Well as the subject say RIP Intermatic C8865 Timer.
For those that live in the North East last week we were in the minus F temperatures and now this week we are in the 50's and 60's. As this is my first couple of weeks with AA260 running and have never had a stoker boiler before I was concerned with the warm temps and thought it would be a good idea to put the pins in the cycle timer. I would rather burn a little extra coal then have a problem with my fire. This unit has been running fantastic to the point where I am waiting for the other shoe to drop and come home to a nightmare. Well that was true on Monday night when I came home and noticed the cycle timer was at the exact same position as when I put the pins in earlier that morning. So me being the skeptic that I am decided to investigate a little further to find out the gears in the old timer gave up and finally stripped out.
So off to the wonderful internet to search for a replacement timer only to have a mild heart attack when I saw the price of an exact replacement. The thought of putting out another $200 -$250 had me quite upset. So I started looking around and found this great digital cycle timer for $12.39 on Amazon. this timer will do a multitude of timing functions and was just what I needed.
https://www.amazon.com/Digital-Delay-Relay-Timer- ... elay+timer
Much to my disappointment the contacts for the onboard relay were rated a mere 10 amps. So back to the internet I go and to my favorite site Amazon. I found a RIB (Relay In a Box) with a 120 VAC coil and a 1HP contact rating for $16.53.
https://www.amazon.com/gp/product/B000LEUJU6/ref= ... UTF8&psc=1
So with a little work I gutted the old intermatic and removed the guts and installed my new electronic timer. The wiring was pretty easy as I powered up the clock from the stoker circuit and and used the timer relay to control the coil of the RIB and the contacts on the RIB to control the stoker.
Programming was a little more difficult because the instructions were a little lacking. But none the less I was able to get it programmed and know have my timer again to carry me through any warm days ahead. I will eventually add an outdoor temperature sensor to the circuit so the Rib will only be operational when the temperature is above 50* F.
For those that live in the North East last week we were in the minus F temperatures and now this week we are in the 50's and 60's. As this is my first couple of weeks with AA260 running and have never had a stoker boiler before I was concerned with the warm temps and thought it would be a good idea to put the pins in the cycle timer. I would rather burn a little extra coal then have a problem with my fire. This unit has been running fantastic to the point where I am waiting for the other shoe to drop and come home to a nightmare. Well that was true on Monday night when I came home and noticed the cycle timer was at the exact same position as when I put the pins in earlier that morning. So me being the skeptic that I am decided to investigate a little further to find out the gears in the old timer gave up and finally stripped out.
So off to the wonderful internet to search for a replacement timer only to have a mild heart attack when I saw the price of an exact replacement. The thought of putting out another $200 -$250 had me quite upset. So I started looking around and found this great digital cycle timer for $12.39 on Amazon. this timer will do a multitude of timing functions and was just what I needed.
https://www.amazon.com/Digital-Delay-Relay-Timer- ... elay+timer
Much to my disappointment the contacts for the onboard relay were rated a mere 10 amps. So back to the internet I go and to my favorite site Amazon. I found a RIB (Relay In a Box) with a 120 VAC coil and a 1HP contact rating for $16.53.
https://www.amazon.com/gp/product/B000LEUJU6/ref= ... UTF8&psc=1
So with a little work I gutted the old intermatic and removed the guts and installed my new electronic timer. The wiring was pretty easy as I powered up the clock from the stoker circuit and and used the timer relay to control the coil of the RIB and the contacts on the RIB to control the stoker.
Programming was a little more difficult because the instructions were a little lacking. But none the less I was able to get it programmed and know have my timer again to carry me through any warm days ahead. I will eventually add an outdoor temperature sensor to the circuit so the Rib will only be operational when the temperature is above 50* F.
- nepacoal
- Member
- Posts: 1696
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
Good find... And, wow, that 260 must draw a lot. I think I could run 4 of my little boilers on 10 amps, including both circulators...
- nepacoal
- Member
- Posts: 1696
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
That is a beast... Do you have to be careful walking by when it starts up? Might get sucked in...
