Leaking EFM 520

 
JMakin
New Member
Posts: 8
Joined: Fri. Nov. 23, 2018 3:46 pm
Stoker Coal Boiler: EFM 520
Hot Air Coal Stoker Furnace: Leisure Line Hyfire II
Hot Air Coal Stoker Stove: Harman Magnum , Alaska kast console
Hand Fed Coal Stove: Really old probly home made shaker

Post by JMakin » Fri. Nov. 23, 2018 4:15 pm

Hi everyone. This is my first post here but i have been reading this form for years and first just want to say thank your for all the helpful info i have gotten from it!
Now on to my issue lol. I have burned coal for about the past 12 years and had great luck with all my stoves. I have always had hot air stoves from hand feed shakers to my last hyfire but i have been wanting a boiler for a while and decided when we bought this next house i would get one. I picked up an older 520 (late 50's early 60's i think, round door). The unit was in pretty good shape and was in service until the end of last winter when it was removed. The previous owner had taken good care of it and it didnt need much for repair other than a good cleaning. before i installed it i pressure tested the tank to 40 psi and let it sit over night with no pressure loss, so i thought i was all set. well i got it fired up about a week ago and all was great..... until last night that is lol. When i went out this morning pressure was down to about 5psi so i started checking all the connections and piping. I found a leak directly above the burn pot that was dripping down on to the fire. I dont see any cracks or damage, it just looks to be seeping through. im sure there must be a rust hole or a crack there but i cant seem to find it. I have gotten it shut down and drained so its not leaking any more. So my question is where do i go from here? Are the tanks repairable where the leak is or should i be looking for a new tank? Any thoughts or advice is welcome..Thanks


 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Nov. 23, 2018 4:23 pm

It is very uncommon for these boilers to leak in that area unless they are seriously corroded. I would remove the baffle, give it a good cleaning/vacuum, then refill the boiler and watch for a leak so you can pinpoint it. If the boiler is rusted through it is likely junk - but if it appears solid and is leaking at a weld, it can probably be repaired.

 
JMakin
New Member
Posts: 8
Joined: Fri. Nov. 23, 2018 3:46 pm
Stoker Coal Boiler: EFM 520
Hot Air Coal Stoker Furnace: Leisure Line Hyfire II
Hot Air Coal Stoker Stove: Harman Magnum , Alaska kast console
Hand Fed Coal Stove: Really old probly home made shaker

Post by JMakin » Fri. Nov. 23, 2018 4:28 pm

Ok thanks for the quick reply. i will get it cleaned out and wire brush it to see what i can find. ill post some pics when i get it cleaned.

 
ben
Member
Posts: 178
Joined: Thu. Aug. 06, 2009 9:06 pm
Location: n central PA
Stoker Coal Boiler: EFM 350 with an S-20 pot (1966)
Coal Size/Type: Rice

Post by ben » Sat. Nov. 24, 2018 7:47 am

Is there a boiler sealer product ? I think I heard of something that actually is added to the boiler.

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Sun. Nov. 25, 2018 1:24 am

Yes, from experience I can say Oatey Boiler Liquid is effective at sealing leaks. Maybe others have experience with other specific products.

Mike

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sun. Nov. 25, 2018 7:05 am


 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Nov. 25, 2018 9:34 am

If the leak is from a hairline crack in otherwise solid steel, a stop-leak product may be all that is needed. If the boiler is rusted through, no amount of stop leak is going to correct it.


 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Sun. Nov. 25, 2018 9:37 am

Find the leak...
Determine the cause...
Fitting loose, bad weld, crack but sound or rot...
You don't want the boiler to burst from rot...

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Sun. Nov. 25, 2018 11:22 am

I guess I am assuming that the 40 psi pressure test described by the OP would have identified any major rot issues affecting the integrity of the boiler vessel. I think even some new boiler mfgrs recommend use of boiler liquid during installation, which can address isolated flaws in materials, welds, etc. that may exist. Obviously it has limits, but if there isn't a big rot issue it can provide a cost-effective remedy.

Mike

 
JMakin
New Member
Posts: 8
Joined: Fri. Nov. 23, 2018 3:46 pm
Stoker Coal Boiler: EFM 520
Hot Air Coal Stoker Furnace: Leisure Line Hyfire II
Hot Air Coal Stoker Stove: Harman Magnum , Alaska kast console
Hand Fed Coal Stove: Really old probly home made shaker

Post by JMakin » Wed. Nov. 28, 2018 4:12 pm

Finally got some time to work on the boiler. I wire wheeled the tank and tried to get it cleaned up a bit. Man it tough working on the inside of a round door! Got it cleaned up and found the hole/crack sort of. The tank does have some rust but doesn't seem rotten. I took a hammer and gave it a few good whacks and I didn't punch through or cause any new holes. I think at this point I'm just going to tear it all back down and remove the tank so I can get at it better. I contacted scrapper and I might just replace the tank depending on what he has. I attached a few photos. The wetspot in the middle of the dry part is where the hole is. The last one is after I beat on it with a hammer lol

Attachments

IMG_20181128_155108.jpg
.JPG | 370.1KB | IMG_20181128_155108.jpg
IMG_20181128_155111.jpg
.JPG | 372.4KB | IMG_20181128_155111.jpg
IMG_20181128_155118.jpg
.JPG | 366.2KB | IMG_20181128_155118.jpg
IMG_20181128_155222.jpg
.JPG | 351KB | IMG_20181128_155222.jpg

 
ryan20strohl
Member
Posts: 145
Joined: Tue. Jul. 03, 2012 10:00 pm
Stoker Coal Boiler: efm coal boiler
Coal Size/Type: rice
Other Heating: Bryant evolution heat pump

Post by ryan20strohl » Wed. Nov. 28, 2018 4:45 pm

Never seen a boiler do that unless it was a steam boiler, that was taken out of service if so junk it just problem in the future, i dont save steam boiler i womt touch them i got burned on a couple

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Nov. 28, 2018 6:42 pm

Wow! That's a shame about your boiler. Replacing it won't be easy, that's a big job.

The only thing I can think of that would cause that is firing it with the water level too low. As Ryan pointed out, that is more likely with a steam system then a hot water system. I'm sure Scrapper can fix you up with another boiler to replace it.

-Don

 
JMakin
New Member
Posts: 8
Joined: Fri. Nov. 23, 2018 3:46 pm
Stoker Coal Boiler: EFM 520
Hot Air Coal Stoker Furnace: Leisure Line Hyfire II
Hot Air Coal Stoker Stove: Harman Magnum , Alaska kast console
Hand Fed Coal Stove: Really old probly home made shaker

Post by JMakin » Wed. Nov. 28, 2018 6:59 pm

Thanks for the replies. I'm not sure if it was set up for steam or hot water. Not looking forward to taking it all apart again! I just got it all put together. There was nothing to indicate if it was steam. How can you tell? There was none of the controllers with the boiler when I got it.

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Wed. Nov. 28, 2018 7:28 pm

Sight glass...

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Nov. 28, 2018 7:39 pm

Looks like a pinhole. I would drill it out and weld it up. Drill right through and go less with larger drills until you have a nice scooped out spot to weld out.


Post Reply