Noticed my boiler was starting to take heat shedding dumps to my dump zone (family room) during a warm day last week, so knew it was time to lower the boiler LL temp from my winter 190 F setting to my spring 160 F setting.

Attachments

CB7B06C1-BF9B-4E1E-B2F9-45EDB276629A.jpeg

Fluffing the fire because of few natural heat calls.

65B55E90-7C1E-44D2-B3A5-74B9F4B12581.jpeg

Day Dump count, where the boiler couldn't fluff the fire because it had reached high temp boiler limit and had to dump btu's.

0ACD1761-3D6B-4DE9-A8C6-9C933C8F3661.jpeg

Day after lowering boiler temp LL.

88A2E788-D0CE-4F78-8C28-AE696F896BA5.jpeg

Day after lowering boiler temp LL.

6709F906-7F0E-4CF1-B163-8127C501C9F2.jpeg

Day after lowering boiler temp LL.



 
User avatar
vermontday
Member
Posts: 358
Joined: Wed. Oct. 22, 2008 8:27 pm
Location: Bennington, VT
Stoker Coal Boiler: EFM 520

Post by vermontday » Wed. Apr. 12, 2023 8:06 pm

Just noticed posting the above that I hadn't set my outfire timer down from 60 min winter setting to 30 min summer setting and my dump from 70 min winter setting to 40 min summer setting. So I just did that. I am getting old!

Attachments


 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Apr. 12, 2023 8:39 pm

vermontday wrote:
Wed. Apr. 12, 2023 7:53 pm
Noticed my boiler was starting to take heat shedding dumps to my dump zone (family room) during a warm day last week, so knew it was time to lower the boiler LL temp from my winter 190 F setting to my spring 160 F setting.
Does the boiler maintain 190F during the heating season? Or is that the high limit it will reach on a long heat call?

I run mine at 160 with a 10 degree differential for most of the heating season.

 
User avatar
vermontday
Member
Posts: 358
Joined: Wed. Oct. 22, 2008 8:27 pm
Location: Bennington, VT
Stoker Coal Boiler: EFM 520

Post by vermontday » Wed. Apr. 12, 2023 9:27 pm

I usually set the LL for 180 F for most of the winter. However with that bitter cold we had I set the LL to 190 F. I had forgotten to lower it after the weather warmed.

I leave the HL at 210 F and the differential at 10.

The reason I go with a shorter out fire time in the spring is the warm weather reduces the chimney draft.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Apr. 13, 2023 7:34 am

vermontday wrote:
Wed. Apr. 12, 2023 9:27 pm
I usually set the LL for 180 F for most of the winter. However with that bitter cold we had I set the LL to 190 F. I had forgotten to lower it after the weather warmed.

I leave the HL at 210 F and the differential at 10.

The reason I go with a shorter out fire time in the spring is the warm weather reduces the chimney draft.
Next winter try leaving it at 160 and see how far you can make it. I would expect it will heat your house fine on all but a few days. For every 4 degrees you reduce the operating temperate you should see about a 1% reduction in fuel consumption, and the heat calls will be longer with less variability in room temperature.

I run a 30 minute timer cycle in warm weather also. Not only does it maintain the draft better, the fire responds faster on heavy DHW usage.

 
User avatar
vermontday
Member
Posts: 358
Joined: Wed. Oct. 22, 2008 8:27 pm
Location: Bennington, VT
Stoker Coal Boiler: EFM 520

Post by vermontday » Thu. Apr. 13, 2023 10:24 am

Good to know Rob.

I will try leaving it longer at 160 F next fall.

Thanks

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Apr. 14, 2023 7:47 am

Thanks for the reminder!!!

