Determining Needed Baseboard Radiation

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Jan. 09, 2022 12:45 pm

Here we go again with another Sunday fun day conversation starter.. I thought this was very exciting!

So as you guys may know, I plan to make the switch to 100% hot water baseboard heating. Currently I'm using a huge water to air heat exchanger to heat the entire downstairs with 16ft of baseboard for the 2 bedrooms upstairs.

Recently I determined my heating requirement to be ~ 47.5 pounds per day (which excludes DHW) with an average OAT of 34 degrees. This equals about 1.5 pounds of coal per heated degree based on heated to 65 degrees in the house.. Of course we like it warmer than that, we run the thermostat 73 during the day and 71 at night.

Ok.. so given we need 1.5 pounds per heated degree we can estimate our daily usage at the system design temperature of OAT at -2 degrees Fahrenheit. So, based on heated to 65 degrees in the house we need 67 degrees worth of coal at 1.5 pounds per degree. This arrives at about 101 pounds per day with an OAT of -2 degrees.

Given this information above, we now can get a really good idea of how many ft of baseboard the entire house will need. We'll use 10,000 btu per pound to factor 80% efficiency of the Axe and keep things simpler. At 101 pounds per day at design temperature of -2 we should require 1,010,000 BTUs. This works out to be about 42000 BTUs per hour which then translates into a requirement of 84 ft of baseboard that would need to run nonstop at a design temperature of -2 degrees OAT.

84 ft... why is this interesting? I also used the Omni heat loss calculator app and input each room size, number of windows, doors, exterior walls and factors insulation.. That app calculated a need of 82 ft total in the house at -2 design temp.

I was very shocked that my real world usage lined up so closely with a heat loss calculator..

Who'd a thought??


 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Jan. 09, 2022 12:54 pm

I should add that there is one other variable I did not account for.. this would be the outbuilding. We've only been keeping the outbuilding at 40 degrees which is only 6 degrees above the average OAT for that period. The outbuilding has a couple little refrigerators and other electrical things that also generate a small amount of heat. So I estimate that only a tiny amount of heat went down there. Probably the additional 2 ft of baseboard requirement I came up with :lol:

 
franco b
Site Moderator
Posts: 11417
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Sun. Jan. 09, 2022 12:57 pm

You also have to factor in the design temperature of the water.

Degree days are based on a 65 degree average outside temperature because with that average outside temperature no heat will be needed inside.

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Jan. 09, 2022 1:03 pm

franco b wrote:
Sun. Jan. 09, 2022 12:57 pm
You also have to factor in the design temperature of the water.
Right! I figured 500 BTU per foot. I'm not exactly sure what the boiler temp needs to be for that. Some baseboards are better than others also :)
franco b wrote:
Sun. Jan. 09, 2022 12:57 pm
Degree days are based on a 65 degree average outside temperature because with that average outside temperature no heat will be needed inside.
Yes, the first 5-7 degrees are heated by people, refrigerator compressors, computers, TVs, ect.. they all contribute heat to the house.

 
franco b
Site Moderator
Posts: 11417
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Sun. Jan. 09, 2022 1:11 pm

The literature for the particular baseboard should give the BTU rating for different water temperatures.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Jan. 09, 2022 1:12 pm

Length of baseboard required will vary decoding on temperature of water, and model of baseboard.

Most baseboard has literature with the output per ft at different water temps. I prefer high output baseboard, which puts out about 50% more buys per foot.

 
User avatar
BunkerdCaddis
Member
Posts: 708
Joined: Sun. Jan. 18, 2015 10:26 am
Location: SW Lancaster County
Stoker Coal Boiler: Bairmatic-Van Wert
Hand Fed Coal Boiler: Van Wert VW85H
Hand Fed Coal Stove: Saey Hanover II working when I feel the desire, Waterford 105 out on vacation, Surdiac Gotha hiding somewhere
Coal Size/Type: pea/nut/rice/stove-anthracite, nut/stove bit when I feel the urge
Other Heating: oil fired hydronic

Post by BunkerdCaddis » Sun. Jan. 09, 2022 1:51 pm

Lightning wrote:
Sun. Jan. 09, 2022 12:45 pm
Here we go again with another Sunday fun day conversation starter.. I thought this was very exciting!

I feel more enlightened already... I'm not sure what that says but :annoyed:

Anyway, that would also mean your building heatloss is "average" or is the factored amount correct, I don't know if that's good or bad?


 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Sun. Jan. 09, 2022 2:02 pm

I'm with Rob on the higher output baseboard. Higher upfront costs, but better to turn down than run out of capacity, or require higher water temps to get the output you need.

Zoning will make a difference in your required BTUs.

Heatload calcs depend on heat going ONLY where it is needed. Better targeted zoning and controlling the length of runs makes a difference.

Splitting the supply and return per zone can keep more of your baseboard at the higher supply temp vs running in one big series and the lower temps and output of baseboard farther down the line in a series.

IMHO, make the distribution as efficient as possible (multiple zones, splitting supply/return lines, higher output baseboard, insulation) and then work on the supply end, being the boiler and controls.

