Lets talk liners coming from a EFM furnace

Post Reply
 
djm123456
New Member
Posts: 18
Joined: Thu. Jul. 15, 2021 9:11 pm
Stoker Coal Boiler: EFM
Coal Size/Type: rice

Post by djm123456 » Sat. Aug. 21, 2021 9:24 pm

Pipe from stoker is about 8 inches being connected to 6 " liners. Doesnt this move smoke backwards so chimney cant breath correctly shouldnt it be 8 to 8 or like 8 to 7??? Is liner installed wrong??

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Sat. Aug. 21, 2021 10:35 pm

Yes it should be 8 to 8. If there is positive pressure over the fire when running, then you have three options. Lower the firing rate of the furnace, or install a booster fan at the smoke pipe, or a larger chimney liner.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sun. Aug. 22, 2021 9:26 am

Why is the chimney lined?

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sun. Aug. 22, 2021 10:07 am

Aaaaahaaaa--real good question!!!!!!!!!!!!!!!!!!!!!!!!!!!! Some idiot had to talk him into it!!!!!!!!!!!!!!!!!!!!!!! :(


 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Aug. 22, 2021 11:53 am

A 6" liner is undersized for an EFM. If the chimney is tall enough you can probably get by with the stoker on a low firing rate, but it is not ideal.

If the chimney is structurally sound you should not need a liner at all for an EFM.

 
ziggy87
Member
Posts: 311
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Sun. Aug. 22, 2021 8:58 pm

Liners should always be bigger then pipe size leaving heating unit. You could probably get away with 7” depending on the height of the chimney. Worst that will happen is that you will not get full capacity out of the stoker due to the draft over the fire going positive.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. Aug. 23, 2021 9:30 am

In most cases, unless there is something seriously wrong with the chimney, the last thing it needs is a liner. However, they seem to be an easy sell and are very profitable, hence the big push to line a chimney. It's called profit.