Post by StokerDon » Sat. Apr. 01, 2023 7:19 pm

We are well into Spring down here now. Mid 70's and sunny today then a Big thunderstorm went through. It started out with some good sized Hail. :o

80's in the garage with the door open.
IMG_0011.JPG
.JPG | 270.3KB | IMG_0011.JPG
75 outside before the thunderstorm.
IMG_0012.JPG
.JPG | 218KB | IMG_0012.JPG
Back to business...
IMG_0007.JPG
.JPG | 352.4KB | IMG_0007.JPG
Over the past 7 days;
Fan reading, 3310.8 - 3274.8 = 36.0 hours of fan run time, 5.14 hours per day.
Ash reading, 1904.7 - 1885.8 = 19.2 hours of ashing, 2.74 hours per day, 53% of fan run time.
IMG_0008.JPG
.JPG | 493.3KB | IMG_0008.JPG
1 ashpan this week. Some gray rocks that come with Spring but, we still have some nice clinkers too.
IMG_0010.JPG
.JPG | 400.3KB | IMG_0010.JPG
Gofer action.
IMG_0009.JPG
.JPG | 454.3KB | IMG_0009.JPG
Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 175*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 130*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Apr. 08, 2023 5:58 pm

Been pretty warm this week. 60's, 70's and a couple days in the 80's. AC season has started along with mowing season. :cry:
IMG_0002.JPG
.JPG | 364.8KB | IMG_0002.JPG
Over the past 7 days;
Fan reading, 3343.5 - 3310.8 = 32.7 hours of fan run time, 4.67 hours per day.
Ash reading, 1920.9 - 1904.7 = 16.2 hours of ashing, 2.31 hours per day, 50% of fan run time.
IMG_0003.JPG
.JPG | 409KB | IMG_0003.JPG
One ashpan per week now! Powder, clinkers and some gray rocks, not to bad.
IMG_0004.JPG
.JPG | 443.2KB | IMG_0004.JPG
The Gofer hole had finally made it down to the mouth of the auger this week. I raked the coal off the sides to even things out. It will be time for the barrel in about a month.
IMG_0005.JPG
.JPG | 373.1KB | IMG_0005.JPG
Down to 1 slat now.
IMG_0006.JPG
.JPG | 317.6KB | IMG_0006.JPG
I visited my coal supplier last week. $350 a ton is the current Summer special price.

Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 175*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 130*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Apr. 14, 2023 7:41 pm

It's That Time Of Year!!!

Daytime highs are in the 70's and 80's down here. Thank's to VermontDay for reminding me that I normally reduce my boiler temperature set point this time of year. :yes:

Winter set point, 175. Boiler will fire at 170 and run to 180.
IMG_0001.JPG
.JPG | 393.4KB | IMG_0001.JPG
Summer set point, 155. Boiler will fire at 150 and run to 160.
IMG_0002.JPG
.JPG | 360.3KB | IMG_0002.JPG
The coal bin is getting low.
IMG_0004.JPG
.JPG | 335KB | IMG_0004.JPG
So low that every 5 days I can see the mouth of the auger.
IMG_0002 (2).JPG
.JPG | 509.6KB | IMG_0002 (2).JPG
In a few weeks it will be time to through in the barrel!

Here is some rare video footage of the Axeman sucking in coal. :o

-don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Apr. 15, 2023 6:36 pm

Another 7 days.
IMG_0001.JPG
.JPG | 348.8KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 3373.8 - 3343.5 = 30.3 hours of fan run time, 4.33 hours per day.
Ash reading, 1935.5 - 1920.9 = 14.6 hours of ashing, 2.09 hours per day, 48% of fan run time.
IMG_0002.JPG
.JPG | 361.7KB | IMG_0002.JPG
Ash is a bit heavier these days. Yesterday I witched to Summer settings. Boiler lowered from 175 to 155, ashing lowered from 130 to 125.
IMG_0003.JPG
.JPG | 494.2KB | IMG_0003.JPG
We have started "Shoveling Around" season. Every 4 or 5 days coal needs to be shoveled over to the middle where the auger is.
IMG_0004.JPG
.JPG | 336.9KB | IMG_0004.JPG
Today it was time to do some Spring Cleaning.

A quick bath for the Black Car.
IMG_0006.JPG
.JPG | 310.5KB | IMG_0006.JPG
IMG_0009.JPG
.JPG | 323.1KB | IMG_0009.JPG
IMG_0011.JPG
.JPG | 334.2KB | IMG_0011.JPG
IMG_0012.JPG
.JPG | 268.2KB | IMG_0012.JPG
The White Car got a quick bath too!
IMG_0016.JPG
.JPG | 336KB | IMG_0016.JPG
IMG_0019.JPG
.JPG | 429.3KB | IMG_0019.JPG
Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Apr. 22, 2023 9:04 pm

