Coal BTU content vary with years?

Post Reply
 
jonesrm55
New Member
Posts: 6
Joined: Sat. Nov. 12, 2022 11:10 am
Stoker Coal Boiler: Keystoker KAA2
Coal Size/Type: rice
Other Heating: Utica oil boiler

Post by jonesrm55 » Fri. Feb. 10, 2023 9:56 am

Good morning, havent used my boiler in 3 years and this year I cannot get it to run over 120 deg. Gave it a thorogh cleaning yesterday ant it is set up to Keystoker specs (KAA22). Does coal BTU output change year to year? I have always used Blaschak ( since 2008) and this is the first year it doesnt run very well. Any ideas?

 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Feb. 10, 2023 10:01 am

I doubt it is the coal. More likely something is wrong with the stoker.

How does the fire look?

 
jonesrm55
New Member
Posts: 6
Joined: Sat. Nov. 12, 2022 11:10 am
Stoker Coal Boiler: Keystoker KAA2
Coal Size/Type: rice
Other Heating: Utica oil boiler

Post by jonesrm55 » Fri. Feb. 10, 2023 10:53 am

Fire just about covers the whole stoker plate


 
User avatar
SMITTY
Member
Posts: 12496
Joined: Sun. Dec. 11, 2005 12:43 pm
Location: West-Central Mass
Stoker Coal Boiler: EFM 520 Highboy
Coal Size/Type: Rice / Blaschak anthracite
Other Heating: Oil fired Burnham boiler

Post by SMITTY » Fri. Feb. 10, 2023 12:04 pm

Make sure there's nothing blocking the airflow. You'd have to let the fire go out, and maybe remove the stoker assembly depending on how much room you have in there.

My old flat bed stoker used to get little pieces jammed in the holes, and every fall I'd have to poke them through with a tiny screwdriver or piece of wire, plus vacuum out a MOUNTAIN of fines beneath the bed. The fines really choked off the BTU output, since it restricted and redirected airflow.

 
jonesrm55
New Member
Posts: 6
Joined: Sat. Nov. 12, 2022 11:10 am
Stoker Coal Boiler: Keystoker KAA2
Coal Size/Type: rice
Other Heating: Utica oil boiler

Post by jonesrm55 » Fri. Feb. 10, 2023 12:07 pm

Did that too

 
User avatar
Lightning
Site Moderator
Posts: 14652
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Feb. 10, 2023 12:36 pm

Could you post some pictures or even a short video of your fire?


 
User avatar
nepacoal
Member
Posts: 1690
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Fri. Feb. 10, 2023 12:41 pm

Maybe a blocked chimney or an open chimney clean out door. Are you smelling any sulfur at all? Is your triple aquastat acting normal? Your stoker should never turn off if the temp remains below your low limit. A video of your fire would definitely help.
Last edited by nepacoal on Fri. Feb. 10, 2023 2:57 pm, edited 1 time in total.

 
jonesrm55
New Member
Posts: 6
Joined: Sat. Nov. 12, 2022 11:10 am
Stoker Coal Boiler: Keystoker KAA2
Coal Size/Type: rice
Other Heating: Utica oil boiler

Post by jonesrm55 » Fri. Feb. 10, 2023 12:46 pm

I will later. As I said , I gave boiler a solid cleaning front to back-that’s what is so confusing. Thanks

 
User avatar
Lightning
Site Moderator
Posts: 14652
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Feb. 10, 2023 12:50 pm

Is the boiler firing constantly and not able to get above 120 degrees?

 
lzaharis
Member
Posts: 2358
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Fri. Feb. 10, 2023 12:53 pm

You have a kaa2 not a kaa22 right??

All types of coal fuels can vary in carbon content and the BTU per pound.

If the entire fire bed of your kaa-2 has a fire on it, it may feeding too much coal
as you need to have a 2+ inch band of ash band of ash at the base of the
fire grate a 2 inch band of fire and the rest of the coal being unburned coal.

I reduced my coal flow rate by two thirds by reducing the size of the hopper
draw point and I am burning much less coal and still having plenty of heat.

If you have not changed the air setting for the squirrel cage blower you should
back the stoker feed off by 2 threads and wait to see what the fire looks like in
a couple of hours.

It is entirely possible that your unit may have a mountain of fly ash in the flue
breech blocking the flow of flue gasses and it needs to be cleaned.

This occurred with my kaa-4-1 as I was never aware the flue baffle could be
removed to clean behind it until I bumped it and it slid sideways.

When I did remove the baffle the very first time I found had a mountain of fly ash
in the flue breech and I vacuumed it all out.

I would check behind the baffle first for fly ash build up and then slow the feed rate
down by 2 threads.