Aquastat

 
Randyman
Member
Posts: 21
Joined: Fri. Dec. 07, 2018 11:19 am
Location: bernville pa
Stoker Coal Boiler: 1967 efm 520 round door
Hand Fed Coal Stove: harman mark3

Post by Randyman » Wed. Mar. 20, 2019 3:51 pm

New aquastat works good thanks guys 210 shipped from supplyhouse thats a good tip i learned from this website it saved a lot

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Wed. Mar. 20, 2019 3:56 pm

Glad it was an easy fix! Is the new boiler fired up?

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Mar. 20, 2019 7:35 pm

Glad it worked out for you. $210 is a pretty dern good price for a new triple aquastat.

-Don

 
User avatar
coaledsweat
Site Moderator
Posts: 13767
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Mar. 20, 2019 10:06 pm

Does anyone repair those?

 
Randyman
Member
Posts: 21
Joined: Fri. Dec. 07, 2018 11:19 am
Location: bernville pa
Stoker Coal Boiler: 1967 efm 520 round door
Hand Fed Coal Stove: harman mark3

Post by Randyman » Thu. Mar. 21, 2019 12:17 am

One more question I have a wilburt timer no 34170 that came with , but it has terminals for a thermostat hookup can I still wire this into the terminals zr and zc in the aquastat and do I have to hookup the thermostat? Im not sure how this works


 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 21, 2019 6:10 am

Randyman wrote:
Thu. Mar. 21, 2019 12:17 am
One more question I have a wilburt timer no 34170 that came with , but it has terminals for a thermostat hookup can I still wire this into the terminals zr and zc in the aquastat and do I have to hookup the thermostat? Im not sure how this works
The thermostat terminals are for a steam application. You won't use them.

Run power to the timer, and run the switched power from the timer to the ZR terminal in the aquastat.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Mar. 21, 2019 11:29 am

*RM*, Did or will you wire in a high limit safety, if timer or aquastat were ever to get 'stuck' you wouldn't have a 'run away' boiler...

If you have one wired in, then you only need to test if it is working. :)

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 21, 2019 11:36 am

That L6006 mentioned on the first page would make a good high limit control.

 
Randyman
Member
Posts: 21
Joined: Fri. Dec. 07, 2018 11:19 am
Location: bernville pa
Stoker Coal Boiler: 1967 efm 520 round door
Hand Fed Coal Stove: harman mark3

Post by Randyman » Thu. Mar. 21, 2019 11:50 am

No i dont dont a high limit stop the 6006 is a low temp stop in case of an outfire should i change it, i thought the aquastat would shut it down at the hi limit.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Mar. 21, 2019 2:28 pm

Randyman wrote:
Thu. Mar. 21, 2019 11:50 am
No i dont dont a high limit stop the 6006 is a low temp stop in case of an outfire should i change it, i thought the aquastat would shut it down at the hi limit.
A run-away boiler is not Stopped by the aquastat high limit when timer sticks or that aquastat hi limit fails closed...

Out-fire low temp Breaks on a temp DROP
Run-away high temp Breaks on a temp RISE

Set-points for both are at opposite ends of the spectrum...very different requirements of any single L6006 or the like...pick what's important to you...nuisance out-fire or a catastrophic run-away...
Last edited by McGiever on Thu. Mar. 21, 2019 4:21 pm, edited 1 time in total.


 
Randyman
Member
Posts: 21
Joined: Fri. Dec. 07, 2018 11:19 am
Location: bernville pa
Stoker Coal Boiler: 1967 efm 520 round door
Hand Fed Coal Stove: harman mark3

Post by Randyman » Thu. Mar. 21, 2019 3:03 pm

I guess I'll be adding another one, there goes another hundred this things like a old boat it never ends

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 21, 2019 3:28 pm

Randy, if you have a good chimney, the chance of that EFM going out is pretty slim...and an ash pan full of coal is an inconvenience rather that a safety issue. I suggest using the L6006 you already have as a separate high limit control.

Watch eBay for a good deal on a L4006B or another L6006 to add as an outfire control at a later date. Once in a while you can get a nice one for $50 or so.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Mar. 21, 2019 3:39 pm

Just keep in mind that the high safety can only be the Break on temp Rise type aquastat...if the current L6006 has 3 terminal screws you're good to just move the one wire...if it where the L4006 with only the 2 terminal screws it cannot be made to work as a high safety.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Mar. 21, 2019 4:34 pm

L4006A breaks on rise, and would be fine for a high limit safety, but not an outfire control...for that, the "B" version is needed.

Post Reply