Bleeding secondary loops
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
No, but it creates challenges in removing the air. When you mix down to a low temperature most of the water in that loop stays in that loop, only a small portion goes through the boiler. Try adjusting the mixing valve to a high temperature and running it for a few days. This will result in a more direct path for the water to go through the boiler and air scoop.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Note to self…when piping for a low temperature loop using a mixing valve remember to add a quick purge stop valve and boiler drain to rapid purge/flush just ahead of the mixing valve for immediate air removal at time of first fill of system . Also allow for a garden hose connection for house pressure to be temporary introduced at time of system fill and air purge.
YouTube has many videos of different air purge configurations.
YouTube has many videos of different air purge configurations.
-
- Member
- Posts: 438
- Joined: Wed. Dec. 07, 2016 3:57 pm
- Location: north west of Pitts Pa.
- Stoker Coal Boiler: AHS S-130
- Coal Size/Type: pea/anthracite
Great video thanks a lot. I got a lot of banging going on in my 1 zone, I think the video will be a big help. as will any info you all give me. THANKS AGAIN!!