Efm wcb 24-1 circ. Pump

Post Reply
 
User avatar
firewoodman
Member
Posts: 152
Joined: Sat. Dec. 19, 2009 9:10 pm
Location: Carbondale, Pa.

Post by firewoodman » Mon. Nov. 06, 2017 5:45 pm

In the process of installing this boiler...efm install manual has the pump pulling out of the return(bottom) with arrow on pump pointing away from boiler toward existing boiler...
I better check the direction of flow on my existing boiler as I don't want them pumping against each other...

I just figured they would push the hottest water first...idk...pardon my newb questions...lol

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Nov. 06, 2017 6:17 pm

You can pump through the other boiler in either direction...but I would pull from the zone return manifold and pump back into the pipe over the oil boiler - this will ensure that you get full temperature water to the zones. Otherwise it gets "blended" with the water returning from the radiators...that is how I started with mine, and I like it much better with the circulator going the other way.

See diagram below (I would skip the flow check shown in the diagram).

Attachments

AHSDiagram.JPG
.JPG | 32.2KB | AHSDiagram.JPG

 
User avatar
firewoodman
Member
Posts: 152
Joined: Sat. Dec. 19, 2009 9:10 pm
Location: Carbondale, Pa.

Post by firewoodman » Tue. Nov. 07, 2017 1:15 pm

Do I need a second circulator ....efm doesn't show one on this wiring diagram?
Screenshot_20171107-131206.png
.PNG | 348.4KB | Screenshot_20171107-131206.png


 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Tue. Nov. 07, 2017 2:45 pm

it all depends how you want to hook it up. You can hook the boilers in series and just use the existing circulator, or you can put a circulator between the two boilers and just let it run.

 
User avatar
firewoodman
Member
Posts: 152
Joined: Sat. Dec. 19, 2009 9:10 pm
Location: Carbondale, Pa.

Post by firewoodman » Tue. Nov. 07, 2017 9:59 pm

Since the boiler came with a pump Im putting it in...I was just concerned about the dump zone as I dont want to have any issues in a overfire situation.

 
User avatar
firewoodman
Member
Posts: 152
Joined: Sat. Dec. 19, 2009 9:10 pm
Location: Carbondale, Pa.

Post by firewoodman » Sun. Nov. 12, 2017 8:49 am

20171112_084254.jpg
.JPG | 329KB | 20171112_084254.jpg
Happy to say she is alive and throwing out heat! A toasty 70 degrees in the house...todays project is to pipe in the dhw coil and laugh at the gas man!
20171112_084254.jpg
.JPG | 329KB | 20171112_084254.jpg

Attachments

20171112_084304.jpg
.JPG | 343.7KB | 20171112_084304.jpg


 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Sat. Dec. 16, 2017 8:31 am

My WCB has been in daily use for about 11 years. In the non-heating months, I use some pallet wood to make hot water.

My setup uses one Taco 007 circulator and 3 zone valves. An aquastat on the WCB turns on the Taco when the water hits 160. In the Summer, the water circulates to an Ergomax indirect tank (E23) and back to the WCB. In the heating months, the water goes through the E23, then to the bottom of my oil boiler, out the top to the zone valve manifold and out into the zones. It returns to the WCB. Hand valves are used for different uses and different seasons. A Modine is another zone used to heat the garage.

The basement zone became the dump zone, using another aquastat that opened the zone valve for the basement. This worked great until last year when the Taco zone valve head failed and my system turned into a steam system. Also, if the power goes out with a full bed of coal and you're not home to put it out, you'll also have a steam system.

So, with the mental assistance of fellow member Scottscoaled, I am switching to a better system. A battery and inverter will power one circulator the keep the water flowing to the dump zone. To keep it simple, I didn't want to run 24V wires to the existing Taco, so I am replacing it with an Automag zone valve (RI3/4-14UR) which is letters R and I, then 3/4 for 3/4" pipe. This valve OPENS on loss of power and works normally with 24V applied. So, the next time the power goes out, the circulator will kick on and the zone valve will open automatically without power. The zone valve costs about $100. My WCB is about 35 years old.

 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Sat. Dec. 16, 2017 8:33 am

By the way, some guy got pea coal by mistake, instead of rice coal, and I got a ton of pea cheap. Once you have some clinkers covering the grates, pea burns very well in a WCB.