Post by Rob R. » Thu. Nov. 17, 2022 7:28 am

At one time Keystoker offered something called “The Keystoker Chimney”, I think that is what we are seeing here. In addition to the things already mentioned it would be a good idea to check the draft.


 
waytomany?s
Member
Posts: 3747
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Thu. Nov. 17, 2022 10:01 am

Rob R. wrote:
Thu. Nov. 17, 2022 7:28 am
At one time Keystoker offered something called “The Keystoker Chimney”, I think that is what we are seeing here. In addition to the things already mentioned it would be a good idea to check the draft.
Is there anything you don't know?

 
waytomany?s
Member
Posts: 3747
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Thu. Nov. 17, 2022 10:02 am

If that sounds sarcastic, it's not. I'm impressed by the depth of your knowledge.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Nov. 17, 2022 10:30 am

Not mentioned...air in system may cause little to no circulation/flow...purge air to have solid volume of flow thru baseboards.

As for the scalding DHW...we see a thermostatic mixing valve that should have that under control...may need attention??

 
k-2
Member
Posts: 1744
Joined: Thu. Sep. 28, 2017 10:57 am
Location: Coal Township Pa
Stoker Coal Boiler: K2- Keystoker
Hot Air Coal Stoker Stove: Alaska Stoker Stove
Coal Size/Type: Rice

Post by k-2 » Thu. Nov. 17, 2022 11:27 am

Scott1010 wrote:
Wed. Nov. 16, 2022 2:23 pm
So, Just bought house in upstate NY. So far 1100 pounds since Oct 27th for an 1800 sqft house. I made sure my high Low wasn't too high, it was and still is set at 160 to 180.
Iv used about 1000 pounds since mid oct this yr already and im south of you. So that s not too far off. It was crappy coal but its been unseasonably cold lately. I have 4 ton of very good coal left for the remainder of the winter. Also Ck that flue ,i have to shovel the fly ash out if mine regularly.
Last edited by k-2 on Thu. Nov. 17, 2022 11:35 am, edited 1 time in total.

 
Qtown1835
Member
Posts: 705
Joined: Sat. Nov. 08, 2014 11:47 am
Location: Quakertown, PA
Stoker Coal Boiler: Keystoker '81 KA4 (online 1/16/17)
Coal Size/Type: WAS Lehigh Rice (TBD)
Other Heating: EFM SPK600

Post by Qtown1835 » Thu. Nov. 17, 2022 11:32 am

k-2 wrote:
Thu. Nov. 17, 2022 11:27 am
Iv used about 1000 pounds since mid oct this yr already and im south of you. So that s not too far off. It was crappy coal but its been unseasonably cold lately. I have 4 ton left for the remainder of the winter. Also Ck that flue ,i have to shovel the fly ash out if mine regularly.
Considerable fly ash accumulates in my flue as well. its surprising how much makes it through 2 90*s to get to the horizontal run.

 
k-2
Member
Posts: 1744
Joined: Thu. Sep. 28, 2017 10:57 am
Location: Coal Township Pa
Stoker Coal Boiler: K2- Keystoker
Hot Air Coal Stoker Stove: Alaska Stoker Stove
Coal Size/Type: Rice

Post by k-2 » Thu. Nov. 17, 2022 11:38 am

Qtown1835 wrote:
Thu. Nov. 17, 2022 11:32 am
Considerable fly ash accumulates in my flue as well. its surprising how much makes it through 2 90*s to get to the horizontal run.
Depends on the coal ,some yrs i only have to do it once a season. One year i had to do it for every ton burned,about once a month.
I just did mine and it was 60% blocked coming out of the boiler ,50% in the 45 degree pipe after that.


 
Qtown1835
Member
Posts: 705
Joined: Sat. Nov. 08, 2014 11:47 am
Location: Quakertown, PA
Stoker Coal Boiler: Keystoker '81 KA4 (online 1/16/17)
Coal Size/Type: WAS Lehigh Rice (TBD)
Other Heating: EFM SPK600

Post by Qtown1835 » Thu. Nov. 17, 2022 11:41 am

k-2 wrote:
Thu. Nov. 17, 2022 11:38 am
Depends on the coal ,some yrs i only have to do it once a season. One year i had to do it for every ton burned,about once a month.
I just did mine and it was 60% blocked coming out of the boiler ,50% in the 45 degree pipe after that.
oh wow. Mine has never been that bad. I will run 4-5tn through it and at the end of the season there will be 1"-1.5" that i clean out. 8" flue. See how it goes this year. it will be the first full season on Blaschak.

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Nov. 17, 2022 1:03 pm

waytomany?s wrote:
Thu. Nov. 17, 2022 10:01 am
Is there anything you don't know?
There is a lot I don't know. Just ask my wife. :lol:
Scott1010 wrote:
Wed. Nov. 16, 2022 10:39 pm
I live in Apalachin, NY just west of Binghamton so technically upstate but not up up state but cold enough.
Welcome. Those of us up North would say you are in the Southern Tier....and those in NYC think we are both in Canada. :roll:

Don't get discouraged with your boiler. With some simple changes it will be running good very soon.

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Nov. 17, 2022 1:15 pm

Could you please post another picture of this area so we can better see the piping? I am trying to figure out how these two boilers are hooked together.

Attachments

Untitled.png
.PNG | 5.1MB | Untitled.png

 
lzaharis
Member
Posts: 2366
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Thu. Nov. 17, 2022 1:55 pm

They plugged the manometer probe hole in the door with silicone UGH!!

 
waytomany?s
Member
Posts: 3747
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Thu. Nov. 17, 2022 3:08 pm

lzaharis wrote:
Thu. Nov. 17, 2022 1:55 pm
They plugged the manometer probe hole in the door with silicone UGH!!
Probably too warm for a finger.

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Thu. Nov. 17, 2022 9:11 pm

That power vent could be part of the cause of hi coal consumption . ie; Sucking the heat out of the boiler , and sending it up the stack.

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Thu. Nov. 17, 2022 9:20 pm

Rob R. wrote:
Thu. Nov. 17, 2022 1:15 pm
Could you please post another picture of this area so we can better see the piping? I am trying to figure out how these two boilers are hooked together.
+ 1 on that Rob.

New guy, ......stick with this , it will all work out . It's a step by step deal , but it will work.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Nov. 19, 2022 9:04 am

Scott1010 wrote:
Wed. Nov. 16, 2022 2:23 pm
. So last night the CO2 alarm went off, I didn't have the ash door tight enough.
Seeing that you have a power stack vent pushing positive exhaust air downstream toward topside to chimney exit, your gasket imperfections at the ash door would not allow a backup of stove fumes unless fan quit or failed. So finding CO leak still remains to be found.
However that gasket imperfection at the ash door (negative pressure) does allow a surplus of mostly unregulated combustion air to enter past bad gaskets in to accelerate the fire in proportion to whatever draft the fan/chimney air is being pulled by. Bad gasket will allow little if much any fire taming control so yes you are sending too much heat up your chimney and that wastes coal!