AHS S130 boiler installed low grate temp

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Fri. Nov. 26, 2021 9:30 am

Cannot get the grate temp above 70 deg. Been running good for 30 hrs now floors are warm. Jeff from AHS had me set the grate pause timer to 0 so that the grate will cycle when the fan runs. Since there is no signal to it due to the low temp. Anyone else experience this with a coal gun?


 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Nov. 26, 2021 10:05 am

Have you put a load on the boiler to establish a fire? You need to make it run hard.

 
User avatar
coaledsweat
Site Moderator
Posts: 13761
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Fri. Nov. 26, 2021 10:18 am

You've been burning 30 hours now? Axemans and AHS boilers have a very specific start up procedure to avoid a lot of grief. Can you explain the process you used to start the initial fire? If you started the fire on the grate, your problem most likely started right there.

 
User avatar
StokerDon
Site Moderator
Posts: 7484
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Nov. 26, 2021 10:37 am

Dudest wrote:
Fri. Nov. 26, 2021 9:30 am
Cannot get the grate temp above 70 deg.
Welcome to the forum Dude,

If this is a new install, make sure the ash temperature sensor is installed correctly and in the right place. If it's only seeing 70 degrees it must not be very close to the bottom of the 180 degree boiler.

Is this a remote install? Do you have it in a cold outbuilding? If so, it will be drawing in colder than normal air into the base. If this is the case you will need to lower the ashing temperature.

-Don

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Fri. Nov. 26, 2021 12:35 pm

Thanks for the replies. I followed the exact procedure on start up and loaded it the best I could. Opened all the windows and set the heat to 82. Having a good fire still going good..
AHS says run it. What do u think? BTW Jeff is a great guy.

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Fri. Nov. 26, 2021 2:59 pm

Ive never seen an ash temp that low on mine.
Within 2hrs of startup and good load i was at 150

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Fri. Nov. 26, 2021 5:23 pm

How many inches is your sensor above the grate?


 
User avatar
nepacoal
Member
Posts: 1690
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Fri. Nov. 26, 2021 6:26 pm

Those probes can go bad... Have you tried using a lighter to see if the temp climbs with actual flame applied?

 
Jkohanski
Member
Posts: 252
Joined: Mon. Nov. 25, 2019 11:11 pm
Location: ringoes, nj central west jersey near pA border
Stoker Coal Boiler: ahs s260
Coal Size/Type: pea
Other Heating: fuel oil
Contact:

Post by Jkohanski » Fri. Nov. 26, 2021 7:31 pm

I think either thermocouple or controller has an issue. I have never seen mine behave like that.

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Wed. Dec. 01, 2021 7:09 pm

Boiled water and wet a rag...temp indicator went up immediately.

 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Dec. 01, 2021 7:10 pm

Dudest wrote:
Wed. Dec. 01, 2021 7:09 pm
Boiled water and wet a rag...temp indicator went up immediately.
Did you enable the ashing? it should run the grate until the setpoint is reached.

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Wed. Dec. 01, 2021 7:10 pm

Ill measure the height of the thermocouple tomorrow. Thanks again.

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Wed. Dec. 01, 2021 7:13 pm

Hi Rob. It only runs when the fan is enabled (0 pause setting). Is what AHS said to do since I can't hit 130 on the grate.

 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Dec. 01, 2021 7:20 pm

Well, I am not normally one to disagree with the folks that make the equipment, but if the fire has not migrated to the grate by now, I don't think it will on its own.

 
Dudest
Member
Posts: 77
Joined: Thu. Nov. 18, 2021 7:05 pm
Stoker Coal Boiler: AHS S130
Coal Size/Type: Anth. Pea
Other Heating: Lopi Liberty

Post by Dudest » Wed. Dec. 01, 2021 7:52 pm

Got it up to 120...but only 81 when I got home from work.


Post Reply