Flumoxed by Efel Harmony III Clearance Instructions

Post Reply
 
Ossa
Member
Posts: 37
Joined: Sat. Dec. 17, 2016 12:28 pm
Hand Fed Coal Stove: Efel Harmony III
Coal Size/Type: Nut/Anthracite
Other Heating: Propane Boiler

Post by Ossa » Sat. Dec. 17, 2016 1:09 pm

Hi Folks,

I have an Efel Harmony III I purchased for installation in a new log cabin I have in VT. I purchased it in fall of 2015 new from a dealer. It was manufactured in 2012 according to the plate on the back. I had it installed by my General Contractor who is very conscientious about doing things right. Plus I kept an eye on what he did with regard to clearances and a pad for underneath. Left/Right/Top clearances are not in question. It is a rear exhaust, hopper fed coal stove with a double-walled pipe. the stove has a heat shield on the back. The wall behind the stove is cedar tongue & groove wood.

On start up of the stove the over evening, it got much hotter than I run it when idling along to keep the house warm. The wall behind was quite warm, but I could still keep my hand flat on it without getting burned or having to withdraw with pain. Nonetheless, this made me want to re-check the clearances. My understanding is the clearances on the plate on the back of the stove should be considered gospel for a certified stove, yes? The clearances on the back plate for a double-walled installation are 10" from the back of the stove to a combustible surface. My installation is 10" from the wall to the double-walled pipe (rear exit) and 18" to the back of the stove; so I'm well beyond recommended minimums and code says anything over six inches clearance is OK for a double-walled pipe. HERE'S THE PROBLEM!

The paper manual, shows a line drawing for clearances showing a top exhaust stove (impossible for this stove being hopper fed from the top). Not only does this drawing contradict the reality of the stove, it also defines the minimum clearance for the top exhaust pipe to the back wall to be 13", and the minimum clearance from the stove back to the wall to be 24". Yes! The two dimensions are an impossible contradiction. I'm guessing this is my ignorance and it's just industry standard to show the drawing this way and it's just defining minimum distance, pipe to wall? The manual only shows single wall pipe installation and offers no account for double walled installations.

You might say, "Just go with the back plate!" Here's another aspect that confounds me: On the back plate, reading the text above the dimensions, it instructs "This is a solid fuel, wood burning stove Only." Go figure! It has a hopper, a knifing port in the front, an ash pan, and a bottom, thermostatic damper. Looks like a coal stove to me! The manual specifically says it is NOT a dual fuel stove, coal only, despite the door on the right side. I had the identical stove back in the '80s and it was sold as a dual fuel.

Maybe my confusion is based on my ignorance. I called the dealer and they are trying to get an answer from their distributor; not a very encouraging response. They are clueless.

I'd really appreciate any help you might offer. Thanks!

 
User avatar
SWPaDon
Member
Posts: 9857
Joined: Sun. Nov. 24, 2013 12:05 pm
Location: Southwest Pa.
Hand Fed Coal Furnace: Clayton 1600M
Coal Size/Type: Bituminous
Other Heating: Oil furnace

Post by SWPaDon » Sat. Dec. 17, 2016 1:30 pm

I'm thinking someone accidently put the wrong plate on it.

 
User avatar
warminmn
Member
Posts: 8109
Joined: Tue. Feb. 08, 2011 5:59 pm
Location: Land of 11,842 lakes
Hand Fed Coal Stove: Chubby Junior, Efel Nestor Martin, Riteway 37
Coal Size/Type: nut and stove anthracite, lignite
Other Heating: Wood and wear a wool shirt

Post by warminmn » Sat. Dec. 17, 2016 2:50 pm

I used to use a twin to your stove, called many different names, but mine a Bayard with a fancy cast iron top. I had mine at an angle to my wall and will admit I was just a couple inches from my double heat shield and the wall never got warm, much less hot. Those distances on the stove are before using a heat shield on the wall, and really, you should install a heat shield of some type on a wood wall, for sparks if nothing else. There are some nice looking heat shields you can make, it doesnt have to be ugly. Tin, painted cement board, etc.

My stove was a NOS stove from the 80's I think. Ive got my manual somewhere, not sure where.

 
Ossa
Member
Posts: 37
Joined: Sat. Dec. 17, 2016 12:28 pm
Hand Fed Coal Stove: Efel Harmony III
Coal Size/Type: Nut/Anthracite
Other Heating: Propane Boiler

Post by Ossa » Sat. Dec. 17, 2016 3:10 pm

SWPaDon wrote:I'm thinking someone accidently put the wrong plate on it.
Good thought, but not the case. The floor model I looked at when I bought it had the same plate, as did mine, as did the one on the floor they looked at in the store yesterday. Maybe they put the wrong one on a whole production run...


 
Ossa
Member
Posts: 37
Joined: Sat. Dec. 17, 2016 12:28 pm
Hand Fed Coal Stove: Efel Harmony III
Coal Size/Type: Nut/Anthracite
Other Heating: Propane Boiler

Post by Ossa » Sat. Dec. 17, 2016 3:14 pm

warminmn wrote:I used to use a twin to your stove, called many different names, but mine a Bayard with a fancy cast iron top. I had mine at an angle to my wall and will admit I was just a couple inches from my double heat shield and the wall never got warm, much less hot. Those distances on the stove are before using a heat shield on the wall, and really, you should install a heat shield of some type on a wood wall, for sparks if nothing else. There are some nice looking heat shields you can make, it doesnt have to be ugly. Tin, painted cement board, etc.

