Thinking of switching KAA2 for a warm air
-
- Member
- Posts: 133
- Joined: Thu. Jan. 23, 2014 10:23 am
- Location: Western Michigan
- Stoker Coal Boiler: KAA-2
- Hand Fed Coal Stove: Hitzer model 30-95 EZ Flow Sadly Retired
- Coal Size/Type: Rice
- Other Heating: Propane furnace/elec. water heater
Larry I will try that after it cools down outside, might hit 50* today. It is crazy, Wednesday morning -19, Sunday and Monday morning +41.
-
- Member
- Posts: 3555
- Joined: Tue. Sep. 04, 2007 10:14 pm
- Location: Dalton, MA
- Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
- Coal Size/Type: Buckwheat/anthracite
When fiddling with the system you might want to keep in mind the plenum temp and air-side delta-T that the furnace is designed for (sometimes shown on nameplate). Obviously you may want to use the coil to boost the btu's somewhat relative to that, but if you alter the airflow too much the system may not perform well if/when you switch back to the furnace.
Mike
Mike
-
- Member
- Posts: 133
- Joined: Thu. Jan. 23, 2014 10:23 am
- Location: Western Michigan
- Stoker Coal Boiler: KAA-2
- Hand Fed Coal Stove: Hitzer model 30-95 EZ Flow Sadly Retired
- Coal Size/Type: Rice
- Other Heating: Propane furnace/elec. water heater
Mike, my furnace blower was set on medium, I now have it on low now. When I shut down the boiler to work on the plumbing and to clean it, the furnace was cycling. The supply plenum temp. was about 165, I have not looked to see if that is two much or not.