-
- Member
- Posts: 80
- Joined: Fri. Aug. 01, 2014 9:40 pm
- Location: Bushkill, Pa
- Stoker Coal Boiler: AA 260
- Hand Fed Coal Stove: Harmon 2000
It really is amazing how much of a beast it is When it jumps to life and pulls the viewing hole plate shut it does it with quite an amount of authority I can not believe how well built these units are. The old girl had a hard neglected life in her earlier years
- StokerDon
- Site Moderator
- Posts: 7486
- Joined: Mon. Nov. 11, 2013 11:17 am
- Location: PA, Southern York County!
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
Now that is pretty neat! I think that is the most innovative and inexpensive timer solution I have heard of. What do you have it set at?
-Don
-Don
- Hambden Bob
- Member
- Posts: 8535
- Joined: Mon. Jan. 04, 2010 10:54 am
- Location: Hambden Twp. Geauga County,Ohio
- Hot Air Coal Stoker Stove: Harman 1998 Magnum Stoker
- Hand Fed Coal Stove: Blower Model Coal Chubby 1982-Serial#0097
- Coal Size/Type: Rice-A-Roni ! / Nut
- Other Heating: Pro-Pain Forced Air
Nice Job hammering this Control Deal out!!
- StokerDon
- Site Moderator
- Posts: 7486
- Joined: Mon. Nov. 11, 2013 11:17 am
- Location: PA, Southern York County!
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
-
- Member
- Posts: 80
- Joined: Fri. Aug. 01, 2014 9:40 pm
- Location: Bushkill, Pa
- Stoker Coal Boiler: AA 260
- Hand Fed Coal Stove: Harmon 2000
I am running off the high limit still because I have the Triple Aquastat t terminals jumped to keep the circulataor running 24-7. Monitoring the pipe I am seeing temps of 180-182 even though I only have the Triple Aquastat set to about 165. I need to replace the square gauge on the boiler as it is only showing 140*F. Amazon had replacement tridicator for $34.29.
https://www.amazon.com/gp/product/B00FBQBQ56/ref= ... UTF8&psc=1
I also need to get some thermal compound for the Triple Aquastat well so i can find the discrepancy between my digital thermometer and the Triple Aquastat set point. I have not had any problems with popping the relief valve or activating the high limit otherwise
-
- Member
- Posts: 2366
- Joined: Sun. Mar. 25, 2007 8:41 pm
- Location: Ithaca, New York
- Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
- Hand Fed Coal Boiler: former switzer CWW100-sold
- Coal Size/Type: rice
- Other Heating: kerosene for dual fuel Keystoker/unused
Please do not buy that triple aquastat off amazon!!!!!!!!!!!!!!!!!
The manufacturers name is not on the face plate it is not a Marsh Instruments or other united states manufacturer of gauges.
If you look at stoker dons 4 inch guage on his AA its a Marshalltown gauge which I also have having replaced the Chinese made junk I was given by keystoker.
My first Marshalltown gauge was on the avco Lycoming boiler that this house came with and it never gave me a wrong pressure or temperature reading. I wish I had not been lied to about its leaking by the plumber I bough the Buderus from as a friend that took the old boiler said it had no leaks and I would still have it 40 years later.
The Marshalltown triple gauge will cost you more but it has a 2 year guarantee against defects as it was tested before it was shipped in its closed cell foam filled carton to the buyer. This marsh gauge can be sent back to the factory in Ohio if it needs to be rebuilt if that is ever needed.
The investment you have made in this excellent boiler is worth the money spent on a new 4 inch square Marshalltown Triple Gauge as it will give you many decades of service and you will have the 2 year guarantee that comes with it.
The conductive paste for the triple aquastat can be purchased separately from Honeywell retailer as it comes in a squeezable packet.
One question; if you used Teflon Tape for the probe well before you will need to remove the probe well, clean the threads with a 3/4" tap and then use liquid pipe dope on the bronze probe well as it will not interfere with the temperature conductive pastes ability to transfer the actual water temperature through the bronze probe well.
