One would think after 8 years I would remember everything about the operation of my boiler. But ....!
So today I had it shut down to really clean out the fines underneath the burner platform and I ran a drill bit through all the holes.
So I lit a fire as normal, water temp shower 100 degrees, but the fire seems to remain at idle.
So am I missing something?? I know I should know but...!
Thanks!
KA2 & Brain Cramp!
- nepacoal
- Member
- Posts: 1701
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
Do you have a low temp cutoff? If so, did you throw the bypass switch so it would run below 125?
- freetown fred
- Member
- Posts: 30300
- Joined: Thu. Dec. 31, 2009 12:33 pm
- Location: Freetown,NY 13803
- Hand Fed Coal Stove: HITZER 50-93
- Coal Size/Type: BLASCHAK Nut
Nice K--patience my friend!! Brain farts are GOOD!!!!!!!!!!!!!!!!!!!!!!!!!
-
- Member
- Posts: 2379
- Joined: Sun. Mar. 25, 2007 8:41 pm
- Location: Ithaca, New York
- Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
- Hand Fed Coal Boiler: former switzer CWW100-sold
- Coal Size/Type: rice
- Other Heating: kerosene for dual fuel Keystoker/unused
Hello Kungur,
Did you remove the baffle plate in front of the flue breech
and clean the fly ash out from behind it??
Have you checked the horizontal runs of flue pipe for
fly ash?
It will take a while to catch up if you have done the above chores.
Did you remove the baffle plate in front of the flue breech
and clean the fly ash out from behind it??
Have you checked the horizontal runs of flue pipe for
fly ash?
It will take a while to catch up if you have done the above chores.
-
- Member
- Posts: 2379
- Joined: Sun. Mar. 25, 2007 8:41 pm
- Location: Ithaca, New York
- Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
- Hand Fed Coal Boiler: former switzer CWW100-sold
- Coal Size/Type: rice
- Other Heating: kerosene for dual fuel Keystoker/unused
Hello Kungur,
Don't forget its cold out and that it is a huge draw down on the boilers heating ability and capacityon its smaller 25 gallon volume.
Don't forget its cold out and that it is a huge draw down on the boilers heating ability and capacityon its smaller 25 gallon volume.