Ongoing Problem With Fields Type M Baro-Damper Sticking Open

User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 9:19 am

I'm about to pull it out and replace it with an RC model. Any comments or suggestions?


User avatar
Rob R.
Site Moderator
Posts: 11669
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Sun. Oct. 18, 2015 9:27 am

Does it stick in the max open position?

User avatar
hotblast1357
Member
Posts: 3140
Joined: Mon. Mar. 10, 2014 10:06 pm
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: oil furnace
Location: Peasleeville NY

Post Sun. Oct. 18, 2015 9:28 am

ive had my rc model stick open before.. had to do some tweaking with the T and what not, was putting pressure on it.

User avatar
tsb
Member
Posts: 1829
Joined: Wed. Jul. 30, 2008 8:38 pm
Stoker Coal Boiler: Binford 2000
Hot Air Coal Stoker Stove: LL Pioneer top vent
Hand Fed Coal Stove: Saey Hanover II
Baseburners & Antiques: Grander Golden Oak , Glenwood # 6
Coal Size/Type: All of them
Location: Douglassville, Pa

Post Sun. Oct. 18, 2015 9:29 am

Did you run the numbers yet ?

User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 10:02 am

It can stick open at anywhere from a bit less than half open to anywhere past that point. I've even seen it stick open at about 1/3 open. I just completely cleaned it (and the entire system) roughly 2 weeks ago. It is not hitting anything internally. The internal side "leafs" (only a type M owner would understand) are not creating a pinch point.

I just placed a drop of 3 in 1 type oil on each axle pivot point, and it seems to be working much better now.

User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 10:06 am

tsb wrote:Did you run the numbers yet ?
All I can say (so far at least) is that the two CO meters in my boiler room are still reading zero. But seriously, this matter is not one for humor.

franco b
Site Moderator
Posts: 8660
Joined: Wed. Nov. 05, 2008 5:11 pm
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea
Location: Kent CT

Post Sun. Oct. 18, 2015 10:12 am

All you can do is thoroughly clean it and double check level in both directions. When stuck open, does a very light tap instantly close it? If so it is binding at that position.

JeepinPete
Member
Posts: 127
Joined: Fri. Mar. 04, 2011 6:29 pm
Stoker Coal Boiler: EFM
Coal Size/Type: Rice
Stove/Furnace Make: EFM
Stove/Furnace Model: Highboy
Location: Quakertown PA

Post Sun. Oct. 18, 2015 10:15 am

I found mine was prone to sticking if the shaft wasn't perfectly level.


User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 10:19 am

It sounds like I've got some level checking to do.

User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 10:20 am

franco b wrote:All you can do is thoroughly clean it and double check level in both directions. When stuck open, does a very light tap instantly close it? If so it is binding at that position.
It seems like this might be it franco b!

User avatar
tsb
Member
Posts: 1829
Joined: Wed. Jul. 30, 2008 8:38 pm
Stoker Coal Boiler: Binford 2000
Hot Air Coal Stoker Stove: LL Pioneer top vent
Hand Fed Coal Stove: Saey Hanover II
Baseburners & Antiques: Grander Golden Oak , Glenwood # 6
Coal Size/Type: All of them
Location: Douglassville, Pa

Post Sun. Oct. 18, 2015 10:22 am

Summer humidity and fly ash make for problems. Numbers meaning:
How old
Did you clean it this fall
Did the boiler run all summer
Did the weight fall off
Windy days, not windy days

Oil will only be a temporary fix. Fly ash loves oil too.
Get a new one.

User avatar
Lightning
Member
Posts: 8705
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post Sun. Oct. 18, 2015 10:28 am

I found that oiling the pin saddles on the RC seems to make it operate smoother too. Making it level should keep the door from creeping to one side or the other if it's binding.

User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 10:58 am

I just did a re-leveling job. Now I need to watch it.

User avatar
Rob R.
Site Moderator
Posts: 11669
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Sun. Oct. 18, 2015 11:21 am

Is the Bari even necessary for your application?

User avatar
lsayre
Member
Posts: 12833
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Oct. 18, 2015 11:56 am

Rob R. wrote:Is the Bari even necessary for your application?
The manual states "Do not operate with flue draft exceeding -.08 inches of water column.", and also "The standard type “M” Field Control with a “T” is recommended for satisfactory performance."

Mine is set to open at about 0.05". Perhaps I should increase this to 0.06"?