Va-600 Water Pressure ?

Post Reply
 
RON1958
Member
Posts: 67
Joined: Sun. Jan. 23, 2022 9:34 am
Location: Port Matilda, Pa. Area (Stormstown)
Stoker Coal Boiler: Van Wert 600
Hand Fed Coal Stove: Hitzer 30-95
Coal Size/Type: chestnut , buck

Post by RON1958 » Thu. Mar. 23, 2023 8:42 am

Been running fine till the other day, keep water at about 180 and pressure @ 20. When stoker is not running and water temp goes down to around 160 the pressure drops to 0. Soon as she fires and goes back to 180 the pressure returns to 20 again. Is this normal? It's heating the house just fine. I'm also gonna try the 2" pulley on the motor deal to see if I can cut coal usage a bit? Any thoughts on this is appreciated.

 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 23, 2023 9:41 am

Ron, what you have described is usually the symptom of failed/flooded expansion tank, or not enough water in the system.

 
RON1958
Member
Posts: 67
Joined: Sun. Jan. 23, 2022 9:34 am
Location: Port Matilda, Pa. Area (Stormstown)
Stoker Coal Boiler: Van Wert 600
Hand Fed Coal Stove: Hitzer 30-95
Coal Size/Type: chestnut , buck

Post by RON1958 » Thu. Mar. 23, 2023 11:42 am

Its brand new,has air in it?


 
User avatar
nepacoal
Member
Posts: 1690
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Thu. Mar. 23, 2023 11:47 am

Does your boiler have an air vent on top? Our EFM's pressure does odd stuff (usually higher) when there is air in the boiler. We have a manual coin vent on the top. Not sure why yours drops to zero at 160° but our pressure will drop from 20 to 15 by just letting the air out.

 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 23, 2023 11:53 am

RON1958 wrote:
Thu. Mar. 23, 2023 11:42 am
Its brand new,has air in it?
Do you have an automatic water feeder on the system? If you do not, or it is turned off, you probably need to add a little water to the system. It is not uncommon to need some makeup water after the air from the initial fill is removed.

 
RON1958
Member
Posts: 67
Joined: Sun. Jan. 23, 2022 9:34 am
Location: Port Matilda, Pa. Area (Stormstown)
Stoker Coal Boiler: Van Wert 600
Hand Fed Coal Stove: Hitzer 30-95
Coal Size/Type: chestnut , buck

Post by RON1958 » Thu. Mar. 23, 2023 11:58 am

I manual feed. I'll add a bit and see how she goes.


 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 23, 2023 1:21 pm

RON1958 wrote:
Thu. Mar. 23, 2023 11:58 am
I manual feed. I'll add a bit and see how she goes.
That is your issue, the system needs some water added.

Get yourself a fill valve and install it. You can always valve it off if you want to monitor for leaks.

https://www.supplyhouse.com/Boiler-Fill-Valves-17081000

 
User avatar
Lightning
Site Moderator
Posts: 14652
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Mar. 23, 2023 2:28 pm

I assume the air bladder in the expansion tank was tested for air pressure while there was no water pressure on the boiler?