7 more days...
IMG_0001.JPG
.JPG | 373.8KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 3398.7 - 3373.8 = 24.9 hours of fan run time, 3.56 hours per day.
Ash reading, 1949.6 - 1935.5 = 14.1 hours of ashing, 2.09 hours per day, 57% of fan run time.
IMG_0002.JPG
.JPG | 357.1KB | IMG_0002.JPG
Time to shovel some coal!
IMG_0003.JPG
.JPG | 447.1KB | IMG_0003.JPG
Ash is still looking pretty good.
IMG_0004.JPG
.JPG | 358.7KB | IMG_0004.JPG
Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Apr. 29, 2023 6:33 pm

Another 7 days, this is git'in pretty boring! :o
IMG_0001.JPG
.JPG | 319.9KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 3425.6 - 3398.7 = 26.9 hours of fan run time, 3.84 hours per day.
Ash reading, 1965.4 - 1949.6 = 15.8 hours of ashing, 2.26 hours per day, 59% of fan run time.
IMG_0002.JPG
.JPG | 400.7KB | IMG_0002.JPG
Ash still looks pretty good.
IMG_0003.JPG
.JPG | 403.6KB | IMG_0003.JPG
Gofer action.
IMG_0004.JPG
.JPG | 441.7KB | IMG_0004.JPG
Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sun. Apr. 30, 2023 3:53 pm

Don at the lower speed does it fall behind during long domestic use? I feel this is a pretty taxing draw since the boiler volume is kinda small, or do you have an indirect or a holding tank or something? Can't quite recall....


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 30, 2023 4:33 pm

Retro_Origin wrote:
Sun. Apr. 30, 2023 3:53 pm
Don at the lower speed does it fall behind during long domestic use? I feel this is a pretty taxing draw since the boiler volume is kinda small, or do you have an indirect or a holding tank or something? Can't quite recall....
If by "lower speed" you are talking about the fan, 1725 RPM down to 1635 RPM isn't very much lower and shouldn't cause any DHW problems. But you have to remember that This boiler is running and AHS fan, not an Axeman fan.

I use an indirect water heater and have no DHW problems.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 07, 2023 7:43 am

The past 7 days have been much cooler than normal. 30's and 40's in the morning so we actually used some heat.
IMG_0001.JPG
.JPG | 386.7KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 3453.5 - 3425.6 = 27.9 hours of fan run time, 3.98 hours per day.
Ash reading, 1981.9 - 1965.4 = 16.5 hours of ashing, 2.36 hours per day, 59% of fan run time.
IMG_0002.JPG
.JPG | 452.4KB | IMG_0002.JPG
Ash is a bit heavy this week but we got some nice sized clinkers.
IMG_0003.JPG
.JPG | 389.4KB | IMG_0003.JPG
Still got some coal left.
IMG_0004.JPG
.JPG | 441.7KB | IMG_0004.JPG
Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. May. 13, 2023 7:28 pm

Too many Axemans! Got to make some room in here.
IMG_0003.JPG
.JPG | 380.8KB | IMG_0003.JPG
IMG_0004.JPG
.JPG | 400.5KB | IMG_0004.JPG
Over the past 7 days;
Fan reading, 3475.6 - 3453.5 = 22.1 hours of fan run time, 3.12 hours per day.
Ash reading, 1997.4 - 1981.9 = 15.5 hours of ashing, 2.21 hours per day, 70% of fan run time.
IMG_0005.JPG
.JPG | 469.6KB | IMG_0005.JPG
Ash is not great. Some clinkers, some ash and a lot of gray rocks. I decided to weigh it, 39.5 pounds.
IMG_0006.JPG
.JPG | 502KB | IMG_0006.JPG
Very soon it will be time for the barrel.
IMG_0007.JPG
.JPG | 433.6KB | IMG_0007.JPG
Current settings,

Fan RPM = 1635 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35-ish (2 teeth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sat. May. 13, 2023 8:45 pm

StokerDon wrote:
Sat. May. 13, 2023 7:28 pm
Too many Axemans!
Don, your account has been hacked! These words could never come out of your mouth! :o :o :o

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. May. 20, 2023 5:34 pm

Time for a little Rice Coal Experiment!

Mined 9 buckets of Rice coal out of the basement.
IMG_0001.JPG
.JPG | 333KB | IMG_0001.JPG
IMG_0002.JPG
.JPG | 367.7KB | IMG_0002.JPG
cleaned the Pea Coal way from the top of the Dog House.
IMG_0005.JPG
.JPG | 481KB | IMG_0005.JPG
Set the 20 gallon trash can with the hole in the bottom on top of the Dog House.
IMG_0007.JPG
.JPG | 397.5KB | IMG_0007.JPG
Filled it with Rice Coal!
IMG_0010.JPG
.JPG | 353.8KB | IMG_0010.JPG
It's about 150 pounds. 4.5 buckets at about 34 pounds each is 153. A 55 gallon barrel holds about 400 pounds, 20 is 36% of 55, 144 pounds. so we'll say it 150 pounds.

