K6 boiler won’t stop heating

 
Aecarl
New Member
Posts: 17
Joined: Sun. Nov. 10, 2019 9:55 am
Stoker Coal Boiler: K6
Coal Size/Type: Rice

Post by Aecarl » Sun. Nov. 10, 2019 10:06 am

Hey all new here,I have a K6 boiler and I have 4 zones. 3 zones run off from circulator relay and zone controller. The 4 th runs off from triple aqua stat. That one we have wire so that when it calls for heat it turns on the main circulator pump to the boiler and turns the boiler on. My problem is that the first 3 zones heat as follows: run#1 heats concrete in basement, run#2 heats mud room kitchen living room, run #3 heats 3 bedrooms and 2 bathrooms. The fourth zone runs to a heat exchanger which is 19”x22” with 3/8 tubes that is duct into multiple rooms with about 1200 sq. ft. The 3 zones never call for heat because for some reason it’s always 78 degrees in there, I can’t seem to get those zones to cool down. The 4th zone calls for heat and in fact does heat. Also, I have the triple aqua stat set at 140 and 160 but the boiler continues to run even above 180. I hope it’s not too confusing any help would be great, sick of sweating all night!!


 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Sun. Nov. 10, 2019 10:25 am

Check valves anywhere...
Sounds like a ghost flow...
Open some windows first...
The boiler stops running at what temp...
Does it go over 210*...

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Sun. Nov. 10, 2019 10:30 am

If the stoker and fan are running above 160, you either have a bad triple aquastat or you are backfeeding the b1 terminal somehow. It should never fire above the high limit except possibly on the timer. Has it ever ran correctly or is this a new system?

 
Phil May
Member
Posts: 320
Joined: Sun. Nov. 06, 2011 9:12 pm
Location: Wellsville NY
Stoker Coal Boiler: EFM 700
Hot Air Coal Stoker Stove: Liesure Line
Coal Size/Type: Rice

Post by Phil May » Sun. Nov. 10, 2019 11:39 am

Sound like you are getting gravity convection through the 3 zones when the 4th one is on. Hot to cold convection can be a problem if not piped properly or zone valves are leaking by.

 
Aecarl
New Member
Posts: 17
Joined: Sun. Nov. 10, 2019 9:55 am
Stoker Coal Boiler: K6
Coal Size/Type: Rice

Post by Aecarl » Sun. Nov. 10, 2019 12:10 pm

It doesn’t ever go over 210, all valves are open and solenoids are working properly. It worked correctly for a few days and then started acting up.

 
Aecarl
New Member
Posts: 17
Joined: Sun. Nov. 10, 2019 9:55 am
Stoker Coal Boiler: K6
Coal Size/Type: Rice

Post by Aecarl » Sun. Nov. 10, 2019 12:10 pm

I currently have the valves off to the first 3 zones just to help cool it down

 
lzaharis
Member
Posts: 2379
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Sun. Nov. 10, 2019 6:21 pm

Hello Aecarl,

Does your kaa-6 have a hydrolevel triple aquastat??


 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Nov. 10, 2019 6:39 pm

Aecarl wrote:
Sun. Nov. 10, 2019 12:10 pm
It doesn’t ever go over 210, all valves are open and solenoids are working properly. It worked correctly for a few days and then started acting up.
Welcome to the forum.

Is this a new install??? Or has it been in place for many heating season and just started having this problem??? This is very important to know if we are to figure out if it is a failed part or an install problem.

-Don

 
Aecarl
New Member
Posts: 17
Joined: Sun. Nov. 10, 2019 9:55 am
Stoker Coal Boiler: K6
Coal Size/Type: Rice

Post by Aecarl » Sun. Nov. 10, 2019 7:08 pm

This is a new install. I think I attached a couple of pictures

Attachments

C42B29FB-3EAD-46CB-B88B-CE2D0D383AAF.jpeg
.JPEG | 627KB | C42B29FB-3EAD-46CB-B88B-CE2D0D383AAF.jpeg

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Nov. 10, 2019 7:54 pm

You may have multiple things going on. Wiring issues, ghost flows, etc.

I would start by checking the high limit functionality on the aquastat.

 
Aecarl
New Member
Posts: 17
Joined: Sun. Nov. 10, 2019 9:55 am
Stoker Coal Boiler: K6
Coal Size/Type: Rice

Post by Aecarl » Sun. Nov. 10, 2019 8:50 pm

So, I am going to order a new aqua stat but, I have had 3 zones off all day. I just went and turned them on and got flow through the manifolds, do I need to install a solenoid on the inlets as well? None of the zones were calling for heat except zone 4.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Nov. 10, 2019 11:38 pm

Mixing valve for zone 1 garage floor likely needs check valve(s)...there is pressure differential from other zones passing through there somehow.
You should be able to use your hand and feel that there is heat flow even when zone 1 is not calling for heat...

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Nov. 11, 2019 6:40 am

Aecarl wrote:
Sun. Nov. 10, 2019 8:50 pm
So, I am going to order a new aqua stat but, I have had 3 zones off all day. I just went and turned them on and got flow through the manifolds, do I need to install a solenoid on the inlets as well? None of the zones were calling for heat except zone 4.
Before you order a new one I would just troubleshoot the one you have. Remove all but the incoming power wires in the aquastat, and with the boiler at a known temperature, adjust the high and low limits with a voltage meter (or wire up a light bulb) across the B1 & B2 terminals.

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Mon. Nov. 11, 2019 6:49 am

Aecarl wrote:
Sun. Nov. 10, 2019 8:50 pm
So, I am going to order a new aqua stat but, I have had 3 zones off all day. I just went and turned them on and got flow through the manifolds, do I need to install a solenoid on the inlets as well? None of the zones were calling for heat except zone 4.
+1 on troubleshooting your triple aquastat. Most of the time when this comes up, it's a wiring issue.

Also, do all of your taco circulators have integrated flow checks? If not they can be added into any newer taco circulator (newer housings are all machined to accept the IFC). They are sold separately and are just press fit by hand in the end of the circulator.

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Mon. Nov. 11, 2019 7:36 am

You should post a picture of how the 4 th zone is plumbed. I think that you have set your system up that a call for heat from the 4th zone is pressurizing the supply on the other three zones. Post more pics showing the piping from the three zones to the boiler. Nice pipe job by the way. Did you do that?