Yes. When I set the operating limit to 200, nothing happens. When I return it to 180 and set the high limit single to 200, the fan kicks on.
Boiler piping
-
- Member
- Posts: 230
- Joined: Sun. Feb. 10, 2019 8:37 am
- Location: West Middlesex, PA
- Stoker Coal Boiler: AHS130 Coal Gun
- Coal Size/Type: Pea
- Other Heating: Electric baseboards (hopefully never use these again)
- nepacoal
- Member
- Posts: 1701
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
That does sound backwards... I'm sure one of our resident AHS experts will chime in and help you get it squared away.
- coaledsweat
- Site Moderator
- Posts: 13768
- Joined: Fri. Oct. 27, 2006 2:05 pm
- Location: Guilford, Connecticut
- Stoker Coal Boiler: Axeman Anderson 260M
- Coal Size/Type: Pea
You need to raise the temperature setting on the single aquastat by 20°. It is killing power when it reaches the limit as it acts as over temperature safety. If it isn't wired properly it may cause the problem you describe. It should be normally closed and open on a temp rise to its set point. They can be wired normally open or normally closed, you need to look at that.
-
- Member
- Posts: 230
- Joined: Sun. Feb. 10, 2019 8:37 am
- Location: West Middlesex, PA
- Stoker Coal Boiler: AHS130 Coal Gun
- Coal Size/Type: Pea
- Other Heating: Electric baseboards (hopefully never use these again)
That seemed to work. Thanks!coaledsweat wrote: ↑Wed. Oct. 30, 2019 6:59 pmYou need to raise the temperature setting on the single aquastat by 20°. It is killing power when it reaches the limit as it acts as over temperature safety. If it isn't wired properly it may cause the problem you describe. It should be normally closed and open on a temp rise to its set point. They can be wired normally open or normally closed, you need to look at that.
- coaledsweat
- Site Moderator
- Posts: 13768
- Joined: Fri. Oct. 27, 2006 2:05 pm
- Location: Guilford, Connecticut
- Stoker Coal Boiler: Axeman Anderson 260M
- Coal Size/Type: Pea
It may have been wired to trigger a dump zone.
-
- Member
- Posts: 230
- Joined: Sun. Feb. 10, 2019 8:37 am
- Location: West Middlesex, PA
- Stoker Coal Boiler: AHS130 Coal Gun
- Coal Size/Type: Pea
- Other Heating: Electric baseboards (hopefully never use these again)
The dump zone aquastat is a different one. It is the right side of the double.