Coalgun s130 adjustment

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sat. Dec. 18, 2021 9:18 pm

coaledsweat wrote:
Sat. Dec. 18, 2021 1:00 pm
It's a safety device. An aquastat can fail "on" and that would be a disaster.
That's probably the scariest thing I've read in a while...why do some boilers have a dump zone and others just have a high limit cutoff? And some have both, right?

My keystoker wants the L4006B and my AA wants the L4006A. I understand the norm. open / norm. closed difference and how the wiring all works. Am I correct in saying these are just two separate ways of preventing a disaster? (one kills, the other dumps)

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Dec. 19, 2021 9:54 am

Retro_Origin wrote:
Sat. Dec. 18, 2021 9:18 pm
That's probably the scariest thing I've read in a while...why do some boilers have a dump zone and others just have a high limit cutoff? And some have both, right?

My keystoker wants the L4006B and my AA wants the L4006A. I understand the norm. open / norm. closed difference and how the wiring all works. Am I correct in saying these are just two separate ways of preventing a disaster? (one kills, the other dumps)
You are correct.

The “dump” is optional but the high/high limit is a often overlooked required safety.

I don’t run a dump zone but still make good use of that N/O contact by toggling on a neon or LED indicator light which shows exactly that the H/HL has been activated. This saves wondering what stopped or killed the boiler…and it will automatically reset after boiler temperature cools sufficiently.


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Dec. 19, 2021 10:03 am

lzaharis wrote:
Sat. Dec. 18, 2021 5:31 pm
It is just like the one I have mounted on the kaa-4.
No it isn't.

Here is a short aquastat recognition guide.
IMG_0001.JPG
.JPG | 310.6KB | IMG_0001.JPG
Type L4006A Single Aquastat. Can be used for boiler control or high limit or dump zone activation.
IMG_0002.JPG
.JPG | 359.4KB | IMG_0002.JPG
IMG_0005.JPG
.JPG | 345KB | IMG_0005.JPG
Type L4081B Dual Aquastat. Can be used for high limit and dump zone activation.
IMG_0003.JPG
.JPG | 303.2KB | IMG_0003.JPG
IMG_0006.JPG
.JPG | 254.1KB | IMG_0006.JPG
Type L8124L Triple Aquastat Relay. Used for boiler control.
IMG_0004.JPG
.JPG | 412.1KB | IMG_0004.JPG
IMG_0007.JPG
.JPG | 300.1KB | IMG_0007.JPG
I hope that helps!

-Don

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Dec. 19, 2021 11:35 am

Retro_Origin wrote:
Sat. Dec. 18, 2021 9:18 pm
That's probably the scariest thing I've read in a while...why do some boilers have a dump zone and others just have a high limit cutoff? And some have both, right?

My keystoker wants the L4006B and my AA wants the L4006A. I understand the norm. open / norm. closed difference and how the wiring all works. Am I correct in saying these are just two separate ways of preventing a disaster? (one kills, the other dumps)
A dump zone is most useful for scrubbing off a little extra heat in the event the boiler overshoots the setpoint a bit, or gets hot from running on the timer cycles. A dump zone will not be helpful in a runaway boiler situation unless the zone can absorb the full output of the boiler.