Approximate heat loss for bare copper pipe at 160 degrees F.

Post Reply
 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jan. 20, 2019 7:36 am

Per foot:

1/2" = 40 BTUH
3/4" = 49 BTUH
1" = 68 BTUH
1-1/4" =80 BTUH
1-1/2" = 92 BTUH

For my case, our homes zones average roughly 135 feet in total length, and each zone has on average 41 feet of 3/4" hot water baseboards.

135 - 41 = 94 feet of bare 3/4" copper pipe
94 feet x 49 BTUH/Ft. = 4,606 BTUH

If my hot water baseboards emit a nominal 550 BTUH per foot, then on each of my zones my bare copper pipe is adding roughly an additional 8.37 feet of "baseboard equivalent".

4,606 BTUH/550 BTUH/Ft.= 8.37 Ft. of baseboard equivalent

So effectively, each of my zones has (on average) 41 ft + 8.37 ft = 49.37 feet of baseboard equivalence.

Excluding the garage, and considering our 3 home heating zones:

3 x 49.37 Ft. x 550 BTUH/Ft. = 81,460 BTUH of radiators in my house (or roughly 32.33 BTUH per sq-ft).

 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Sun. Jan. 20, 2019 1:19 pm

You are not losing that heat. All the bare copper pipe is in your home. Put your slide rule away and enjoy the warmth.

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Sun. Jan. 20, 2019 1:28 pm

But sometimes ya just gotta play with numbers for the sake of it...
Rocket scientists and Nuclear engineers...
Astrophysicists just go off on a tangent...
LOL...
Made a rocket out of two soda cans and a small fire cracker....
The Nuke engineer was entertained for hours...
The shear simplicity of it...
Then he proceed to modify it...
Nose cones, tail fins, ballast, multiple stages...
LOL...


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jan. 20, 2019 1:52 pm

My calculations indicate the utilization of this heat as effective feet of HWB's. I tossed this out there for anyone considering HWB's and copper piping. I do not know the heat loss for PEX, or I would outline that also. It is likely well less than that for copper.

 
User avatar
wilder11354
Member
Posts: 1221
Joined: Sat. Jan. 29, 2011 10:48 pm
Location: Montrose, Pa.
Hand Fed Coal Boiler: Harman SF260 Boiler
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: nut or pea, anthracite
Other Heating: crown oil boiler, backup.if needed

Post by wilder11354 » Sun. Jan. 20, 2019 2:57 pm

This is what i used on copper pipes under house. House is on columns, and skirted. No Full foundation.http://www.industrialinsulation.com/images/fiberg ... 032018.pdf. Was looking for the website where i bought. Did notice price has gone up about double from when i got it 4 years ago.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jan. 20, 2019 3:47 pm

That's premium stuff there. My problem is finished ceilings in the basement and garage. I'm not changing anything due to that, and due to likely benefiting from the heat from most of the bare pipes regardless.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Jan. 20, 2019 5:29 pm

Are the heat loss numbers all equal if bare copper pipe in a open ceiling vs being in a closed or confined cavity above a finished ceiling?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jan. 20, 2019 5:52 pm

McGiever wrote:
Sun. Jan. 20, 2019 5:29 pm
Are the heat loss numbers all equal if bare copper pipe in a open ceiling vs being in a closed or confined cavity above a finished ceiling?
No. As the temperature differential between the surrounding air and the pipe surface diminishes, the quantity of BTUH evolving off of the pipe diminishes also. And visa-versa.

The figures I gave in my first post are for roughly 85 degrees of difference between surrounding air temperature and pipe surface temperature.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Jan. 20, 2019 11:24 pm

How about bare copper pipe in a open drafty space at 85* vs a sealed above finished ceiling dead air space at 85*, still same?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Mon. Jan. 21, 2019 3:22 am

McGiever wrote:
Sun. Jan. 20, 2019 11:24 pm
How about bare copper pipe in a open drafty space at 85* vs a sealed above finished ceiling dead air space at 85*, still same?
I'm not sure. My intuition would say that for this specific case the enclosed ceiling might more advantageously direct the heat to beneficial living areas above (vs. having some of it go out the basement walls), but I'm also aware that more often than not intuition makes for bad science. What is your opinion on this?

Post Reply

Return to “Stoker Coal Boilers Using Anthracite (Hydronic & Steam)”