Changed the fan pulley to 3" and the gearbox pulley to 3". This will increase the fan speed to 1725 RPM and the auger speed to 5.75 RPM.
IMG_0009.JPG
.JPG | 318.2KB | IMG_0009.JPG
Over the past 7 days;
Fan reading, 3496.1 - 3475.6 = 20.5 hours of fan run time, 2.93 hours per day.
Ash reading, 2013.6 - 1997.4 = 16.2 hours of ashing, 2.31 hours per day, 79% of fan run time.
IMG_0013.JPG
.JPG | 403.2KB | IMG_0013.JPG
The Pea Coal ash is very heavy and has a lot of gray rocks in it. Hopefully the Rice Coal changes that.
IMG_0011.JPG
.JPG | 423.6KB | IMG_0011.JPG
IMG_0012.JPG
.JPG | 565.9KB | IMG_0012.JPG
Current settings,

Fan RPM = 1725 RPM (Stock AHS is 1725 RPM)
Auger speed = 5.75 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 13-ish (2 teeth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
lzaharis
Member
Posts: 2366
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Sat. May. 20, 2023 6:10 pm

I will be trying buckwheat again this fall to see how well it burns in my kaa-4-1 using 14 threads out
and reducing the coal draw point width by another inch and burn a few bags Blashack Buckwheat to
see how the coal burns and how heavy the ash is as I am still getting a great deal of dead ash that
has partially burned coal in it and rock.

I wish the eastern Anthracite was as clean and free of rock as the Sub Bituminous coal from Wyoming
and Montana.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. May. 24, 2023 7:49 pm

Well that didn't last as long as I thought it would. :o
IMG_0001.JPG
.JPG | 423.8KB | IMG_0001.JPG
Over the past 4 days;
Fan reading, 3514.9 - 3496.1 = 18.8 hours of fan run time, 4.70 hours per day.
150 pounds over 4 days is 37.5 per day. About 8 pounds per hour.

We had some problems to work through. The chimney needed a cleaning on Monday night. After that I riddled around up in the cyclone come and a whole pile of flyash stated pouring out. :what:
Filled that coffee can 1.5 times!
IMG_0004.JPG
.JPG | 338.9KB | IMG_0004.JPG
IMG_0005.JPG
.JPG | 414.2KB | IMG_0005.JPG
The fire has been buried the whole time so I reduced the auger speed to 5.03 RPM by replacing the 4" gearbox pulley with a 3.5" one.
I also reduced the ashing speed to 1 tooth and tonight I dropped the ashing temp to 120 from 125.
IMG_0006.JPG
.JPG | 395KB | IMG_0006.JPG
Put 4 buckets of Rice Coal in.
IMG_0003.JPG
.JPG | 414.1KB | IMG_0003.JPG
I'm hoping that the chimney and flyash coupled with working through some of the Pea/Rice mix caused our 37.5 pound per day average consumption.
Current settings,

Fan RPM = 1725 RPM (Stock AHS is 1725 RPM)
Auger speed = 5.03 RPM (Stock is 8.05 RPM)
Grate cycles per hour = ? (1 tooth on the ashing gear)
Aquastat = 155*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

Attachments

IMG_0002.JPG
.JPG | 447.2KB | IMG_0002.JPG

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 28, 2023 7:06 pm

The Rice Coal Experiment continues...


This has not gone the way I thought it would. I started out with the settings I ran a few years ago when I burned 5 ton of Rice. The fire kept getting berried and there were lots of puffbacks and heavy ash.

I increased the fan speed to 2208 RPM with a 4" pulley on the motor. Raised the boiler temp to 160 and raised the ashing motor cut off to 185 and decreased the ashing temp to 120.

Then I disabled the ashing overnight to get the fire to spread out the entire fire chamber. Now the fire actually breaks through the top and lights the volatiles before they go Ka BOOM! I also had to give it a bunch of overfire air by propping the fire door open and little.
IMG_0001.JPG
.JPG | 370.6KB | IMG_0001.JPG
Over the past 4 days;
Fan reading, 3530.0 - 3514.9 = 17.1 hours of fan run time, 4.28 hours per day.
150 pounds over 4 days is 37.5 per day. About 8 pounds per hour.
We'll see if we do better this week. 37 pounds a day is a lot for DHW. :what:
IMG_0002.JPG
.JPG | 396KB | IMG_0002.JPG
IMG_0003.JPG
.JPG | 383.1KB | IMG_0003.JPG
1 Day worth of ash.
IMG_0004.JPG
.JPG | 361.3KB | IMG_0004.JPG
Mined 10 buckets of Rice Coal out of the basement.
IMG_0005.JPG
.JPG | 324.5KB | IMG_0005.JPG
About 150 pounds back in the barrel.
IMG_0006.JPG
.JPG | 380.9KB | IMG_0006.JPG
Current settings,

Fan RPM = 2208 RPM (Stock AHS is 1725 RPM?)
Auger speed = 5.03 RPM (Stock is 8.05 RPM)
Grate cycles per hour = ? (1 tooth on the ashing gear)
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 185*F, Hysteresis = 0.1*

-Don