Hello this is my first coal furnace and I keep having this problem for over two weeks every time I go to my furnace the fire is out I Call a Plumer multiple times but I keep having the same problem The fire keeps going of What I notice is that it’s takes forever to turn on And once it turns on the fire it’s already out
I have it in
4 coal
4 air
The chimney is clean
I have it in
4 coal
4 air
The chimney is clean
Attachments
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
how handy w/ electric are you? maybe don't call a plumber???
is the shiny clock motor warm or cold to the touch?
take a marker or crayon and mark 1 very fine line on the notched tripper wheel...then watch if mark moves/turns...
is the shiny clock motor warm or cold to the touch?
take a marker or crayon and mark 1 very fine line on the notched tripper wheel...then watch if mark moves/turns...
Last edited by McGiever on Thu. Jun. 11, 2020 9:58 am, edited 3 times in total.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
That is a highly reliable Wilburt Timer...
Right now the clock is hot
what I notice is that the boiler will start wen the temperature is 175 and will heat for 9 minute then it will stop at 190
And it will not star again until is 175 that takes about 2 hours so is turning on every 2 hr for 9 minute
The setting in the back is 160Lo 200Hi 15Dif
what I notice is that the boiler will start wen the temperature is 175 and will heat for 9 minute then it will stop at 190
And it will not star again until is 175 that takes about 2 hours so is turning on every 2 hr for 9 minute
The setting in the back is 160Lo 200Hi 15Dif
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Angel wrote: ↑Thu. Jun. 11, 2020 9:57 amRight now the clock is hot
what I notice is that the boiler will start wen the temperature is 175 and will heat for 9 minute then it will stop at 190
And it will not star again until is 175 that takes about 2 hours so is turning on every 2 hr for 9 minute
The setting in the back is 160Lo 200Hi 15Dif
The hot timer clock motor indicates timer is not dead.
Timer's job is to cycle an ?interval? for a ?duration? and to repeat again forever... if a single aquastat was added before or was desired now it could allow boiler temps up to 200* before cutting out stoker. Further more this added aquastat could have a narrow diferential to not wait so long to resume the needed 'hold-fire' timer function...
Last edited by McGiever on Thu. Jun. 11, 2020 11:00 am, edited 2 times in total.
Den034071
That’s a perfect idea
A las plumer came las week told me that my HI and LO where off and left
I call him yesterday and told him the problem was not fix so he came and told me that the tube that connects the boiler with the chimney was dirty but my chimney was clean He told me that maybe that was the problem also he checked the timer and told me that it was off so he set it up for three minutes every 30 minutes And he left again
Right now I decided to time it So I can give you guys a better understanding
The boiler start at 9:40 am
Temperature was 175
Run for 9 minute
Stop on wen it hits 190
I will check the temperature every five minute Until it turns back on
5 min 190
5 min 191
5 min 192
5 min 191
5 min 191
5 min 191
5 min 191
5 min 189
5 min 189
5 min 189
5 min 189
Right now is 10:43 AM and it haven’t turn on yet since 9:40 am
George form PA Hazleton
That’s a perfect idea
A las plumer came las week told me that my HI and LO where off and left
I call him yesterday and told him the problem was not fix so he came and told me that the tube that connects the boiler with the chimney was dirty but my chimney was clean He told me that maybe that was the problem also he checked the timer and told me that it was off so he set it up for three minutes every 30 minutes And he left again
Right now I decided to time it So I can give you guys a better understanding
The boiler start at 9:40 am
Temperature was 175
Run for 9 minute
Stop on wen it hits 190
I will check the temperature every five minute Until it turns back on
5 min 190
5 min 191
5 min 192
5 min 191
5 min 191
5 min 191
5 min 191
5 min 189
5 min 189
5 min 189
5 min 189
Right now is 10:43 AM and it haven’t turn on yet since 9:40 am
George form PA Hazleton
- nepacoal
- Member
- Posts: 1696
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
Did your plumber actually clean the stovepipe that goes between the chimney and boiler? A stovepipe full of fly ash will cause outfires but I didn't suggest that earlier since you said the chimney was clean... If the stovepipe is now clean, you should not have any issues with outfires once you get the timer working correctly.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Tell us how long ago stove pipe was cleaned...was stove pipe disassembled for total interior back into stove outlet, as *NEAPACOAL* has asked?
As you noted earlier the boiler temp requires now a 15* drop before next firing cycle...your timer is missing 'hold-fire' for too long waiting to drop the large 15 degees.
As you noted earlier the boiler temp requires now a 15* drop before next firing cycle...your timer is missing 'hold-fire' for too long waiting to drop the large 15 degees.
- Rob R.
- Site Moderator
- Posts: 17977
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
Although those timers are very reliable, after a few decades of service the microswitch can quit working. I am referring to Item #3 in the attached parts list.
When that switch drops into the slot on your timer wheel, you should find power at terminal #4 in the timer with a meter. If you do not, the switch needs to be replaced.
Also, in addition to cleaning the boiler and flue pipe well, I would also make sure your draft control on the flue pipe is not sticking, and check the inlet of your auger (in the bin) for debris.
When that switch drops into the slot on your timer wheel, you should find power at terminal #4 in the timer with a meter. If you do not, the switch needs to be replaced.
Also, in addition to cleaning the boiler and flue pipe well, I would also make sure your draft control on the flue pipe is not sticking, and check the inlet of your auger (in the bin) for debris.