Chances are good that you tweak and modify the supply end in the future, but likely never change the distribution side after it is installed, so do that part right in the beginning.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Jan. 09, 2022 2:04 pm

High output baseboard costs more per foot, but you need less of it. 8-)

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Jan. 09, 2022 7:38 pm

I know you guys mean well with the top shelf baseboard but they're pretty expensive. The Slant fin Base line 2000 is only about $10 per foot and delivers 500 BTU at 170 degrees. This still leaves me wiggle room to turn the boiler temp down to 150-160 until it goes below 15-20 degrees outside, then I'd be forced to run it between 170-180 to get 500 or more BTU per foot. I don't mind turning up the boiler temp if I need to since its in the basement (standby loss contributes to heating) and the boiler and piping is mostly insulated. Plus I'm thinking that using more instead of less footage will spread out the heat distribution more evenly. I'll give it more consideration but I think the Base Line 2000 will do the job, plus I already have 36 feet of it ready to put up. Some of it was a facebook market place find that I got quite below cost :) The 81A baseboard puts out 40% more BTUs but costs about 125% more.

Also! We have the Hitzer 503 insert for auxiliary heat when it goes -15 every 10 years :D

I currently have the upstairs bedrooms on one zone. The downstairs will have at least 2 zones possibly 3.

Thank you for the fine advice fellas!

What would you say is the max baseboard footage on one zone considering its all 3/4 inch? I imagine it depends on gallons per minute but I have no idea how to measure that.

Attachments

Screenshot_20220109-151605.jpg
.JPG | 106.9KB | Screenshot_20220109-151605.jpg

 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Sun. Jan. 09, 2022 8:59 pm

Lightning wrote:
Sun. Jan. 09, 2022 7:38 pm
What would you say is the max baseboard footage on one zone considering its all 3/4 inch? I imagine it depends on gallons per minute but I have no idea how to measure that.
If you use split supply and return, you can use more feet of baseboard, since twice as much of it will be at full supply temp. Your supply is 1" and extends to roughly midpoint of your zone, tees off to two 3/4" runs of baseboard. 1" carries more BTUs

How many feet are you considering per zone?

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Jan. 09, 2022 9:14 pm

Lightning wrote:
Sun. Jan. 09, 2022 7:38 pm

What would you say is the max baseboard footage on one zone considering its all 3/4 inch? I imagine it depends on gallons per minute but I have no idea how to measure that.
It depends on flow rate and type of baseboard. Please see attached for rules of thumb on this.

Also, some good reading here: https://heatinghelp.com/systems-help-center/loop- ... g-q-and-a/

Attachments

810.pdf
.PDF | 286.7KB | 810.pdf

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Jan. 10, 2022 1:06 am


 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Mon. Jan. 10, 2022 3:45 pm

CoalisCoolxWarm wrote:
Sun. Jan. 09, 2022 8:59 pm
If you use split supply and return, you can use more feet of baseboard, since twice as much of it will be at full supply temp. Your supply is 1" and extends to roughly midpoint of your zone, tees off to two 3/4" runs of baseboard. 1" carries more BTUs

How many feet are you considering per zone?
Oh wow.. I didn't think of that but it makes really good sense!

My biggest zone will be the living room which used to be a garage. It has 3 exterior walls and seems to require a lot of heat. The heat loss calculator says to use 36 ft but I'm inclined to put in 45, 15 ft on each exterior wall. So 45 ft would be the longest zone.

I'm not sure what to do with the kitchen. Its in the middle of the house with only 1 exterior wall. The heat loss calc says it should have 1530 BTUs worth but I'm struggling to find a place for it. Would it make sense to add a little baseboard to the adjacent rooms instead?

Then there is the far room on the other side of the house. The boiler room is directly underneath it. It current has no heating but only feels slightly cooler, its also where the cold air return is so heat gets dragged out there after being pulled thru the kitchen. But of course that won't be the case once its not windy in here anymore. I'm considering giving that room its own zone so that I don't overheat it since it gets some radiant heat from underneath. My cat loves to lay on the floor directly over the Axeman, a sure sign that he's found a warm spot :lol:

 
LTStorm07
Member
Posts: 106
Joined: Tue. Sep. 11, 2012 8:32 pm
Location: Stillwater, PA
Stoker Coal Boiler: 1980 EFM DF520
Hot Air Coal Stoker Furnace: Alaska Stoker II
Coal Size/Type: Rice
Other Heating: Heat pump / Propane

Post by LTStorm07 » Mon. Jan. 10, 2022 5:49 pm

Lightning wrote:
Mon. Jan. 10, 2022 3:45 pm
I'm not sure what to do with the kitchen. Its in the middle of the house with only 1 exterior wall. The heat loss calc says it should have 1530 BTUs worth but I'm struggling to find a place for it. Would it make sense to add a little baseboard to the adjacent rooms instead?
Just a thought I had, but what about a through wall vent or two located between rooms? I know some are powered but for as little BTU input you need, that might be the ticket?