nepacoal wrote:
Wed. Oct. 30, 2019 5:40 pm
If your high and operating are both set to 180, it might just "appear" that the high is controlling the fan... Did you try setting the high, higher than operating?
Yes. When I set the operating limit to 200, nothing happens. When I return it to 180 and set the high limit single to 200, the fan kicks on.

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Wed. Oct. 30, 2019 6:00 pm

That does sound backwards... I'm sure one of our resident AHS experts will chime in and help you get it squared away.

 
User avatar
coaledsweat
Site Moderator
Posts: 13768
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Oct. 30, 2019 6:59 pm

You need to raise the temperature setting on the single aquastat by 20°. It is killing power when it reaches the limit as it acts as over temperature safety. If it isn't wired properly it may cause the problem you describe. It should be normally closed and open on a temp rise to its set point. They can be wired normally open or normally closed, you need to look at that.


 
Trumpeterb
Member
Posts: 230
Joined: Sun. Feb. 10, 2019 8:37 am
Location: West Middlesex, PA
Stoker Coal Boiler: AHS130 Coal Gun
Coal Size/Type: Pea
Other Heating: Electric baseboards (hopefully never use these again)

Post by Trumpeterb » Wed. Oct. 30, 2019 7:39 pm

coaledsweat wrote:
Wed. Oct. 30, 2019 6:59 pm
You need to raise the temperature setting on the single aquastat by 20°. It is killing power when it reaches the limit as it acts as over temperature safety. If it isn't wired properly it may cause the problem you describe. It should be normally closed and open on a temp rise to its set point. They can be wired normally open or normally closed, you need to look at that.
That seemed to work. Thanks!

 
User avatar
coaledsweat
Site Moderator
Posts: 13768
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Oct. 30, 2019 9:01 pm

It may have been wired to trigger a dump zone.

 
Trumpeterb
Member
Posts: 230
Joined: Sun. Feb. 10, 2019 8:37 am
Location: West Middlesex, PA
Stoker Coal Boiler: AHS130 Coal Gun
Coal Size/Type: Pea
Other Heating: Electric baseboards (hopefully never use these again)

Post by Trumpeterb » Wed. Oct. 30, 2019 10:36 pm

coaledsweat wrote:
Wed. Oct. 30, 2019 9:01 pm
It may have been wired to trigger a dump zone.
The dump zone aquastat is a different one. It is the right side of the double.