It's been in the 80's for the past few days down here and the garage has been in the 90's. :o
I totally forgot about lowering the boiler temp from 175 to 155 for Summer running.
IMG_0001.JPG
.JPG | 393.4KB | IMG_0001.JPG
The Inkbird's that I am using work a little differently than an Aquastat as far as differential goes. With a setpoint of 155 degrees and Hysteresis of 5 degrees the boiler will fire at 150 degrees and stop at 160.
IMG_0002.JPG
.JPG | 360.3KB | IMG_0002.JPG
I have been seeing overshoots to about 210 degrees this week. :what:

Again, thanks for the reminder!
-Don


 
User avatar
mozz
Member
Posts: 1351
Joined: Mon. Sep. 17, 2007 5:27 pm
Location: Wayne county PA.
Stoker Coal Boiler: Axeman Anderson 1982 AA-130 Steam

Post by mozz » Fri. Apr. 14, 2023 3:16 pm

"For every 4 degrees you reduce the operating temperate you should see about a 1% reduction in fuel consumption"

Not all are happy with a constant temp in all the rooms, i like to know when the heat is on. More btu's from higher temps. Coal likes to burn hot. I can bet the year to year winter temp difference is way more than 1% so i doubt there will be any savings you can actually see.

 
User avatar
vermontday
Member
Posts: 358
Joined: Wed. Oct. 22, 2008 8:27 pm
Location: Bennington, VT
Stoker Coal Boiler: EFM 520

Post by vermontday » Fri. Apr. 14, 2023 3:20 pm

That's quite a system you have there StokerDon!

We are in the 80's here now. I lowered the boiler to 150F and have had one dump so far today as it walks its way up to 210F.

When I installed the boiler, I insulated inside and outside the base and all the pipes are insulated, so this isn't bad for a super insulated heat generator. Tuff to make an air conditioner out of it!

I will run it for another week or so and then switch over to oil for my domestic hot water.

Attachments

76B14D32-BEA0-4737-AC9C-0418BA41EC0E.jpeg
.JPEG | 671KB | 76B14D32-BEA0-4737-AC9C-0418BA41EC0E.jpeg

 
User avatar
vermontday
Member
Posts: 358
Joined: Wed. Oct. 22, 2008 8:27 pm
Location: Bennington, VT
Stoker Coal Boiler: EFM 520

Post by vermontday » Fri. Apr. 14, 2023 3:47 pm

I just signed a contract this morning to have 43 PV solar panels installed on my garage roof.

Next week I will be signing a contract for a heat pump for our family room to suck up the extra electricity.

Then I can watch the heat pump air condition the family room when the EFM uses it as a dump zone.

American ingenuity at its finest!

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Apr. 14, 2023 6:38 pm

vermontday wrote:
Fri. Apr. 14, 2023 3:20 pm

We are in the 80's here now. I lowered the boiler to 150F and have had one dump so far today as it walks its way up to 210F.

When I installed the boiler, I insulated inside and outside the base and all the pipes are insulated
You must be running 5 or 6 teeth of feed? Even with it well insulated you should be able to avoid the dump zone cycle.

Mine has no dump zone at all, just a second high limit control set at 210. Boiler and piping is insulated also, I have not caught it over 180F.

 
User avatar
vermontday
Member
Posts: 358
Joined: Wed. Oct. 22, 2008 8:27 pm
Location: Bennington, VT
Stoker Coal Boiler: EFM 520

Post by vermontday » Sat. Apr. 15, 2023 9:44 am

4 teeth...

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Apr. 15, 2023 10:35 am

vermontday wrote:
Sat. Apr. 15, 2023 9:44 am
4 teeth...
I guess you really do have it insulated like a thermos!

 
User avatar
SMITTY
Member
Posts: 12520
Joined: Sun. Dec. 11, 2005 12:43 pm
Location: West-Central Mass
Stoker Coal Boiler: EFM 520 Highboy
Coal Size/Type: Rice / Blaschak anthracite
Other Heating: Oil fired Burnham boiler

Post by SMITTY » Sat. Apr. 15, 2023 12:54 pm

I lowered my temp to ZERO. :D
IMG_8170.jpeg
.JPEG | 457.1KB | IMG_8170.jpeg

 
User avatar
davidmcbeth3
Member
Posts: 8505
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra

Post by davidmcbeth3 » Sat. Apr. 15, 2023 1:20 pm

vermontday wrote:
Fri. Apr. 14, 2023 3:47 pm
I just signed a contract this morning to have 43 PV solar panels installed on my garage roof.

Next week I will be signing a contract for a heat pump for our family room to suck up the extra electricity.

Then I can watch the heat pump air condition the family room when the EFM uses it as a dump zone.

American ingenuity at its finest!
Start a thread on your PV system...keep track and post KW produced by them.