"Best" Constant circulator for primary loop?

Post Reply
 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Thu. Dec. 16, 2021 4:12 pm

My primary loop is about 20-25ft total that goes horizontally down the wall, up about 18 inches and back.

I am considering running a circulator constantly. Currently has Taco 007.

This is to allow my Living Room to gravity flow as well as run its zone pump (simply remove the flow check).

The 007 is a good little circulator, but is there something better and more efficient for 100% duty cycle?

Thanks.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Dec. 16, 2021 4:32 pm

What flow rate do you need through that loop? What size is the piping?

 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Thu. Dec. 16, 2021 5:01 pm

Rob R. wrote:
Thu. Dec. 16, 2021 4:32 pm
What flow rate do you need through that loop? What size is the piping?
Actually I have to make a correction to add about 12ft of 1.5" cast iron, then reduced into the rest is 1.25" copper.

I had forgotten I doubled the length of the copper primary to add the extra zones.

This is Keystoker KA6.

According to this excerpt from PexSupply/com, 8.2-16.3gpm is the recommended range for the piping.

Not sure what the Keystoker wants ideally. I have forgotten a whole lot of stuff, so if I'm asking repeated questions, just raise a cup of coffee, have a chuckle about it, and be gentle. LOL

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Dec. 16, 2021 6:35 pm

Just run the 007 until it dies, then replace with an 007E or equivalent.

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Dec. 16, 2021 7:31 pm

I'm pretty happy with this little guy right here.. 85 watts

Attachments

20211216_192930.jpg
.JPG | 202KB | 20211216_192930.jpg
20211216_192903.jpg
.JPG | 465.9KB | 20211216_192903.jpg


 
User avatar
dbsuz05
Member
Posts: 191
Joined: Thu. Nov. 28, 2013 8:09 am
Location: Central Pennsylvania
Stoker Coal Boiler: Axeman Anderson
Hand Fed Coal Boiler: Burnham 23"

Post by dbsuz05 » Thu. Dec. 16, 2021 7:55 pm

I have a Wilo 3 speed pump. Ran for 8 years 24-7 about 8 months out of the year. I’d say It’s good. Very quiet on the 65 watt setting. It had no problem circulating water from garage underground to the house through primary/secondary system with huge rads. It’s surprising how much just 65 watts will do. Even though you can run it on speed 3 with 110 watts.

 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Thu. Dec. 16, 2021 8:13 pm

Thanks.

I have a situation where the pump is running continuously right now, though it isn't firing the stoker from a call for heat. Not sure if it used to do that before? Maybe, maybe not.

But now I'm wondering if it will hold up. If so, great. If not, when I get a replacement on hand, which one to get.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Dec. 16, 2021 8:28 pm

I have a Grundfos Alpha on my primary loop, it draws 23 watts

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Dec. 16, 2021 8:33 pm

Rob R. wrote:
Thu. Dec. 16, 2021 8:28 pm
I have a Grundfos Alpha on my primary loop, it draws 23 watts
What the hell.. a couple double A batteries could run that thing :lol:

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Dec. 16, 2021 8:49 pm

Lightning wrote:
Thu. Dec. 16, 2021 8:33 pm
What the hell.. a couple double A batteries could run that thing :lol:
I know, it is pretty amazing. There are 3 of those circulators in my system, even with all zones calling for heat the 3 circulators barely draw 100 watts.


 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Thu. Dec. 16, 2021 9:22 pm

Rob R. wrote:
Thu. Dec. 16, 2021 8:49 pm
I know, it is pretty amazing. There are 3 of those circulators in my system, even with all zones calling for heat the 3 circulators barely draw 100 watts.
That's pretty sweet! The 007 I have is .71 amps, so about 85 watts

 
LTStorm07
Member
Posts: 106
Joined: Tue. Sep. 11, 2012 8:32 pm
Location: Stillwater, PA
Stoker Coal Boiler: 1980 EFM DF520
Hot Air Coal Stoker Furnace: Alaska Stoker II
Coal Size/Type: Rice
Other Heating: Heat pump / Propane

Post by LTStorm07 » Thu. Dec. 16, 2021 9:28 pm

Rob R. wrote:
Thu. Dec. 16, 2021 8:49 pm
I know, it is pretty amazing. There are 3 of those circulators in my system, even with all zones calling for heat the 3 circulators barely draw 100 watts.
I'm right there with you Rob. I went with Alphas as well after comparing too many pumps. They were the strongest, most efficient pumps. Definitely beat out Taco in that area. I put an extra on the shelf for that middle of the night pump died insurance plan.

 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Thu. Dec. 16, 2021 11:31 pm

Which Alpha do you have?

Which model is a good replacement for the Taco 007 in my size primary loop?

https://product-selection.grundfos.com/products/a ... tab=models

https://product-selection.grundfos.com/products/a ... tab=models

 
LTStorm07
Member
Posts: 106
Joined: Tue. Sep. 11, 2012 8:32 pm
Location: Stillwater, PA
Stoker Coal Boiler: 1980 EFM DF520
Hot Air Coal Stoker Furnace: Alaska Stoker II
Coal Size/Type: Rice
Other Heating: Heat pump / Propane

Post by LTStorm07 » Fri. Dec. 17, 2021 12:05 am

CoalisCoolxWarm wrote:
Thu. Dec. 16, 2021 11:31 pm
Which Alpha do you have?

Which model is a good replacement for the Taco 007 in my size primary loop?

https://product-selection.grundfos.com/products/a ... tab=models

https://product-selection.grundfos.com/products/a ... tab=models
I went with Alpha 1s because I was focused on gpm, head, and watts. The Alpha 2s have more fancy features but for an extra $30 per pump and to not use the extras was a waste to me. I just wanted the pump to basically take my target gpm based on head and adjust automatically which is exactly what the alpha 1 series does.

I bought these specific ones and it will replace your Taco 007 easily:
https://www.supplyhouse.com/Grundfos-99287256-ALP ... rminal-Box

Brochure for it:
https://www.pexuniverse.com/uploads/docs/pdf/alph ... ochure.pdf