Ok so been running the new 520 for about 2 weeks and just noticed when thermostat calls for heat boiler turns on and runs instantly is this normal? I don’t remember my last boiler doing this till water temp was under temp? Or is something g wired wrong?

 
User avatar
Retro_Origin
Member
Posts: 926
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Fri. Dec. 23, 2022 11:00 pm

It’s typical to setup them that way, the boiler is firing so it doesn’t fall behind during a heat call. This is especially important for slow ramp up fires like coal.

 
User avatar
nepacoal
Member
Posts: 1700
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Sat. Dec. 24, 2022 5:36 am

Yep, that's exactly how a triple aquastat works when the TT terminal is connected to a thermostat ( or end switch if using a Taco SR type control). A simple on off aquastat would work like your old one.

Attachments

honeywell.gif
.GIF | 57.9KB | honeywell.gif


 
User avatar
klim1972
Member
Posts: 74
Joined: Tue. Nov. 01, 2011 11:15 am
Location: lake ariel Pa
Stoker Coal Boiler: EFM df 520
Coal Size/Type: Buck

Post by klim1972 » Sat. Dec. 24, 2022 8:26 am

Ok so that’s fine then to let it stay that way?

 
User avatar
nepacoal
Member
Posts: 1700
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Sat. Dec. 24, 2022 8:31 am

Yes... The majority of boilers use a triple aquastat. What's your high limit and low limit? A good starting point for an EFM is 200 HL, 160 LL with a differential of 10.

 
User avatar
Rob R.
Site Moderator
Posts: 18003
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Dec. 24, 2022 10:52 am

klim1972 wrote:
Sat. Dec. 24, 2022 8:26 am
Ok so that’s fine then to let it stay that way?
It is not a problem, but depending on the rest of your setup it might result in the boiler always running at the high limit. Just keep an eye on it and see how it behaves.