My stove was a NOS stove from the 80's I think. Ive got my manual somewhere, not sure where.
I don't disagree with regards to the wall shield. Even if I've got the necessary spacing, for extra safety it's a good idea. You did hit the mark on the appearance; It's a very nice, new log home, not like hunting camp where any rugged look would be fine. I need to do some thinking on that...

thanks.

 
User avatar
warminmn
Member
Posts: 8109
Joined: Tue. Feb. 08, 2011 5:59 pm
Location: Land of 11,842 lakes
Hand Fed Coal Stove: Chubby Junior, Efel Nestor Martin, Riteway 37
Coal Size/Type: nut and stove anthracite, lignite
Other Heating: Wood and wear a wool shirt

Post by warminmn » Sat. Dec. 17, 2016 3:20 pm

This will take an hour to look at, but might give you some ideas. Pictures of Your Stove I'm sure you can google for pics too. There should be a custom shop around to make anything you can dream up. It doesnt have to be high heat paint unless real close.

 
ddahlgren
Member
Posts: 1769
Joined: Tue. Feb. 19, 2013 3:30 pm
Location: Mystic CT
Hand Fed Coal Stove: Crane 404
Contact:

Post by ddahlgren » Sat. Dec. 17, 2016 3:30 pm

Does it actually have coal grates? I can believe 13 inches with a heat shield spaced off the wall so air can circulate behind it.

 
User avatar
SWPaDon
Member
Posts: 9857
Joined: Sun. Nov. 24, 2013 12:05 pm
Location: Southwest Pa.
Hand Fed Coal Furnace: Clayton 1600M
Coal Size/Type: Bituminous
Other Heating: Oil furnace

Post by SWPaDon » Sat. Dec. 17, 2016 3:40 pm

Ossa wrote:
SWPaDon wrote:I'm thinking someone accidently put the wrong plate on it.
Good thought, but not the case. The floor model I looked at when I bought it had the same plate, as did mine, as did the one on the floor they looked at in the store yesterday. Maybe they put the wrong one on a whole production run...
Do they drug test employees? ;)


 
ddahlgren
Member
Posts: 1769
Joined: Tue. Feb. 19, 2013 3:30 pm
Location: Mystic CT
Hand Fed Coal Stove: Crane 404
Contact:

Post by ddahlgren » Sat. Dec. 17, 2016 3:48 pm

Without knowing what the other finishes are they do make light weight stone looking randome size tiles for a better word but the look like a hand laid up wall when done with all odd shapes if you like. If you like a brick look they make lightweight brick tiles that are actual red brick and easy to install as well. Obviously over cement board for either choice spaced off the wall a minimum of 1 inch.

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Sat. Dec. 17, 2016 4:04 pm

The confusion over dual fuel is because of EPA rules. It no longer can be called a wood stove.

If the wood wall is on the edge of being too warm, I would put a heat shield there. Over time with steady heat the wood will combust at lower temperatures than normal. A bottom heat shield is a good idea too.

 
Ossa
Member
Posts: 37
Joined: Sat. Dec. 17, 2016 12:28 pm
Hand Fed Coal Stove: Efel Harmony III
Coal Size/Type: Nut/Anthracite
Other Heating: Propane Boiler

Post by Ossa » Sat. Dec. 17, 2016 7:22 pm

franco b wrote:The confusion over dual fuel is because of EPA rules. It no longer can be called a wood stove.

If the wood wall is on the edge of being too warm, I would put a heat shield there. Over time with steady heat the wood will combust at lower temperatures than normal. A bottom heat shield is a good idea too.
That makes sense regarding the EPA being at the root of the confusion.

Thanks to you and the previous poster as well for input on the heat shield. I've started to look around already. I like some that I've seen that are the requisite 24 guage metal (NFPA 211 requirement...), are black and are laser cut with designs at the top to be attractive.

I'm still hoping someone might have some input on the clearance requirements...

 
User avatar
warminmn
Member
Posts: 8109
Joined: Tue. Feb. 08, 2011 5:59 pm
Location: Land of 11,842 lakes
Hand Fed Coal Stove: Chubby Junior, Efel Nestor Martin, Riteway 37
Coal Size/Type: nut and stove anthracite, lignite
Other Heating: Wood and wear a wool shirt

Post by warminmn » Sat. Dec. 17, 2016 8:04 pm

Its way to cold for me to look at my stove as its in an outbuilding, but I'll take a pic of the label in 2 or 3 days that shows what my clearances were. Adding a heat shield will cut the distance almost in half.

You can always remove the heat shield when the stove is not in use, as long as you remember to put it back on when burning.

 
Ossa
Member
Posts: 37
Joined: Sat. Dec. 17, 2016 12:28 pm
Hand Fed Coal Stove: Efel Harmony III
Coal Size/Type: Nut/Anthracite
Other Heating: Propane Boiler

Post by Ossa » Sat. Dec. 17, 2016 11:13 pm

warminmn wrote:Its way to cold for me to look at my stove as its in an outbuilding, but I'll take a pic of the label in 2 or 3 days that shows what my clearances were. Adding a heat shield will cut the distance almost in half.

You can always remove the heat shield when the stove is not in use, as long as you remember to put it back on when burning.
Thanks! I'll look forward to anything you can offer!