Radient floor Pex under plywood ..insulation thoughts?

Post Reply
 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Fri. Dec. 17, 2021 4:12 pm

Tore out a bunch of pink fiberglass insulation from my basement ceiling to access the tubing. What insulation do most folks use in this type of application? Would prefer to use something that won't get wrecked if that zone leaks somewhere. Thanks Ron

 
User avatar
Rob R.
Site Moderator
Posts: 18003
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Dec. 17, 2021 4:24 pm

For that type of radiant I have always seen it insulated with fiberglass bats. Rockwool would handle a leak better, but is more expensive. If the whole job is already insulated with fiberglass I would stick with that.

 
KLook
Member
Posts: 5791
Joined: Sun. Feb. 17, 2008 1:08 pm
Location: Harrison, Tenn
Other Heating: Wishing it was cold enough for coal here....not really

Post by KLook » Fri. Dec. 17, 2021 7:00 pm

We tore my brothers out when he had to replace the tubing and when we put it back up it was Blue styrofoam. Fiberglass sucks. For many reasons.

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Fri. Dec. 17, 2021 8:17 pm

When I was plumbing we always used foil.... sometimes foil faced fiberglass, other times foil bubble wrap alone, or bubble wrap under some other insulation. The foil must be a minimum of 2" below the tubing.


 
User avatar
Rob R.
Site Moderator
Posts: 18003
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Dec. 17, 2021 9:03 pm

The foil faced bubble wrap works good until it gets dusty on top.

 
User avatar
franpipeman
Member
Posts: 690
Joined: Fri. Jan. 11, 2008 4:27 pm
Location: Wernersville pa
Stoker Coal Boiler: efm 520 stoker fitzgibbons pressure vessel
Hand Fed Coal Stove: harman, russo
Coal Size/Type: rice
Other Heating: alpine propane condensing boiler radiant floor

Post by franpipeman » Tue. Dec. 21, 2021 8:29 am

I used precut reflective bubble wrap to insulate the floor joists. While when it gets dusty it reduces the radiant reflectance, it still makes a captured convection to be trapped in the joist cavity and directed at the floor above rather than the basement , which still obtains some of the leaking heat which for us is fine as by coincidence everything balances out quite well a two space for one installation idea. I also have a drop acoustical tile ceiling which capture more heat. Dont put your wi fi router up there as i did as it gets too hot for it , in my opinion

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Dec. 22, 2021 10:48 am

I am installing radiant pex in my house next spring, then finishing the downstairs ceiling with white tin, was thinking of just using the cheap foil faced stuff… thoughts?

 
coalmanjoe
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:21 am
Location: Mt. Carmel
Stoker Coal Boiler: EFM 520
Coal Size/Type: Rice

Post by coalmanjoe » Thu. Dec. 23, 2021 7:14 am

The placement and type of insulation depends upon whether or aluminum transfer plates are used. I used Uponor plates which are heavier extruded plates (they are not cheap) which are first screwed to the underside of the floor and afterwards the pex is pushed/pounded in with a rubber mallet. Uponor specifically states that fiberglass insulation should be placed directly against the plates and tight to the floor. I have the radiant system under wood look ceramic tile on a ditra mat throughout the house except for the bedrooms where I have copper fin baseboard. The radiant zone consists of 9 loops of 1/2" pex none being longer than 275 feet. I have R 30 unfaced fiberglass in my 2x10 floor joists and 1/2" polyiso foam board on the bottom of the joists in the basement. ***It is critical to insulation properly against the rim joists as heat goes to cold and will migrate outwards. I cut 1 1/2" polystrene foam and place it in the joist bays against the rim joists. I have an EFM 520DF with primary/secondary piping and am heating my 2100 square foot rancher burning no more than 5 tons YEAR ROUND------including our domestic hot water. Finally, once you have radiant you won't want any other type of system although cast iron baseboard is also excellent----I actually have a 2 foot section of Burnham cast iron BB behind my toilets as part of the radiant loops in our bathrooms as you can't place the pex too close to the wax seals. Feel free to pm me with any questions and I want to wish you and everyone on this great forum a Merry Christmas and a happy, healthy, and safe new year.


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. Dec. 23, 2021 8:49 pm

This is what I plan on using, I have fully insulated rim joist with 2” foam board spray foamed in already.

Attachments

1CAD4645-2899-4A70-82E3-C1CE8A0827D0.png
.PNG | 726.1KB | 1CAD4645-2899-4A70-82E3-C1CE8A0827D0.png
7C011261-10C0-47B9-BF3C-CA82CF65CB25.png
.PNG | 258.3KB | 7C011261-10C0-47B9-BF3C-CA82CF65CB25.png

 
User avatar
franpipeman
Member
Posts: 690
Joined: Fri. Jan. 11, 2008 4:27 pm
Location: Wernersville pa
Stoker Coal Boiler: efm 520 stoker fitzgibbons pressure vessel
Hand Fed Coal Stove: harman, russo
Coal Size/Type: rice
Other Heating: alpine propane condensing boiler radiant floor

Post by franpipeman » Fri. Dec. 24, 2021 8:26 am

KLook wrote:
Fri. Dec. 17, 2021 7:00 pm
We tore my brothers out when he had to replace the tubing and when we put it back up it was Blue styrofoam. Fiberglass sucks. For many reasons.
what kind of tubing was it that required removal?

 
KLook
Member
Posts: 5791
Joined: Sun. Feb. 17, 2008 1:08 pm
Location: Harrison, Tenn
Other Heating: Wishing it was cold enough for coal here....not really

Post by KLook » Fri. Dec. 24, 2021 9:04 am

It was the Goodyear rubber hose that had a class action lawsuit filed and won. Sure was easy to put in with a staple gun but it became hard and brittle and sprung many leaks. Luckily? for him, it was a crawlspace not a finished basement under it.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Dec. 24, 2021 2:41 pm

KLook wrote:
Fri. Dec. 24, 2021 9:04 am
It was the Goodyear rubber hose that had a class action lawsuit filed and won. Sure was easy to put in with a staple gun but it became hard and brittle and sprung many leaks. Luckily? for him, it was a crawlspace not a finished basement under it.
My grandfather has something extremely similar in his house that is just stapled in with like fence staples.. same stuff?

 
KLook
Member
Posts: 5791
Joined: Sun. Feb. 17, 2008 1:08 pm
Location: Harrison, Tenn
Other Heating: Wishing it was cold enough for coal here....not really

Post by KLook » Fri. Dec. 24, 2021 3:09 pm

Yes, it should be replaced. It is just a matter of time.

Goodyear made it and it was called Entran II and there was an Entran 3 and a lawsuit.