A hydronic loop (Secondary loop) has 10 feet of head, does it make any difference to mount the circulator at the lowest point or the highest point? Though not normally an option, it would be possible in this situation. I am thinking it would not make a difference but can't seem to rule it out. :annoyed:

 
User avatar
Rob R.
Site Moderator
Posts: 17981
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Nov. 17, 2021 10:30 pm

High or low doesn't matter to the circulator...but I would mount it low. In the event you get some air in the loop it will end up at the highest point.


 
User avatar
BunkerdCaddis
Member
Posts: 708
Joined: Sun. Jan. 18, 2015 10:26 am
Location: SW Lancaster County
Stoker Coal Boiler: Bairmatic-Van Wert
Hand Fed Coal Boiler: Van Wert VW85H
Hand Fed Coal Stove: Saey Hanover II working when I feel the desire, Waterford 105 out on vacation, Surdiac Gotha hiding somewhere
Coal Size/Type: pea/nut/rice/stove-anthracite, nut/stove bit when I feel the urge
Other Heating: oil fired hydronic

Post by BunkerdCaddis » Wed. Nov. 17, 2021 10:35 pm

Thank you Rob,
I was not thinking about trapped air, where I was going to put it is where it will go (which was at the bottom of the loop).

 
ziggy87
Member
Posts: 311
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Thu. Nov. 18, 2021 7:40 pm

Bottom of the look is always best. As Rob said high or low, the circulator does not care.