All good now! With your help, the mystery of the drunken boiler pressure has been solved
I relieved the water pressure on the expansion tank by isolating it with valves and opening the boiler drain on the supply header. I put a tire gauge on the bottom valve of the tank to discover it has 18 pounds of air pressure in it. This is why it fluctuated. With boiler pressure under 18 pounds the water couldn't expand into the tank.
So, what I did was lower the air pressure on the tank to 14 psi. Then filled the boiler to 15 psi. Now expanding water can go into the tank.
Before a combustion call.. After combustion call... The expansion tank is now doing its job and the boiler pressure is stone sober before and after combustion calls
This combustion call only lasted 9 minutes but nothing was calling for heat during those minutes.
I relieved the water pressure on the expansion tank by isolating it with valves and opening the boiler drain on the supply header. I put a tire gauge on the bottom valve of the tank to discover it has 18 pounds of air pressure in it. This is why it fluctuated. With boiler pressure under 18 pounds the water couldn't expand into the tank.
So, what I did was lower the air pressure on the tank to 14 psi. Then filled the boiler to 15 psi. Now expanding water can go into the tank.
Before a combustion call.. After combustion call... The expansion tank is now doing its job and the boiler pressure is stone sober before and after combustion calls
This combustion call only lasted 9 minutes but nothing was calling for heat during those minutes.
- StokerDon
- Site Moderator
- Posts: 7496
- Joined: Mon. Nov. 11, 2013 11:17 am
- Location: PA, Southern York County!
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
NICE! I'm glad it was an easy fix!
I also like those nice Winters gauges too.
-Don
I also like those nice Winters gauges too.
-Don
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Thanks Don it is a sharp looker lol
I was advised to have the fill valve and the expansion tank at the same pressure. But in light of my nubie paranoia, I think I'll leave the fill valve at 10 pounds, which is how I recieved it. My reasoning is that if a leak does occur out on the loop somewhere, it will show up on the boiler gauge.
I was advised to have the fill valve and the expansion tank at the same pressure. But in light of my nubie paranoia, I think I'll leave the fill valve at 10 pounds, which is how I recieved it. My reasoning is that if a leak does occur out on the loop somewhere, it will show up on the boiler gauge.
- coaledsweat
- Site Moderator
- Posts: 13767
- Joined: Fri. Oct. 27, 2006 2:05 pm
- Location: Guilford, Connecticut
- Stoker Coal Boiler: Axeman Anderson 260M
- Coal Size/Type: Pea
It will show up on the floor not the gauge. The PRV will just replace anything that leaks.Lightning wrote: ↑Fri. Dec. 13, 2019 8:25 pmThanks Don it is a sharp looker lol
I was advised to have the fill valve and the expansion tank at the same pressure. But in light of my nubie paranoia, I think I'll leave the fill valve at 10 pounds, which is how I recieved it. My reasoning is that if a leak does occur out on the loop somewhere, it will show up on the boiler gauge.
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Well, it may not show up on the floor if a leak develops out on a pex loop somewhere. In that case, the boiler gauge will fall to 10 pounds since that's where the fill valve will let water back into the system..coaledsweat wrote: ↑Fri. Dec. 13, 2019 8:55 pmIt will show up on the floor not the gauge. The PRV will just replace anything that leaks.
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Ghost update - I turned down the primary pump a little bit to slow down the ghost flow in the salon. It helped somewhat, 62 degrees in there with 25 OAT.
I have some leftover 1.5 inch nipples that I want to use to build a primary/secondary intersection with that should prevent the ghost flow. If it works out, I'll send back the 100 dallar zone valve and the whole thing will be that much simpler.. The diagram is below.
I think the upsizing to 1.5 inch thru the intersection will help keep pressure even across the Ts. What's yer thoughts?
I have some leftover 1.5 inch nipples that I want to use to build a primary/secondary intersection with that should prevent the ghost flow. If it works out, I'll send back the 100 dallar zone valve and the whole thing will be that much simpler.. The diagram is below.
I think the upsizing to 1.5 inch thru the intersection will help keep pressure even across the Ts. What's yer thoughts?
Attachments
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
1-1/2" is no cure...Like was already stated, closely spaced tees must be in straight run of pipe...double 90s need some straight pipe distance before the first tee...mo straight, mo better...
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Its seems challenging to find definitive rules about closely spaced Ts and adjacent elbows concerning the primary/secondary intersection.
It is VERY important that the closely spaced tees be no further apart than 4 times the diameter of whatever size pipe constitutes the primary/secondary loop, and it is equally important that the length of the straight pipes extending from the closely spaced tees be at least 6 times that same pipe diameter.
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
I have a book about it somewhere. The big things to remember are straight runs of pipe, and no more than 4 pipe diameters between the tees (max of 12").
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Thanks Rob, I'll modify that design to get a decent length of straight pipe before and after the closely spaced Ts.
I did read another article about headers. It said that short and fat is better than long and skinny, imagine that so with applying that principle, upsizing to 1.5 inches for the primary section thru the intersection should also be beneficial.
I did read another article about headers. It said that short and fat is better than long and skinny, imagine that so with applying that principle, upsizing to 1.5 inches for the primary section thru the intersection should also be beneficial.
- hotblast1357
- Member
- Posts: 5661
- Joined: Mon. Mar. 10, 2014 10:06 pm
- Location: Peasleeville NY
- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
Headers are not closely spaced tees.
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Right, but I did read that they use those similar spacing rules stated above and are designed to help keep even pressure across the outlets by using a bigger common pipe with smaller outlets.
By keeping the headers short and generously sized, the pressure drop along the header is very low. This in combination with the very low pressure drop through the hydraulic separator (hydraulic separator is a fancy name for the primary/secondary intersection) provides good hydraulic separation of all the circulators in the system.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
90s are not straight pipe...