EFM-520 Build Thread

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
kevin12973
Member
Posts: 93
Joined: Tue. Jun. 24, 2008 5:10 pm
Stove/Furnace Make: EFM
Stove/Furnace Model: 1956 SF-520 hot water
Location: albany NY

Post Fri. Oct. 24, 2008 8:45 pm

Actually I took the baro off a while ago, the second day of running the unit and havent put nit back on since. I suspected I did not have adequate draft so I put a cap in its place to play it safe. The manometer mesurement was taken with the cap in place and is still at .02 to .03 witch I understand is ok for this stoker but .04 is best. I will see when it gets cold if draft gets better.

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Fri. Oct. 24, 2008 10:17 pm

If the draft in the chimney improves and you don't have the damper adjusted, you'll have a little blast furnace in your house.
‹(•¿•)›

Visit Alternate Heating Sytems

User avatar
kevin12973
Member
Posts: 93
Joined: Tue. Jun. 24, 2008 5:10 pm
Stove/Furnace Make: EFM
Stove/Furnace Model: 1956 SF-520 hot water
Location: albany NY

Post Sun. Oct. 26, 2008 8:48 am

Thanks for the warning stoker man. I mounted the manometer permanently so I can moniter the draft because I don't know what to expect with my new install. Last night I had .01 when not running and .03 when running. By the way, really nice to meet you yesterday at the meet and greet. Wist I lived closer so I could help with your pipeing project.

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Sun. Oct. 26, 2008 11:16 am

If it's negative .03 at the door when running, it should be reduced via the damper to neg. .02. I'll let you know if my system leaks........if it gets done this year.
‹(•¿•)›

Post Reply