The marsh instruments folks also state that pipe dope should be used on the male threads of their gauges used in hot water and steam service.
The manufacturers name is not on the face plate it is not a Marsh Instruments or other united states manufacturer of gauges.
If you look at stoker dons 4 inch guage on his AA its a Marshalltown gauge which I also have having replaced the Chinese made junk I was given by keystoker.
My first Marshalltown gauge was on the avco Lycoming boiler that this house came with and it never gave me a wrong pressure or temperature reading. I wish I had not been lied to about its leaking by the plumber I bough the Buderus from as a friend that took the old boiler said it had no leaks and I would still have it 40 years later.
The Marshalltown triple gauge will cost you more but it has a 2 year guarantee against defects as it was tested before it was shipped in its closed cell foam filled carton to the buyer. This marsh gauge can be sent back to the factory in Ohio if it needs to be rebuilt if that is ever needed.
The investment you have made in this excellent boiler is worth the money spent on a new 4 inch square Marshalltown Triple Gauge as it will give you many decades of service and you will have the 2 year guarantee that comes with it.
The conductive paste for the triple aquastat can be purchased separately from Honeywell retailer as it comes in a squeezable packet.
One question; if you used Teflon Tape for the probe well before you will need to remove the probe well, clean the threads with a 3/4" tap and then use liquid pipe dope on the bronze probe well as it will not interfere with the temperature conductive pastes ability to transfer the actual water temperature through the bronze probe well.
The marsh instruments folks also state that pipe dope should be used on the male threads of their gauges used in hot water and steam service.
- nepacoal
- Member
- Posts: 1696
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
I believe you have this info a little mixed up with the procedures for an electrowell used for low water cutoff (like hydrolevel's triple a aquastat with lwco). A Normal well can use tape and pipe dope and function just fine. Only the electrowell recommends not using Teflon tape. When using the lwco function you are not supposed to use tape or thermal paste as it will mess up the lwco readingslzaharis wrote: ↑Fri. Feb. 08, 2019 11:01 am
One question; if you used Teflon Tape for the probe well before you will need to remove the probe well, clean the threads with a 3/4" tap and then use liquid pipe dope on the bronze probe well as it will not interfere with the temperature conductive pastes ability to transfer the actual water temperature through the bronze probe well.
-
- Member
- Posts: 2366
- Joined: Sun. Mar. 25, 2007 8:41 pm
- Location: Ithaca, New York
- Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
- Hand Fed Coal Boiler: former switzer CWW100-sold
- Coal Size/Type: rice
- Other Heating: kerosene for dual fuel Keystoker/unused
For what its worth,
I used pipe dope on my McDonnell & Miller RB122-E low Water Cut Off.
I used pipe dope on my McDonnell & Miller RB122-E low Water Cut Off.
- nepacoal
- Member
- Posts: 1696
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
Yes, I think we all use pipe dope on our installations. The thermal paste goes inside the well to provide a good thermal conductivity to the probe. not supposed to use tape or thermal paste with a lwco probe like hydrolevel unit i mentioned. You were saying to rip out the well if he used tape. That is not necessary for a normal temperature well. Tape and dope will work great and never interfere with the probe using thermal paste in a normal well.
-
- Member
- Posts: 80
- Joined: Fri. Aug. 01, 2014 9:40 pm
- Location: Bushkill, Pa
- Stoker Coal Boiler: AA 260
- Hand Fed Coal Stove: Harmon 2000
I will take your advice since I am absolutely new at this and find a Marsh gauge to replace the existing one. I will probably not replace anything until after the heating season is over. Everything is working well and right now and I do not want to drain any water out to replace the gauge.
For what its worth I only use Loctite 567 or 565. I have tried other products and for the most part they are ok but inevitably they always leak. When I use the Loctite I have NEVER had a leak so yes $65-80 a tube is expensive but not as expensive as having to take apart threaded pipe you have already assembled. In the thread about getting my boiler up and running I admitted to having a couple of leaks well those joints were assembled with a thread sealant other then the Loctite. I knew better when I did it but refused to take my own advice and dealt with the results of having to redo it.