Post by Kungur » Sun. Dec. 25, 2022 11:27 am

This morning I was checking the boiler,KA2, and I notice that the circulator for our main zone was not running. So I had my wife adjust the thermostat while watched the relay. Nothing even advancing the stat all the way up. So I put a jumper on in the panel.
So I do I determine if the thermostat is bad?

 
User avatar
davidmcbeth3
Member
Posts: 8505
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra

Post by davidmcbeth3 » Sun. Dec. 25, 2022 11:39 am

What model thermostat ..l have link to operating manual ?

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Sun. Dec. 25, 2022 11:45 am

If the zone worked when you added the jumper, either your thermostat is bad or the wiring to the thermostat is bad...

 
Kungur
Member
Posts: 723
Joined: Thu. Sep. 25, 2008 7:09 am
Location: Chardon,Ohio

Post by Kungur » Sun. Dec. 25, 2022 11:51 am

Just had a thought after I ate a gingerbread cookie! Would checking continuity determine it?

 
User avatar
davidmcbeth3
Member
Posts: 8505
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra

Post by davidmcbeth3 » Sun. Dec. 25, 2022 12:55 pm

Kungur wrote:
Sun. Dec. 25, 2022 11:51 am
Just had a thought after I ate a gingerbread cookie! Would checking continuity determine it?
Checking from where to where ?


 
Kungur
Member
Posts: 723
Joined: Thu. Sep. 25, 2008 7:09 am
Location: Chardon,Ohio

Post by Kungur » Sun. Dec. 25, 2022 1:00 pm

I was the on the stat itself.

 
Kungur
Member
Posts: 723
Joined: Thu. Sep. 25, 2008 7:09 am
Location: Chardon,Ohio

Post by Kungur » Sun. Dec. 25, 2022 1:01 pm

Or I could disconnect the wires at the relay

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Dec. 25, 2022 2:00 pm

Disconnect wires at the thermostat and jump them. If the relay engages as expected, your thermostat is faulty.

 
Kungur
Member
Posts: 723
Joined: Thu. Sep. 25, 2008 7:09 am
Location: Chardon,Ohio

Post by Kungur » Sun. Dec. 25, 2022 2:17 pm

Rob, with my wife's help I did just that. Thermostat is bad. HD has them. So tomorrow....
Merry Christmas!

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sun. Dec. 25, 2022 3:49 pm

Kungur wrote:
Sun. Dec. 25, 2022 2:17 pm
Rob, with my wife's help I did just that. Thermostat is bad. HD has them. So tomorrow....
Merry Christmas!
Also be aware some thermostats like the Honeywell white round ones have a short cycle protection feature depending on which type of fuel setting you have the switches set for. This drove me nuts at our apartment because once the temp was met, if you were still chilly and tried to turn it up a freckle you had to wait ten minutes or so till it would finish its cycle. Digital thermostats are not to my liking, my house takes too long to recover from setbacks anyway so I just set and forget the ol mercury style treats me fine!


 
User avatar
WNY
Member
Posts: 6307
Joined: Mon. Nov. 14, 2005 8:40 am
Location: Cuba, NY
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Contact:

Post by WNY » Mon. Dec. 26, 2022 9:02 am

Mine was acting up too (digital), batteries were getting low, changed batteries, then when I went to clip it back on to the base, it didn't latch correctly and make contact with the front cover and stove only went to idle, thermostat said 65 but was only 55. I finally figured got it electronics section clipped onto the base and seems to be holding good temp now.

 
Kungur
Member
Posts: 723
Joined: Thu. Sep. 25, 2008 7:09 am
Location: Chardon,Ohio

Post by Kungur » Wed. Dec. 28, 2022 11:23 am

New thermostat work! Now the weather is warming up!

 
User avatar
davidmcbeth3
Member
Posts: 8505
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra

Post by davidmcbeth3 » Wed. Dec. 28, 2022 2:05 pm

Kungur wrote:
Wed. Dec. 28, 2022 11:23 am
New thermostat work! Now the weather is warming up!
Set at 5000F to test ?

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Wed. Dec. 28, 2022 2:14 pm

Good fix K. :)