carlherrnstein wrote: Does anyone know what the off and on temperatures are or what is a suitable replacement switch.
Are you talking about the fan control temperature on/off settings or high limit temperature setting?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Aug. 17, 2014 10:41 pm

High Limit wants to open circuit upon reaching up to 200*F.

Fan Switch goes on at ~175* and goes off after cooling back to 150*F.

 
User avatar
rockwood
Member
Posts: 1381
Joined: Sun. Sep. 21, 2008 7:37 pm
Location: Utah
Hot Air Coal Stoker Furnace: Stokermatic
Hand Fed Coal Stove: Rockwood Stoveworks Circulator
Baseburners & Antiques: Malleable/Monarch Range
Coal Size/Type: Lump and stoker + Blaschak-stove size

Post by rockwood » Tue. Aug. 19, 2014 1:30 am

Based on my experience with these furnaces, a fan on temp setting in the 140-150 range and fan off setting in the 110-120 range works well.


 
User avatar
carlherrnstein
Member
Posts: 1536
Joined: Tue. Feb. 07, 2012 8:49 am
Location: Clarksburg, ohio
Hot Air Coal Stoker Stove: combustioneer model 77B
Coal Size/Type: pea stoker/Ohio bituminous

Post by carlherrnstein » Tue. Aug. 19, 2014 7:01 pm

Sorry for the delay, the people at Will Burt say that the high limit for this unit is 400*F. I took it off and placed it in the oven and confirmed that it opens at 450*F which seems reasonable to me. This limit switch looks a lot like the temperature control switch for a lee lead melting pot.

I have the fan limit set at the factory setting.

 
User avatar
Berlin
Member
Posts: 1890
Joined: Thu. Feb. 09, 2006 1:25 pm
Location: Wyoming County NY

Post by Berlin » Wed. Aug. 20, 2014 7:11 pm

I'm not a fan of that as a high limit. One of the reasons you see so many combustioneers with sagging tubes and heat exchangers is because of such a high limit when the feed/air is adjusted improperly. I'd prefer to see 350 max on a heat exchanger snap switch or 200 on a combination switch.