you have me really confused. I've sent 225 degree water through mine often enough to know that an unpressurized system achieving at best 212 degrees (and likely less due to altitude) will have no issues.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Dec. 07, 2018 6:04 pm

Well, I meant the motor. Is it thermally protected? Or will it run non stop no problem? The reason I ask is because the motor feels quite hot to the touch.


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Dec. 07, 2018 6:10 pm

Lightning wrote:
Fri. Dec. 07, 2018 6:04 pm
Well, I meant the motor. Is it thermally protected? Or will it run non stop no problem? The reason I ask is because the motor feels quite hot to the touch.
I ran a B&G NRF22 non stop (sans for power outages) for 10 years, and it might have gone another 10. But I have no experience with Grundfos. My suspicion however is that this is a non-issue.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Dec. 07, 2018 6:12 pm

Lightning wrote:
Fri. Dec. 07, 2018 4:53 pm
We should do that. Just disconnect at the boiler and shove a hose into the pex? Would that suffice?
NO!
I'm glad yer do'in this Lee. You are gaining some knowledge that will be very helpful when installing you Axeman.

Power purge is when you connect house pressure (50+ PSI) to one end of your long PEX run. Usually the boiler drain will work. Then valve off the return pipe just before the boiler. There has to be a hose bib or drain valve right before the valve on the return pipe.

The idea is you shut the return valve off, open the boiler drain letting full house pressure in, then open the valve in the return. This will force house pressure through the entire loop and blow it out the return valve. This has enough force to push any air pockets through the system and out the return valve.

Once all the air is out, shut the return valve, shut the boiler drain and open the return valve. Then adjust the system pressure. Here is a video of one I did.


I realize the system you are dealing with here is not pressurized but there should be a way to power purge it. If it was never power purged, there very well may be air pockets stuck in the system.

-Don

 
Olllotj
Member
Posts: 558
Joined: Thu. Sep. 04, 2014 10:01 am
Location: Western NY 14141
Stoker Coal Boiler: Keystoker KB-8
Coal Size/Type: Buckwheat
Other Heating: Utica Propane Hot Water

Post by Olllotj » Fri. Dec. 07, 2018 6:14 pm

A really hot pump motor can be a sign of a bad pump.Measure tne amp draw of the pump to make sure it’s circulating, or do the mechanics screwdriver to the ear trick.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Dec. 07, 2018 7:41 pm

Lightning wrote:
Fri. Dec. 07, 2018 6:04 pm
Well, I meant the motor. Is it thermally protected? Or will it run non stop no problem? The reason I ask is because the motor feels quite hot to the touch.
If this pump is running 24/7 through a hand fired boiler it will always be hot to the touch.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Dec. 08, 2018 9:56 am

Lightning wrote:
Fri. Dec. 07, 2018 10:31 am
I know lol. It was just a whim. So the boiler over shot last night and flat lined the fire. He had to throw wood in to rekindle it.
Why would hitting a mere 205 degrees kill the fire? That is certainly not a feature I would aspire to.

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Sat. Dec. 08, 2018 10:48 am

It seals the air intake...
Massive amt of coal...
Atmospheric system...
Boils at 212*...
Or less in the mountains...
LOL...
We can fix it...

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sat. Dec. 08, 2018 1:18 pm

Look what it's doing now. One of those rare occasions where the fire is matching the heat load of the house almost perfectly. WHILE IT'S IDLING... Look how flat that water temp is holding at 190.

Attachments

Screenshot_20181208-120441.jpg
.JPG | 94.2KB | Screenshot_20181208-120441.jpg

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Dec. 08, 2018 1:20 pm

Lightning wrote:
Sat. Dec. 08, 2018 1:18 pm
Look what it's doing now. One of those rare occasions where the fire is matching the heat load of the house almost perfectly. WHILE IT'S IDLING... Look how flat that water temp is holding at 190.
What is/was the outside temperature during this heat load matching?