Keystoker KA-6 no heat ???

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 4:46 am

My KA-6 has stop sending hot water through the radiator system. It’s just sitting at idle. Water temp at boiler 190. But is not going anywhere. Any ideas on what it could be ?


 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 5:11 am

Could be a bad thermostat or circulator (would be the first things I would check). To check the thermostat, jumper the TT terminals. If it starts the circulator, you have a bad thermostat.
Last edited by nepacoal on Tue. Mar. 12, 2019 5:57 am, edited 1 time in total.

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 5:35 am

Sorry for my lack of knowledge. What is TT terminals ?

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 5:42 am

Where your thermostat wires plug into your triple aquastat. Or, if you have a zone controller, where the thermostat connects there. Be careful, there is 110v in the aquastat/zone controller too. Might want to call in a plumber if you are not very familiar with this...

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 5:49 am

7DF4C89B-A756-4905-A296-43402225FB18.jpeg

Any idea what wires those are ?


 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 5:53 am

Can't see the labels, but It looks like the low voltage thermostat wires are going to the terminals in the upper right. Should be clearly labeled TT. Sounds like you should call in a professional...

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 5:58 am

99626BA2-1BF6-4ACC-B0DA-EDF40B3A42C9.jpeg

Found it. Can I just touch them together or do I need to separate

.JPEG | 672KB | 99626BA2-1BF6-4ACC-B0DA-EDF40B3A42C9.jpeg


 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 6:02 am

Jumper (touch) the TT together... It simulates the thermostat calling for heat.

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 6:04 am

I have no wire for a jumper. Can’t I just touch them together or twist them together ?

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 6:07 am

Yes, using the existing wires would be the same as a jumper... Just triple check to make sure you are doing the TT terminals.

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 6:10 am

Oops missed the touch part in your reply. Touched both together and nothing happened. No circulate. No spark. No nothing 😢. What is next step ? Also thank you for your help

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 6:11 am

Attachments


 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 6:16 am

Is your timer still working? Causing the stoker/blower to cycle on and off every 10 or 15 minutes? I assumed it was since your temp was at 190 but just want to make sure you have power to the boiler.

 
User avatar
jcw265
Member
Posts: 146
Joined: Sun. Jan. 13, 2008 4:52 am
Location: Southern Ohio
Stoker Coal Boiler: Keystoker. KA 6
Coal Size/Type: Rice/Anthracite
Contact:

Post by jcw265 » Tue. Mar. 12, 2019 6:23 am

Yes but here is a new twist. I just turned boiler off at switch. Turned back on and now the secondary fan that runs all the time did not come back on ??? Timer is working. Green light on at power box.

 
User avatar
nepacoal
Member
Posts: 1701
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Tue. Mar. 12, 2019 6:30 am

A bad thermostat would have been the simplest issue and has happened to me before. Troubleshooting is next. Could be the circulator, the aquastat, anything. I would use my multimeter to check the voltage at the C1/C2 terminals which go to the circulator next. If voltage is present, you might have a bad circulator. If you are not comfortable or familiar with troubleshooting 110v you should call in a professional...