Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
U235a4
Member
Posts: 321
Joined: Mon. Oct. 29, 2007 8:26 pm
Stove/Furnace Make: 1958 Axeman-Anderson
Stove/Furnace Model: 260M
Location: South Central PA

Post Sun. Oct. 05, 2008 11:28 pm

Well during spring clearing a few problems were found on the 1958 AA260m, one it had a lot of flyash built up in the swirl chamber and fan area also the fan hub was cracked and one bolt was holding the fan to the hub. The major problem which I can't seem find the picture of at the moment is the front lip erosion of the burn pot and two little cracks into the boiler jacket. I took the boiler to AA back in july and had the lip repaired and while it was there had the new style coil mount installed even though I didn't have problems I'm hoping for 50 more years out of it. I'll be adding picture to this as the I get things done and the boiler reinstalled in it's home.

This is the boiler before the spring tear down.
**Broken Image Link(s) Removed**

Here a groove that has worn into the fan area from flyash after 50 years of service.
**Broken Image Link(s) Removed**

Take note on this piece from the swirl chamber flyash was about 6-7" deep at the top.
**Broken Image Link(s) Removed**

The Fan with the cracked hub and missing bolts, this unit was replaced with a new one.
**Broken Image Link(s) Removed**

Here is some of the flyash build up also take note to the black film that was about 1/16th thick on the surface.
**Broken Image Link(s) Removed**

This was the fan area looks like after a sand blasting the junk off.
**Broken Image Link(s) Removed**

Here is the flyash buildup in the center tube.
**Broken Image Link(s) Removed**

Center tube after blasting
**Broken Image Link(s) Removed**

Flyash buildup on the swirl chamber walls
**Broken Image Link(s) Removed**

Swirl chamber cleaned up
**Broken Image Link(s) Removed**

New style IN162 coil
**Broken Image Link(s) Removed**

Outside before paint
**Broken Image Link(s) Removed**

New coil flange mount
**Broken Image Link(s) Removed**
Last edited by U235a4 on Mon. Oct. 06, 2008 9:42 pm, edited 1 time in total.

Visit Alternate Heating Sytems

User avatar
LsFarm
Member
Posts: 7385
Joined: Sun. Nov. 20, 2005 8:02 pm
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland
Location: Michigan

Post Sun. Oct. 05, 2008 11:33 pm

HI Zach, how did you pickup and move the boiler?? Lots of muscle? or a good lift with wheels??

the repairs look great,, you gonna take a few of the repaired firpot lip?

Greg L
Burning Pea/Buckwheat through an antique stoker [semi retired SSboiler],
Running an Axeman-Anderson 260M boiler burning Pea, About 150-250#per day
Farming, Fixing, Fabricating and Flying: 'spare time' what's that?

User avatar
billw
Member
Posts: 1087
Joined: Mon. Apr. 24, 2006 5:40 pm
Stove/Furnace Make: EFM 520
Stove/Furnace Model: GOODBYE OIL COMPANY
Location: Dallas, PA

Post Mon. Oct. 06, 2008 7:08 am

That thing is huge. It's the first time I ever saw a pic of a 260. What are you heating with it? It looks like it could heat a neighborhood.

User avatar
Adamiscold
Member
Posts: 1117
Joined: Fri. Feb. 29, 2008 7:09 am
Stove/Furnace Make: Chubby Sr. Old School
Location: Winchendon,Ma

Post Mon. Oct. 06, 2008 7:42 am

She sure does look pretty :drool:
Adam

http://www.homepower.com <-- Great magazine.

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Mon. Oct. 06, 2008 10:44 am

Nice photos. When ASME coded boilers are repaired, at least commercial boilers, an new ASME H stamp is issued. It likely makes no difference to you but was the re-stamping of the boiler at all discussed? Just curious.
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Mon. Oct. 06, 2008 11:20 am

Since Axeman did the repair, I believe it needs no reissue. Whomever performs the repairs must be an H stamp holder or the repair can not be approved as it is the repairer, not the repair that is approved in these situations. This only applies to the pressure vessel itself, repairs to other portions of the unit have no bearing on ASME approval IIRC.
billw wrote:That thing is huge. It's the first time I ever saw a pic of a 260. What are you heating with it? It looks like it could heat a neighborhood.
They look big in pictures for some reason, I was surprised at how small my 260M was, I first figured it to be a 130M.
Nothing is impossible for people who don't have to do it themselves.

