Post by franpipeman » Wed. Oct. 07, 2020 9:13 am

This is the most versatile pvc cutter i have ever used. while i like a rachet Rob is right with brittle pipe it counter productive
https://www.supplyhouse.com/Pasco-4336-S-Cable-Sa ... -oQAvD_BwE


 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Thu. Oct. 08, 2020 2:33 pm

installing new cold water lines and installing the water softener today.
got about 1100 dollars worth of stuff in my shopping carts at supply house and pex universe. it will go up once i figure out what length 1 1/4" pipe nipples and fittings i need.

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Thu. Oct. 08, 2020 2:36 pm

Should i order 1" pex and fittings for the baseboards?
3/4" pex has a much smaller inside diameter than 3/4" copper.
want to do this right the first time.
back to it in a few minutes.
the cpvc glue was getting to me lol had to take a break.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Oct. 08, 2020 3:22 pm

lincolnmania wrote:
Thu. Oct. 08, 2020 2:36 pm
Should i order 1" pex and fittings for the baseboards?
It depends upon the total run length your single longest zone loop, and the capabilities of your circulator, and how many BTUH you need to deliver within this loop alone.

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Thu. Oct. 08, 2020 4:18 pm

lsayre wrote:
Thu. Oct. 08, 2020 3:22 pm
It depends upon the total run length your single longest zone loop, and the capabilities of your circulator, and how many BTUH you need to deliver within this loop alone.
it's 55 foot of baseboard, original house, under 800 sq foot, 26'x33' is the first zone i will be installing. the other zone will be the water to air heat exchanger for the addition till i can afford the rest of the baseboard. third zone will be the garage.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Oct. 08, 2020 4:22 pm

lincolnmania wrote:
Thu. Oct. 08, 2020 4:18 pm
it's 55 foot of baseboard, original house, under 800 sq foot, 26'x33' is the first zone i will be installing. the other zone will be the water to air heat exchanger for the addition till i can afford the rest of the baseboard. third zone will be the garage.
What will be the total run length in feet for this loop? (PEX plus baseboards, etc..., from circulator out to circulator in)

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Thu. Oct. 08, 2020 9:57 pm

lsayre wrote:
Thu. Oct. 08, 2020 4:22 pm
What will be the total run length in feet for this loop? (PEX plus baseboards, etc..., from circulator out to circulator in)
approx 120 foot.


 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Thu. Oct. 08, 2020 11:56 pm

looks like my engine hoist will work fine for moving the efm 350 into place.....got 26" between legs, boiler is 24" wide.

mostly done with the plumbing, need to run a non softened line to the outside faucet and to the garage. also have to do final hookups to well pump and the addition and front bathroom.
also have to install the drain for the water softener. going to put the trap in the bathroom closet. want that trap to be higher than the shower trap and the toilet.

need to install the mixing valve too but need to fix the wall and waterproof before i add a piece of plywood to mount the boiler plumbing.

worked 14 hrs today on the house.....pooped.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Oct. 09, 2020 5:04 am

lincolnmania wrote:
Thu. Oct. 08, 2020 9:57 pm
approx 120 foot.
I believe that 3/4" PEX should suffice for a higher head capable circulator such as the Grundfos Alpha. I'm assuming 0.681" ID. The Alpha can deliver 3 GPM into 15 Ft. of friction head. For comparison, the Taco 007 can only deliver 3 GPM into 9 feet of friction head.

3 GPM should carry 30,000 BTUH at a Delta_T of 20 degrees. 30,000/55 = 545 BTUH per foot of HWB.

55 feet of HWB on a single zone should witness right around a 20 degree Delta_T (or temperature drop).

30,000/800 = 37.5 BTUH per sq-ft of floor space. The equivalent of 11 Watts per sq-ft for the case of electric baseboards.

If your area has ~5,700 annual HDD's, which is what I'm seeing for downtown Birdsboro provided that I'm doing the search correctly, then you might find that 25 BTUH per sq-ft is sufficient. That would be 2 GPM flow through your zone. If your elevation is greater than Birdsboro you will experience greater than 5,700 HDD's.

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Fri. Oct. 09, 2020 10:13 am

Thank you.

i have three taco 007e pumps. got them at a really good price last yr. did not buy any more because was not sure what would be needed for a primary circulator.

specs:

Technical Specifications:
Horsepower: 1 HP
Maximum Shut-off Head: 10 ft
Maximum Flow: 16 GPM
Maximum Operating Pressure: 125 psi (8.6 bar)
Fluid Temperature: 36-230°F (2-110°C)
Voltage: 120V
Frequency: 60 Hz
Motor: Single Phase
Maximum Operating Power: 44 Watts
Amperage: 0.54 A
Frequency of Rotation: 4830 RPM
Casing: Cast Iron
Fluids: Water or 50% Water/Glycol Solution
Connection Sizes: 3/4", 1", 1-1/4", 1-1/2" Flanged.

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Fri. Oct. 09, 2020 10:15 am

waiting for mom and son to use the bathroom so i can turn the water off.
Last edited by lincolnmania on Fri. Oct. 09, 2020 10:17 am, edited 1 time in total.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Oct. 09, 2020 10:17 am

If you insist upon putting a Taco 007 on the 55 ft of HWB and 120 ft of run zone loop, it would be best if you use 1" PEX.

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Fri. Oct. 09, 2020 7:07 pm

got to work on the project a few hours today.
the well tank is wobbly, going to build a bracket to bolt to the pump bracket and attach that to a 2x4 screwed to the floor joist.
paid a plumber to replace the tank and had to have him back once because i had a leak, and a second time when the one well pipe fitting blew apart. he said he was on vacation and he could not help me.
he had the tank supported by the water line! quoted me $450 dollars, charged me $800 dollars. Never again!

wish i knew a plumber to come check my work after the boiler is installed.
anyone here? is it worth a case of beer and gas money?

 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Fri. Oct. 09, 2020 7:07 pm


 
lincolnmania
Member
Posts: 2705
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Thu. Oct. 15, 2020 2:03 pm

been super busy working in the basement.
wall is fixed, water softener installed.

just bought stove pipe, wow it went up in price!