Re: EFM 25 Pressure Cold.

Posted: Wed. Sep. 25, 2013 4:24 pm
by GoodProphets
Did you replace the high pressure relief valve?
That is on top of the boiler that releases at 30-32psi

It does not seem to be the problem,

Or are you talking about the auto fill valve?
That could be the problem.

Did you get a new well pump or anything to do with your water pressure incoming?

Re: EFM 25 Pressure Cold.

Posted: Wed. Sep. 25, 2013 5:19 pm
by Sting
shapechanger wrote:I don't have my hot water hooked into the system. Would the domestic coil still be the problem?


if this statement is true -- than it cannot possilbly be impacting your pressure drama
shapechanger wrote:Seems since we replaced the valve it has gotten worse. Does it matter if the pressure reducing valve is on the supply our return. Ours is on the return
It makes absolutely NO difference where you add liquid to a closed system

- Valve off the pressure reducing valve
- adjust the pressure so that the top most air bleed has about- but no less than 3 psi - you can guess it is allowed
- Record the pressure at the boiler then=IGNORE THE GAUGE ON THE BOILER - YOU HAVE CORRECT SYSTEM PRESSURE IF YOU DID THE ABOVE
- leave the PRV feed valve closed

wait 24 hours or two weeks what ever comes last

Get back to us with the pressure change! :roll: