EFM stoker won't heat up

 
coaledfeat
Member
Posts: 33
Joined: Thu. May. 07, 2015 12:51 pm
Location: NY Columbia County
Stoker Coal Boiler: 1982 efm df520
Coal Size/Type: Cornwall rice
Other Heating: VC winterwarm wood

Post by coaledfeat » Sat. Mar. 20, 2021 11:13 am

Time to get dirty! Let the fire go out, empty the barrel, remove the large chunks ( m y guess) lift the pawls and turn the auger backward to empty it. manually crank fresh coal till burn pot is full. the usual clues are CO alarm and hot auger tube. I was using wet coal causing sludge caking. Now I control dust with a hood and shopvac. Sounds like a vintage unit, might be auger is too worn to supply enough fuel. Hope any of these help, Gary.

 
Phil May
Member
Posts: 320
Joined: Sun. Nov. 06, 2011 9:12 pm
Location: Wellsville NY
Stoker Coal Boiler: EFM 700
Hot Air Coal Stoker Stove: Liesure Line
Coal Size/Type: Rice

Post by Phil May » Tue. May. 11, 2021 11:49 am

I would check behind the grates to make sure it is not built up plugging partialy the air to the fire.

 
User avatar
CoalHeat
Member
Posts: 8862
Joined: Sat. Feb. 10, 2007 9:48 pm
Location: Stillwater, New Jersey
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert

Post by CoalHeat » Tue. May. 11, 2021 12:15 pm

I'm suspicious of the coal he's been burning. Even if you ran in different coal there could be a lot of muck clogging up the works if it was really dirty bank coal.
EFM's are designed to burn rice or buck. I generally stick with rice as it's easier on the auger and seals up the feed tube tighter than buck.


 
todapark
New Member
Posts: 5
Joined: Mon. Mar. 15, 2021 4:23 pm

Post by todapark » Tue. Oct. 12, 2021 1:55 pm

Problem solved, been awhile but we finally removed the fire pot assy and found the ring on the bottom of the pot where the grates sit against had a 1/4 inch crack thus allowing the blower air to enter the auger pipe and blow fumes up thru the hopper and not giving enough air to get a good flame and bring the unit up to temp, really not sure why or how it got cracked, however I convinced the home owner to use good coal and not the dirty inconsistent sized discount coal he had been buying. Had someone weld and grind smooth the crack in the cast iron pot, bought new grates and re-assembled the unit, fired it up and now all is fine, temp goes up nicely and no fumes from the hopper, this one had me puzzled as everything looked fine until we removed the fire pot and dis-assembled it and then could see the crack. And yes I know cast iron is difficult to weld but we had a guy who is a pro at cast iron welding do it, he works as a welder for a boiler maker company and welds cast iron on a daily basis at his regular job. Thanks for all the advice, hope no one else has a problem like this.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Oct. 12, 2021 2:32 pm

Thanks for the Return and Reply. Sure others can learn from your experience.

 
Gene315
Member
Posts: 143
Joined: Mon. Jan. 15, 2024 4:16 pm
Stoker Coal Boiler: DS SB200
Coal Size/Type: Rice Anthracite
Other Heating: Oil

Post by Gene315 » Tue. Jan. 16, 2024 11:09 pm

*****Never mind I see it was solved******Interesting. I'm having this same issue with my new DS SB200 except for the blow back into hopper sounds exactly the same..Ever remedy this and if so what was the deal? 4 ton in one month and water doesn't get above 140 when thermostats are calling for heat..