Another ahs 130- finally piping

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Tue. Nov. 05, 2019 7:22 pm

So i finally am getting on to my piping as my parts come in, always seems like i need another one i didnt think of.
Going to do black iron to the manifolds then copper and pex after that.
Initially plumbing heat exchabger and then will add radiators as i can pipe them.
Using blue monster tape and dope..

One question is where should i put the wye strainer?
Before the pump, after the pump- return,supply???
1572999619788350539476549105579.jpg
.JPG | 570KB | 1572999619788350539476549105579.jpg


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Nov. 05, 2019 7:55 pm

Sounds like a good plan there L. Unfortunately, I don't know where the best place to install the Wye strainer would be.

-Don

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Tue. Nov. 05, 2019 8:48 pm

Why the wye? If I may be so bold.

 
lzaharis
Member
Posts: 2366
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Tue. Nov. 05, 2019 10:03 pm

Place the Wye screen before the circulator to protect the volute and then the entire system.

If you have not done it already the circulator will benefit from being on the top of the boiler as it will pull any air bubbles through the steam chest and to the air vent if you do not have a Internal Air Separator, Airtrol Valve,
Steel Compression Tank.

Edit to add:

If you can afford it purchase the circulator mounting flanges with gauge ports and ball valves so that you can have a vacuum gauge on the inlet side and pressure gauge on the output side and you will always know what condition your circulator is in and whether the Wye filter screen needs to be cleaned to.
Last edited by lzaharis on Wed. Nov. 06, 2019 9:02 am, edited 3 times in total.

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Tue. Nov. 05, 2019 10:11 pm

I had read on here in one of the threads that a wye was recomended in case any debris got in so as to protect the circulator.

Are you saying the pump should go before the air scoop on the supply side?

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Nov. 06, 2019 12:51 am

lamina1982 wrote:
Tue. Nov. 05, 2019 10:11 pm
I had read on here in one of the threads that a wye was recomended in case any debris got in so as to protect the circulator.

Are you saying the pump should go before the air scoop on the supply side?
That's where mine is and works without incident.

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Nov. 06, 2019 6:34 am

Unless you have an old cast iron radiator system that was previously open to the atmosphere, or recycled radiators that may have sat outside, debris in the system should not be a problem. With that said, the strainer won't hurt anything, so you might as well install it.

I would mount the strainer on the return header, prior to the boiler. That way any junk returning from the zones is captured prior to the boiler and circulator...and it will be mounted low and be easier to service. Your circulator should be installed after the air scoop and expansion tank, so it is pumping away from the scoop.


 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Nov. 06, 2019 7:28 am

There should be a screen on the fill valve. So unless you have a situation like Rob suggests, it is unnecessary.

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Wed. Nov. 06, 2019 7:47 am

Yes i planned on "pumping away".
I will be installing a bunch of old cast iron radiators.
Thanks for the advice on location, makes sense.

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Mon. Nov. 11, 2019 10:04 pm

Slowly getting there but making progress.
Seems always short 1 or 2 parts.
Sure hope it doesnt leak much.
20191111_214550.jpg
.JPG | 698.4KB | 20191111_214550.jpg
20191111_214537.jpg
.JPG | 639.8KB | 20191111_214537.jpg

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Mon. Dec. 02, 2019 11:18 pm

20191202_230008.jpg
.JPG | 492.6KB | 20191202_230008.jpg
Moving along pretty slow as deer season interupted my piping. Cant wait to get this done and burning.
Got main trunk of supply dome, just gotta run copper to heat exchanger in furnace

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Tue. Dec. 03, 2019 12:34 am

Looking Good...

 
Qtown1835
Member
Posts: 705
Joined: Sat. Nov. 08, 2014 11:47 am
Location: Quakertown, PA
Stoker Coal Boiler: Keystoker '81 KA4 (online 1/16/17)
Coal Size/Type: WAS Lehigh Rice (TBD)
Other Heating: EFM SPK600

Post by Qtown1835 » Wed. Dec. 04, 2019 10:43 am

How much radiation do you have in your house? Curious how you sized your ET. Looks like and EX30 or 60? I sized mine based on the website calc and it was coming up short, so i jumped to the 90. Im guessing you will be on the fringe between a 60 & 90.

 
lamina1982
Member
Posts: 149
Joined: Sat. Oct. 11, 2014 2:11 am
Location: Albio , Ny
Hot Air Coal Stoker Stove: keystoker econo 90
Coal Size/Type: rice

Post by lamina1982 » Wed. Dec. 04, 2019 2:15 pm

Mines a 90, im gonna use a bunch cast iron radiators eventually so went bigger

 
Qtown1835
Member
Posts: 705
Joined: Sat. Nov. 08, 2014 11:47 am
Location: Quakertown, PA
Stoker Coal Boiler: Keystoker '81 KA4 (online 1/16/17)
Coal Size/Type: WAS Lehigh Rice (TBD)
Other Heating: EFM SPK600

Post by Qtown1835 » Wed. Dec. 04, 2019 9:28 pm

lamina1982 wrote:
Wed. Dec. 04, 2019 2:15 pm
Mines a 90, im gonna use a bunch cast iron radiators eventually so went bigger
Good deal.