Electric Baseboard BTU per foot vs. Hot Water baseboard

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Feb. 18, 2019 9:12 am

scottybk wrote:
Sun. Feb. 17, 2019 11:54 pm
Don, if you read the forums for the outdoor wood boiler guys, many who pipe with the Logstor/Thermopex for even 200 foot runs report losing only 1 or 2 degrees of temperature from boiler to the end of the line.
The Delta T is only part of the equation. The bigger part is how many BTU's you loose per hour. This doesn't seem to be a problem for OWB's because wood is "free".

I am only trying to make the point that with a normal residential boiler,coal, gas or oil, you will not get away with this logic, it will bite you.
memco man wrote:
Mon. Feb. 18, 2019 12:43 am
I lost the boiler as well lucky I did not burn down my house it took the boiler almost 8 hrs. to cool down so that I could put water in it to see if it would hold water which it did not.
OUCH!!!

-Don

 
memco man
Member
Posts: 217
Joined: Mon. Oct. 24, 2011 10:18 pm
Location: vermont
Stoker Coal Boiler: 1981 KA-6 Keystoker
Hand Fed Coal Boiler: Tarms 504
Hot Air Coal Stoker Stove: alaska liberty
Hand Fed Coal Stove: jotul NR 507, crane coal cooker 44, crane 404, chubby w/blower, chubby w/out blower, franco blege 10-475 Montgomery ward laundry stove Moore's Brother seventeen circulator stove
Coal Size/Type: nut/anthracite/pea
Other Heating: harman p68, elmtree,harthstone,new mack

Post by memco man » Mon. Feb. 18, 2019 9:02 pm

hotblast1357 wrote:
Mon. Feb. 18, 2019 7:50 am
Why didn’t the manual dump zone work?

Hand feds are a lot different than stokers when we discuss over heating, Ive ran one, yes they are a little more worry some.

But I guess thank god you didn’t have any pex in your system or else!
The reason the manual dump did not work is I had it set up to open the valve when or if I lost power so it would gravity feed I never lost power so the valve stayed closed lesson learned

M.M

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Feb. 19, 2019 4:03 am

memco man wrote:
Mon. Feb. 18, 2019 9:02 pm
The reason the manual dump did not work is I had it set up to open the valve when or if I lost power so it would gravity feed I never lost power so the valve stayed closed lesson learned

M.M
I'm quite thankful that little harm came of this incident. Hindsight is 20-20, but it seems the solution here is to leave a gravity feed dump zone openly active at all times. No valves on it.


 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Fri. Feb. 22, 2019 2:15 am

lsayre wrote:
Sat. Feb. 16, 2019 9:18 pm
I like this solution! Do you have TRV's on the HWB's for each room?
No TRV's. I have thermostat on each zone and setup for a number of zones.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Feb. 26, 2019 6:44 am

Every degree lost to underground piping requires roughly 3-1/3% more coal to be burned. A moderate 3 degrees of temperature loss adds roughly 10% to your annual heat bill.