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Mon. Oct. 06, 2008 1:04 pm

Thanks for sharing the pics. Quite the project to mount a new coil frame. Good going!
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

U235a4
Member
Posts: 321
Joined: Mon. Oct. 29, 2007 8:26 pm
Stove/Furnace Make: 1958 Axeman-Anderson
Stove/Furnace Model: 260M
Location: South Central PA

Post Mon. Oct. 06, 2008 9:43 pm

added a few pictures more to follow!

Visit Alternate Heating Sytems

User avatar
ceccil
Member
Posts: 1062
Joined: Sat. Mar. 15, 2008 11:33 pm
Stove/Furnace Make: Keystoker, Harman
Stove/Furnace Model: 90K, Mark III
Location: Elmira, NY

Post Tue. Oct. 07, 2008 1:28 am

I've never actually seen one of these AA's but I tell ya what, they seem to be a work of art. Compared to a stoker stove they are a true piece of machinery. :D

Jeff
Jeff
Loyalty to the country always. Loyalty to the government when it deserves it. - Mark Twain

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Tue. Oct. 07, 2008 10:53 am

coaledsweat wrote:Since Axeman did the repair, I believe it needs no reissue. Whomever performs the repairs must be an H stamp holder or the repair can not be approved as it is the repairer, not the repair that is approved in these situations. This only applies to the pressure vessel itself, repairs to other portions of the unit have no bearing on ASME approval IIRC.
Thanks for the information. I'm unclear on this whole H stamp process. Do I understand it that it's the individual welder that holds the "H" certification and his resultant repair work then meets the pre-existing ASME boiler vessel certification. Right?
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

U235a4
Member
Posts: 321
Joined: Mon. Oct. 29, 2007 8:26 pm
Stove/Furnace Make: 1958 Axeman-Anderson
Stove/Furnace Model: 260M
Location: South Central PA

Post Tue. Oct. 07, 2008 11:32 am

Yanche, They didn't add any stamps to the boiler nor did Pete say anything about a H-stamp but I do know he has one guy doing the repairs to boiler come in and this could be why.

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Tue. Oct. 07, 2008 1:23 pm

Yanche wrote:Thanks for the information. I'm unclear on this whole H stamp process. Do I understand it that it's the individual welder that holds the "H" certification and his resultant repair work then meets the pre-existing ASME boiler vessel certification. Right?
Correct, to hold an H stamp, the individual himself must be certified to perform pressure vessel repairs. The boiler's material and construction practices hasn't changed, just the point of repair. In most cases, this is simply cleaning and preping a crack and properly welding it. Sometimes it can be a massive undertaking, such as changing a tube sheet at the boilers end.
Nothing is impossible for people who don't have to do it themselves.

U235a4
Member
Posts: 321
Joined: Mon. Oct. 29, 2007 8:26 pm
Stove/Furnace Make: 1958 Axeman-Anderson
Stove/Furnace Model: 260M
Location: South Central PA

Post Mon. Oct. 13, 2008 8:34 pm

Well for the second installment of pictures of past and future I have the added the following:

This picture was taken the night we got the boiler and base back in the basement and my back healed enough to take a picture or two :D
**Broken Image Link(s) Removed**

almost done:
**Broken Image Link(s) Removed**

Here is the repair work done on the front lip of the burn pot, ( if I can find the before shot I'll add that yet)
**Broken Image Link(s) Removed**

**Broken Image Link(s) Removed**

I welded a new ashing cam and feed tube gear on.
**Broken Image Link(s) Removed**

Installed a new cork transfer head gasket
**Broken Image Link(s) Removed**

Installed a new feed collar bearing because you'll see in the picture the old one was worn thin.

old:
**Broken Image Link(s) Removed**

New:
**Broken Image Link(s) Removed**

Had Axeman-Anderson install a new style domestic hot water coil mount.

old:
**Broken Image Link(s) Removed**

new:
**Broken Image Link(s) Removed**

User avatar
LoschStoker
Member
Posts: 163
Joined: Mon. Feb. 04, 2008 12:47 pm
Hand Fed Coal Stove: (New) Warm Morning 400A
Other Heating: Yukon Polar-Eagle II Multi Furnace
Stove/Furnace Make: Losch 350 130k BTU's
Stove/Furnace Model: DS Stoves 1500WH Short Lid
Location: Greencastle, PA.

Post Wed. Oct. 15, 2008 8:13 am

AA got the coil flange build out idea from Orbie Pepley of Shippensburg,PA.
He's been doing it that way for 30 years.

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Wed. Oct. 15, 2008 8:27 am